<p>Mariam,</p>
<p> The wall transfer function coefficients are computed with a
certain time base. When you run a simulation in which your time
step is a lot smaller than the wall time base you start to see the
times at which the wall transfer function coefficients are
updated, which produces this step-like plot. Depending on the
construction of the walls in your building, you can probably
reduce the wall timebase and get rid of the steps. The time base
is set in TRNBuild's output manager. I'd suggest using a 0.25h
time base.</p>
<p>kind regards,</p>
<p> David</p>
<p> <br>
</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 05/06/2020 04:42, Mariam Elnour via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:VI1PR0902MB2192A27685E65B5175AD7EA3E6A40@VI1PR0902MB2192.eurprd09.prod.outlook.com">
<meta http-equiv="Content-Type" content="text/html;
charset=windows-1252">
<style type="text/css" style="display:none;"> P {margin-top:0;margin-bottom:0;} </style>
<div style="font-family: Calibri, Helvetica, sans-serif;
font-size: 12pt; color: rgb(0, 0, 0);">
Dear colleagues,</div>
<div style="font-family: Calibri, Helvetica, sans-serif;
font-size: 12pt; color: rgb(0, 0, 0);">
I am simulating a 3-floor building to observe the change in
the zones' temperature. In reference to the plots below, I
noticed that the
<span style="font-family: Calibri, Helvetica, sans-serif;
background-color: rgb(255, 255, 255); display: inline
!important">
temperature transition has a stair-like behavior. The
simulation step is 0.015 hr (1 min). I would appreciate your
help with this as I don't seem to figure what is causing it? </span></div>
<div style="font-family: Calibri, Helvetica, sans-serif;
font-size: 12pt; color: rgb(0, 0, 0);">
<br>
</div>
<div style="font-family: Calibri, Helvetica, sans-serif;
font-size: 12pt; color: rgb(0, 0, 0);">
<span style="font-family: Calibri, Helvetica, sans-serif;
background-color: rgb(255, 255, 255); display: inline
!important"><br>
</span></div>
<div style="font-family: Calibri, Helvetica, sans-serif;
font-size: 12pt; color: rgb(0, 0, 0);">
<img size="45680" contenttype="image/png" unselectable="on"
tabindex="-1" style="user-select: none; width: 589.967px;
height: 303.58px;" data-imgsize="custom"
data-outlook-trace="F:1|T:1"
src="cid:part1.D8F5B553.17FD0868@tess-inc.com" class=""
width="589.9665665153743" height="303.58049342105267"><br>
</div>
<div style="font-family: Calibri, Helvetica, sans-serif;
font-size: 12pt; color: rgb(0, 0, 0);">
</div>
<div style="font-family: Calibri, Helvetica, sans-serif;
font-size: 12pt; color: rgb(0, 0, 0);">
<div style="margin: 0px; font-size: 12pt; font-family: Calibri,
Helvetica, sans-serif">
<span style="margin: 0px; background-color: rgb(255, 255,
255); display: inline !important"><br>
Regards,</span></div>
<div style="margin: 0px; font-size: 12pt; font-family: Calibri,
Helvetica, sans-serif">
<span style="margin: 0px; background-color: rgb(255, 255,
255); display: inline !important">Mariam</span></div>
<br>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>