<p>Hüseyin,</p>
<p> If you are allowing the temperature of the space to float then
there are no energy demands on the space. If you set a heating
and/or cooling set point temperature such that the temperature of
the space is limited and will not fall below the heating set point
or rise above the cooling set point then you will start to see
energy demands: the energy required to maintain the space between
the bounds that you have defined.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 04/08/2020 13:31, Hüseyin Günhan
Özcan via TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:23859e100a4741bf99f04538a96483c1@ExchMbx2.yustaff.local">
<meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
<meta name="Generator" content="Microsoft Word 15 (filtered
medium)">
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
{font-family:Consolas;
panose-1:2 11 6 9 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri",sans-serif;
mso-fareast-language:EN-US;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:#0563C1;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:#954F72;
text-decoration:underline;}
pre
{mso-style-priority:99;
mso-style-link:"HTML Önceden Biçimlendirilmiş Char";
margin:0cm;
margin-bottom:.0001pt;
font-size:10.0pt;
font-family:"Courier New";}
span.HTMLncedenBiimlendirilmiChar
{mso-style-name:"HTML Önceden Biçimlendirilmiş Char";
mso-style-priority:99;
mso-style-link:"HTML Önceden Biçimlendirilmiş";
font-family:Consolas;
mso-fareast-language:EN-US;}
p.msonormal0, li.msonormal0, div.msonormal0
{mso-style-name:msonormal;
mso-margin-top-alt:auto;
margin-right:0cm;
mso-margin-bottom-alt:auto;
margin-left:0cm;
font-size:11.0pt;
font-family:"Calibri",sans-serif;}
span.E-postaStili20
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:windowtext;}
span.E-postaStili21
{mso-style-type:personal;
font-family:"Calibri",sans-serif;
color:windowtext;}
span.E-postaStili23
{mso-style-type:personal-reply;
font-family:"Calibri",sans-serif;
color:windowtext;}
.MsoChpDefault
{mso-style-type:export-only;
font-size:10.0pt;}
@page WordSection1
{size:612.0pt 792.0pt;
margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal">Dear Jeff,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Hi again. Currently it is working. I
defined the Number of profiles for each day to be 2 in the
parameter part of the type 41. Then, it has stated to operate
between specified points.<o:p></o:p></p>
<p class="MsoNormal">That was the key part. Thanks for your
help.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">I have an other question about my Project
for type 56 building model. Although everthing seem to be
normal for airnodes such as temperature, relative humidity,
the sensible and latent energy demands of the airnodes (the
outputs of type 56) equals to always zero. Should I define
something special here? Do you or does anyone have an idea
about this case ?<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Thanks in advance.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">HG Ozcan<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span
style="mso-fareast-language:TR">From:</span></b><span
style="mso-fareast-language:TR"> Hüseyin Günhan Özcan
<br>
<b>Sent:</b> Wednesday, April 8, 2020 4:42 PM<br>
<b>To:</b> Jeff Thornton <a class="moz-txt-link-rfc2396E" href="mailto:thornton@tess-inc.com"><thornton@tess-inc.com></a>;
TRNSYS users mailing list at OneBuilding.org
<a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org"><trnsys-users@lists.onebuilding.org></a><br>
<b>Subject:</b> RE: [TRNSYS-users] About scheduling<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Dear Jeff,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Thanks for your help. However, type 922c
operates always on althogh I defined the types 14 and 41
together with the type 108 signals outputs by using an
equation. Than, I connected them to conditioning signals of
each 5 stages.<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">Can it be beacuse of proforma definition
for type 41?<o:p></o:p></p>
<p class="MsoNormal">Regards,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">HG OZCAN<o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<div>
<div style="border:none;border-top:solid #E1E1E1
1.0pt;padding:3.0pt 0cm 0cm 0cm">
<p class="MsoNormal"><b><span
style="mso-fareast-language:TR">From:</span></b><span
style="mso-fareast-language:TR"> Jeff Thornton <<a
href="mailto:thornton@tess-inc.com"
moz-do-not-send="true">thornton@tess-inc.com</a>>
<br>
<b>Sent:</b> Wednesday, April 8, 2020 3:01 PM<br>
<b>To:</b> TRNSYS users mailing list at OneBuilding.org
<<a href="mailto:trnsys-users@lists.onebuilding.org"
moz-do-not-send="true">trnsys-users@lists.onebuilding.org</a>><br>
<b>Cc:</b> Hüseyin Günhan Özcan <<a
href="mailto:huseyin.ozcan@yasar.edu.tr"
moz-do-not-send="true">huseyin.ozcan@yasar.edu.tr</a>><br>
<b>Subject:</b> Re: [TRNSYS-users] About scheduling<o:p></o:p></span></p>
</div>
</div>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal">If the control signal to the equipment is a
function of both time of day/ year and a thermostat then the
input should reflect that. Use an equation and multiply the
on/off signal from your forcing function by the on/off signal
from your thermostat. Then use that value (only on when both
are satisfied) as the inputs to fans, pumps, equipment etc.<span
style="mso-fareast-language:TR"><o:p></o:p></span></p>
<div>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt">Jeff - TESS<o:p></o:p></p>
<div>
<p class="MsoNormal">Sent from my iPhone<o:p></o:p></p>
</div>
<div>
<p class="MsoNormal" style="margin-bottom:12.0pt"><o:p> </o:p></p>
<blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
<p class="MsoNormal" style="margin-bottom:12.0pt">On Apr
7, 2020, at 12:42 PM, Hüseyin Günhan Özcan via
TRNSYS-users <<a
href="mailto:trnsys-users@lists.onebuilding.org"
moz-do-not-send="true">trnsys-users@lists.onebuilding.org</a>>
wrote:<o:p></o:p></p>
</blockquote>
</div>
<blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
<div>
<p class="MsoNormal"> <span
style="mso-fareast-language:TR"><o:p></o:p></span></p>
<p class="MsoNormal">Hello everyone,<o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal">I hope you are all doing well and
healthy.<o:p></o:p></p>
<p class="MsoNormal">I am modeling a PV powered air
conditioner unit with back up system. My model cuurently
operates. However, I am also planing to switch off the
air conditioner between 18:00 to 08:00 on weekdays and
also at the weekends.
<o:p></o:p></p>
<p class="MsoNormal">I tried to use type 14 (weekdays and
weekend defination) with type 41 (whole week). But I
could not find the connection for output of type 41,
namely forcing function output for current day. I
suppose that they have to be connected to fan control
signal, mass flow rate or conditioning signals. But they
are all connected to other models like building and
termostat.<o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal">Can you please help me on this issue?<o:p></o:p></p>
<p class="MsoNormal">Best regards.<o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal"><b><span
style="font-family:"Times New
Roman",serif;color:#1F497D;mso-fareast-language:TR">Res.
Assist. Huseyin Gunhan Ozcan</span></b><o:p></o:p></p>
<p class="MsoNormal"><b><span
style="font-family:"Times New
Roman",serif;color:#1F497D;mso-fareast-language:TR">Yasar
Uni. Dept. of Energ. Sys. Eng.
</span></b><o:p></o:p></p>
<div>
<p class="MsoNormal"><b><span
style="font-family:"Times New
Roman",serif;color:#1F497D;mso-fareast-language:TR"><image001.png><o:p></o:p></span></b></p>
</div>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<p class="MsoNormal"> <o:p></o:p></p>
<table class="MsoNormalTable" cellpadding="0" border="0">
<tbody>
<tr>
<td style="background:white;padding:.75pt .75pt
.75pt .75pt">
<pre><span style="color:black">Bu elektronik postada bulunan tum fikir ve gorusler ve ekindeki dosyalar sadece adres sahip/sahiplerine ait olup,<o:p></o:p></span></pre>
<pre><span style="color:black">Yasar Universitesi bu mesajin icerigi ile ilgili olarak hic bir hukuksal sorumlulugu kabul etmez. Eger gonderilmesi<o:p></o:p></span></pre>
<pre style="margin-bottom:12.0pt"><span style="color:black">dusunulen kisi veya kurulus degilseniz, lutfen gonderen kisiyi derhal haberdar ediniz ve mesaji sisteminizden siliniz.
<o:p></o:p></span></pre>
<pre><span style="color:black">The information contained in this e-mail and any files transmitted with it are intended solely for the use of the<o:p></o:p></span></pre>
<pre><span style="color:black">individual or entity to whom they are addressed Yasar University does not accept legal responsibility for the <o:p></o:p></span></pre>
<pre><span style="color:black">contents. If you are not the intended recipient, please immediately notify the sender and delete the message from your system.<o:p></o:p></span></pre>
</td>
</tr>
</tbody>
</table>
<p class="MsoNormal"><span style="mso-fareast-language:TR">_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@lists.onebuilding.org"
moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a><br>
<a
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><o:p></o:p></span></p>
</div>
</blockquote>
</div>
</div>
<table>
<tbody>
<tr>
<td bgcolor="#ffffff"><font color="#000000">
<pre>Bu elektronik postada bulunan tum fikir ve gorusler ve ekindeki dosyalar sadece adres sahip/sahiplerine ait olup,
Yasar Universitesi bu mesajin icerigi ile ilgili olarak hic bir hukuksal sorumlulugu kabul etmez. Eger gonderilmesi
dusunulen kisi veya kurulus degilseniz, lutfen gonderen kisiyi derhal haberdar ediniz ve mesaji sisteminizden siliniz.
The information contained in this e-mail and any files transmitted with it are intended solely for the use of the
individual or entity to whom they are addressed Yasar University does not accept legal responsibility for the
contents. If you are not the intended recipient, please immediately notify the sender and delete the message from your system.</pre>
</font></td>
</tr>
</tbody>
</table>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>