    <p>Muhammad,</p>
    <p>  Are you looking for an absorption heat pump model? My
      understanding of absorption chillers and heat pumps (separately)
      is that they use fundamentally different processes for providing
      cooling. Heat pumps rely on fairly standard vapor compression
      cycle that (normally) use electricity to run the compressor. In an
      absorption chiller you have two coolants, one of which provides
      evaporative cooling and in so doing is absorbed into the second. A
      heat input is then needed to reseparate the coolants. <br>
    </p>
    <p>  There are such things as absorption heat pumps and if you are
      looking for one of those then I am not aware of a TRNSYS model.
      Based on what little I have read, I do not think that Type677 (or
      any of the other TRNSYS absorption chiller models) could be used
      to provide both heating and cooling. If you are aware of a
      specific device for which manufacturer's performance data is
      available then it would not be hard to create a TRNSYS Type that
      reads the data. In fact that is the approach that Type677 takes.</p>
    <p>kind regards,</p>
    <p>David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 04/09/2020 05:58, Muhammad Zeeshan
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAOVVR-c=9jYBhsrxNV1mS6Q7vNOvWWsaAJAbaHAVGyCov1xA6A@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Hello everyone,
        <div>                          I am working on a double effect
          absorption chiller(Type 677) in TRNSYS. Is is possible to use
          the same chiller as heat pump in TRNSYS during heating season.
          Or any other component in TRNSYS which can model absorption
          chiller as heat pump?</div>
        <div><br>
        </div>
        <div>Your help in this regard is highly appreciated.</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>Warm regards,</div>
        <div>Muhammad Zeeshan</div>
      </div>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>