    <p>Hüseyin</p>
    <p>  This may seem very basic but make sure that you have turned off
      the automatic heating and cooling in TRNBuild so that the
      temperature of your zone is floating. You can verify this by
      running your simulation; the zone temperature should more or less
      follow the ambient temperature. You will then implement a
      thermostat to watch the zone temperature and turn on/off the heat
      pump accordingly. <br>
    </p>
    <p>  If that is what you are doing already and the power and
      capacity of the heat pump is not changing at all then it must mean
      that neither the return air temperature nor the water inlet
      temperature is changing at all. It could also mean that the return
      air temperature and inlet water temperature are outside the range
      of data values given in the data file. The routine that reads the
      data file and interpolate within the range but cannot extrapolate
      beyond the range given.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 03/27/2020 09:29, Hüseyin Günhan
      Özcan wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:b81f933764aa4577937ca234704e31d1@ExchMbx2.yustaff.local">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:"Yu Gothic";
        panose-1:2 11 4 0 0 0 0 0 0 0;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
@font-face
        {font-family:Consolas;
        panose-1:2 11 6 9 2 2 4 3 2 4;}
@font-face
        {font-family:"\@Yu Gothic";
        panose-1:2 11 4 0 0 0 0 0 0 0;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:purple;
        text-decoration:underline;}
p
        {mso-style-priority:99;
        mso-margin-top-alt:auto;
        margin-right:0cm;
        mso-margin-bottom-alt:auto;
        margin-left:0cm;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
pre
        {mso-style-priority:99;
        mso-style-link:"HTML Preformatted Char";
        margin:0cm;
        margin-bottom:.0001pt;
        font-size:10.0pt;
        font-family:"Courier New";}
p.msonormal0, li.msonormal0, div.msonormal0
        {mso-style-name:msonormal;
        mso-margin-top-alt:auto;
        margin-right:0cm;
        mso-margin-bottom-alt:auto;
        margin-left:0cm;
        font-size:12.0pt;
        font-family:"Times New Roman",serif;}
span.HTMLPreformattedChar
        {mso-style-name:"HTML Preformatted Char";
        mso-style-priority:99;
        mso-style-link:"HTML Preformatted";
        font-family:"Consolas",serif;}
span.EmailStyle21
        {mso-style-type:personal-reply;
        font-family:"Times New Roman",serif;
        color:windowtext;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-size:10.0pt;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 70.85pt 70.85pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US">Dear all,<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US">I have a similar question about modeling air
            source heat pump.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US">In my case I am working the model inverter heat
            pump so I selected the multi stage heat pump (Type 922c).<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US">Meanwhile, I connected its return temperature
            value to the Type 56 indoor temperature (I am following a
            single room) and I also use Type 15-6 for outdoor
            conditions. Although I make some changes in the building
            file (internal heat gain, regimes, etc.) and weather data
            the model shows always the same values.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US">Therefore, I realized that it only works based
            on external catalogue values. But, it does not make sense.
            Do you have an idea about this case ? How can type 922c
            operates based on temperature variations belongs to the
            building.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US">Another question is how can I change the
            catalogue values ? (I have no problem in proforma including
            parameter, input and output parts).<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"
            lang="EN-US">Thanks in advance.<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><b><span style="font-size:11.0pt">Huseyin
              Gunhan Ozcan<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span style="font-size:11.0pt">Visiting
              Researcher<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span style="font-size:11.0pt">Porto
              Uni., Dept. of Mech. Eng.<o:p></o:p></span></b></p>
        <p class="MsoNormal"><b><span style="font-size:11.0pt"><o:p> </o:p></span></b></p>
        <p class="MsoNormal"><b><span
              style="font-size:11.0pt;font-family:"Yu
              Gothic",sans-serif"><img
                style="width:1.6979in;height:.677in"
                id="Picture_x0020_1"
                src="cid:part1.3FC597C1.F5A9965E@tess-inc.com"
                alt="Adsız" class="" width="163" height="65"><o:p></o:p></span></b></p>
        <p class="MsoNormal"><span
            style="font-size:11.0pt;mso-fareast-language:EN-US"><o:p> </o:p></span></p>
        <div>
          <div style="border:none;border-top:solid #E1E1E1
            1.0pt;padding:3.0pt 0cm 0cm 0cm">
            <p class="MsoNormal"><b><span
                  style="font-size:11.0pt;font-family:"Calibri",sans-serif"
                  lang="EN-US">From:</span></b><span
                style="font-size:11.0pt;font-family:"Calibri",sans-serif"
                lang="EN-US"> TRNSYS-users
                <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org"><trnsys-users-bounces@lists.onebuilding.org></a>
                <b>On Behalf Of </b>David BRADLEY via TRNSYS-users<br>
                <b>Sent:</b> Friday, March 27, 2020 1:45 PM<br>
                <b>To:</b> TRNSYS users mailing list at OneBuilding.org
                <a class="moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org"><trnsys-users@lists.onebuilding.org></a><br>
                <b>Cc:</b> David BRADLEY <a class="moz-txt-link-rfc2396E" href="mailto:d.bradley@tess-inc.com"><d.bradley@tess-inc.com></a>;
                Muhammad Zeeshan <a class="moz-txt-link-rfc2396E" href="mailto:zeeshanmuhammad922@gmail.com"><zeeshanmuhammad922@gmail.com></a><br>
                <b>Subject:</b> Re: [TRNSYS-users] Type 941(Air to water
                heat pump)<o:p></o:p></span></p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p>Muhammad,<o:p></o:p></p>
        <p>  Please refer to the Type941 documentation. It explains how
          the external files and the parameters relate to each other to
          compute the overall capacity and power consumption of the heat
          pump.
          <o:p></o:p></p>
        <p>  The evaporator does not really need to be designed more
          than to choose a machine with an appropriate rated capacity.
          Traditionally that might mean adding a safety factor to the
          peak cooling load (10% is often used) and then selecting a
          machine that will meet that capacity. Also bear in mind that
          Type941 models a single speed (ie single capacity) heat pump
          that is either on or off. Depending on how variable the load
          in your building it, you might want to meet that load with
          multiple smaller heat pumps rather than one big one.<o:p></o:p></p>
        <p>kind regards,<o:p></o:p></p>
        <p> David<o:p></o:p></p>
        <p><o:p> </o:p></p>
        <div>
          <p class="MsoNormal">On 03/27/2020 08:02, Muhammad Zeeshan via
            TRNSYS-users wrote:<o:p></o:p></p>
        </div>
        <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
          <div>
            <p class="MsoNormal">Hello Everyone, <o:p></o:p></p>
            <div>
              <p class="MsoNormal">              <o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal">                            I am
                working on cooling a building with type 41(air to water
                source heat pump). The cooling load of the building is
                25 tons. I want to know<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal"><o:p> </o:p></p>
            </div>
            <div>
              <p class="MsoNormal">1)- how the compressor power will be
                calculated? as the external files of type 941 contains
                fractions of compressor power which shows no link to the
                equations provided in manual. How to link the external
                file with the provided equations?<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal"><o:p> </o:p></p>
            </div>
            <div>
              <p class="MsoNormal">2)-As the cooling load of the
                building is 25 tons, how to design the evaporator for
                this building load?<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal"><o:p> </o:p></p>
            </div>
            <div>
              <p class="MsoNormal">Your help in this regard will be
                highly appreciated.<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal"><o:p> </o:p></p>
            </div>
            <div>
              <p class="MsoNormal"><o:p> </o:p></p>
            </div>
            <div>
              <p class="MsoNormal"><o:p> </o:p></p>
            </div>
            <div>
              <p class="MsoNormal">Regards,<o:p></o:p></p>
            </div>
            <div>
              <p class="MsoNormal">Muhammad Zeeshan<o:p></o:p></p>
            </div>
          </div>
          <p class="MsoNormal"><br>
            <br>
            <o:p></o:p></p>
          <pre>_______________________________________________<o:p></o:p></pre>
          <pre>TRNSYS-users mailing list<o:p></o:p></pre>
          <pre><a href="mailto:TRNSYS-users@lists.onebuilding.org" moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a><o:p></o:p></pre>
          <pre><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><o:p></o:p></pre>
        </blockquote>
        <pre>-- <o:p></o:p></pre>
        <pre>***************************<o:p></o:p></pre>
        <pre>David BRADLEY<o:p></o:p></pre>
        <pre>Principal<o:p></o:p></pre>
        <pre>Thermal Energy Systems Specialists, LLC<o:p></o:p></pre>
        <pre>3 North Pinckney Street - suite 202<o:p></o:p></pre>
        <pre>Madison, WI  53703 USA<o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre>P:+1.608.274.2577<o:p></o:p></pre>
        <pre>F:+1.608.278.1475<o:p></o:p></pre>
        <pre><a href="mailto:d.bradley@tess-inc.com" moz-do-not-send="true">d.bradley@tess-inc.com</a><o:p></o:p></pre>
        <pre><o:p> </o:p></pre>
        <pre><a href="http://www.tess-inc.com" moz-do-not-send="true">http://www.tess-inc.com</a><o:p></o:p></pre>
        <pre><a href="http://www.trnsys.com" moz-do-not-send="true">http://www.trnsys.com</a><o:p></o:p></pre>
      </div>
      <table>
        <tbody>
          <tr>
            <td bgcolor="#ffffff"><font color="#000000">
                <pre>Bu elektronik postada bulunan tum fikir ve gorusler ve ekindeki dosyalar sadece adres sahip/sahiplerine ait olup,
Yasar Universitesi bu mesajin icerigi ile ilgili olarak hic bir hukuksal sorumlulugu kabul etmez. Eger gonderilmesi
dusunulen kisi veya kurulus degilseniz, lutfen gonderen kisiyi derhal haberdar ediniz ve mesaji sisteminizden siliniz.


The information contained in this e-mail and any files transmitted with it are intended solely for the use of the
individual or entity to whom they are addressed Yasar University does not accept legal responsibility for the 
contents. If you are not the intended recipient, please immediately notify the sender and delete the message from your system.</pre>
              </font></td>
          </tr>
        </tbody>
      </table>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>