    <p>Arian,</p>
    <p> There are three desiccant wheel models in the TESS HVAC library:
      Type716, Type1716, and Type1225. None of them have silica gel
      properties built into them. However, Types716 and 1716 use a
      concept called a potential curve that is defined by two
      parameters, F1 and F2. Technically, you could get F1 and F2
      parameters for any desiccant that you want. Practically, though, I
      think it would probably be difficult to find them. Type1225 is a
      performance map that gives outlet air conditions as a function of
      inlet air conditions. The map that is provided as an example was
      generated using a free tool that the manufacturer of a particular
      rotary desiccant system provided in order to assist designers with
      equipment selection.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 03/17/2020 04:57, Arian Bahrami
      wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:730633758.6954328.1584439024636@mail.yahoo.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div class="yahoo-style-wrap" style="font-family:times new roman,
        new york, times, serif;font-size:16px;">
        <div dir="ltr" data-setdir="false">Dear all,</div>
        <div dir="ltr" data-setdir="false"><br>
        </div>
        <div dir="ltr" data-setdir="false">I wonder whether there are
          any TESS components for desiccant wheel using other materials
          rather than Silica gel?</div>
        <div dir="ltr" data-setdir="false"><br>
        </div>
        <div dir="ltr" data-setdir="false">Best Regards,</div>
        <div dir="ltr" data-setdir="false"><br>
        </div>
        <div dir="ltr" data-setdir="false">Arian</div>
        <div dir="ltr" data-setdir="false"><br>
        </div>
        <div dir="ltr" data-setdir="false"><br>
        </div>
        <div dir="ltr" data-setdir="false"><br>
        </div>
      </div>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>