<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>Salma,</p>
    <p>  The method you'd use depends a bit on what you care about. If
      the nearby buildings provide shading to your building but do not
      have any other significant impact then I would set up a shading
      object in Trnsys3d. If the buildings are close enough that the
      temperature of rooms in those buildings impacts the temperature in
      your building then I would suggest using the TRNBuild/Type56
      concept of a BOUNDARY wall for those facades.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 12/09/2019 06:26, SALMA LAHMAR via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAFpXWorJb-t5AO4iSocTb6x4Pv8D=a1kkzu=UsZ8no0i0uRDRA@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">  Hello all,
        <div>The east and west side of my building are close to
          other buildings. How can I simulate that in trnbuild?<br>
        </div>
        <div>thanks in </div>
      </div>
      <div hspace="streak-pt-mark" style="max-height:1px"><img alt=""
          style="width:0px;max-height:0px;overflow:hidden"
src="https://mailfoogae.appspot.com/t?sender=acy5sYWhtYXJAZW5pbS5hYy5tYQ%3D%3D&type=zerocontent&guid=c41065fe-6e4a-41f3-8aee-f2a97d972f88"
          moz-do-not-send="true"><font size="1" color="#ffffff">ᐧ</font></div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>