<div dir="auto">Thanks a lot! </div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">Le mar. 10 déc. 2019 à 19:13, David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>> a écrit :<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <p>Salma,</p>
    <p> There are (as usual) a number of different ways of having all
      the results from a parametric run put into the same output file.
      One way is to use a Type25 printer as an output device in your
      simulation and to set it to "append" mode instead of "overwrite
      mode." The mode is controlled by a parameter.  The other thing
      you'll need to do is to make sure that the name of the output file
      is NOT the same as the name of your input file, otherwise there
      will be one output file produced per table run. Note that a number
      of the standard printer output components in TRNSYS allow the
      switch between append and overwrite mode.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div>On 12/08/2019 07:33, SALMA LAHMAR via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">I have to 
        <span style="color:rgb(17,17,17);font-family:Roboto,Arial,sans-serif;font-size:14px">run
          a lot of simulations to calculate the building energy
          consumption </span>depending on the value of different
        parameters. 
        <div>I tried to use trnedit to make a table but I don't know how
          to have a result of all simulation in one output file like
          : \Examples\Parametric Runs\SDHW-ParametricRuns in trnsys.</div>
        <div>thanks in advance</div>
      </div>
      <div hspace="streak-pt-mark" style="max-height:1px"><img alt="" style="width:0px;max-height:0px;overflow:hidden" src="https://mailfoogae.appspot.com/t?sender=acy5sYWhtYXJAZW5pbS5hYy5tYQ%3D%3D&type=zerocontent&guid=0f6add26-b773-4e64-bdf9-8534d3f5e7f3"><font size="1" color="#ffffff">ᐧ</font></div>
      <br>
      <fieldset></fieldset>
      <pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank" rel="noreferrer">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank" rel="noreferrer">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a href="mailto:d.bradley@tess-inc.com" target="_blank" rel="noreferrer">d.bradley@tess-inc.com</a>

<a href="http://www.tess-inc.com" target="_blank" rel="noreferrer">http://www.tess-inc.com</a>
<a href="http://www.trnsys.com" target="_blank" rel="noreferrer">http://www.trnsys.com</a></pre>
  </div>

</blockquote></div>