<p>You'll need to use a forcing function and set the non-summer months to a value of 1 and the summer months to a value of 0.  Then simply use an equation and multiply the control signals together:</p>
<p>On_Off_Pump = NotSummer * Type2ControlSignal</p>
<p> </p>
<p>where NotSummer is an equation connected to the Type 14 forcing function and Type2ControlSignal is an equation connected to the output of the Type 2 differential controller.  Then simply connect the On_Off_Pump equation to the input control signal for the pump.</p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---<br />Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577  Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton@tess-inc.com
</pre>
</div>
<p>On 12/06/2019 1:41 pm, Emre Arpaci via TRNSYS-users wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->
<div dir="ltr">hi trnsys user
<div>good weekend wishes</div>
<div> </div>
<div>I m controlling a pump with type 2b. I want to do that my pump would control with type 2b but in summer season (june ,july august) the pump would always off. </div>
<div> </div>
<div>Can I do this with trnsys and how ? </div>
<div>I shortly mean</div>
<div>9 months contro with differential element type 2</div>
<div>summer season is off.</div>
<div> </div>
<div>regards</div>