    <p>Emre,</p>
    <p> The most correct way to calculate the solar fraction is to sum
      up all of the energy consumed by the system (fans, pumps,
      auxiliary heaters) for each month and then to run the system again
      with the solar part of it disabled (or you can run a non-solar
      comparison system in parallel) and again sum up the energy
      consumed by all the equipment and divide the two by one another.
      The trouble with the method that you propose is that it may not be
      that all of the energy gain from the collector can be applied
      against the heating load. You have losses from storage, parasitic
      power from pumping, and it may be that the useful solar gain is
      only available when your load is already satisfied.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 11/25/2019 14:00, Emre Arpaci via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CADBhVH2J7=vp6QUAMU196apkDHaHs14y3k4kx=qUG_cy2h_ScQ@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">hi trnsys users
        <div>I have a question about solar fraction I m heating a space
          with solar assisted heat pump. and I want to calculate solar
          fraction with trnsys. I m using fan coils to heat up the
          space. so how can ı calculate solar fraction.If I do that the
          useful energy gain of collector in montly divided by required
          heating load in montly.</div>
        <div>is it give me the montly solar fraction or am i wrong ?  (
          I dont have dhw in my system)</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>regards</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>