<p>Gabriel,</p>
<p> Often heat pump catalogs will give performance data at a few
different flow rates on both the source and load sides of the heat
pump. For instance performance data may be given for 0.32, 0.50,
and 0.63 L/s on the load side and for the same on the source side.
The heat pump's "rated" performance is at one particular flow rate
on the load side and one particular flow rate on the source side.
In the example above, it might be given for 0.5 L/s on both the
load and source side. To get the normalized flow rates, you divide
each flow rate by the flow rate at the rated condition so you
would have 0.64, 1.0, and 1.26.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<div class="moz-cite-prefix">On 10/21/2019 06:15, Gabriel Lopez
Martinez-Fortun via TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:37A68B358C603442A77C7825527B59B950118AF2@vesta.corp.itccanarias.org">
<meta http-equiv="Content-Type" content="text/html;
charset=windows-1252">
<meta name="Generator" content="Microsoft Word 15 (filtered
medium)">
<!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
<style><!--
/* Font Definitions */
@font-face
{font-family:"Cambria Math";
panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
{font-family:Calibri;
panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
{margin:0cm;
margin-bottom:.0001pt;
font-size:11.0pt;
font-family:"Calibri",sans-serif;
mso-fareast-language:EN-US;}
a:link, span.MsoHyperlink
{mso-style-priority:99;
color:#0563C1;
text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
{mso-style-priority:99;
color:#954F72;
text-decoration:underline;}
pre
{mso-style-priority:99;
mso-style-link:"HTML con formato previo Car";
margin:0cm;
margin-bottom:.0001pt;
font-size:10.0pt;
font-family:"Courier New";}
span.EstiloCorreo17
{mso-style-type:personal-compose;
font-family:"Calibri",sans-serif;
color:windowtext;}
span.HTMLconformatoprevioCar
{mso-style-name:"HTML con formato previo Car";
mso-style-priority:99;
mso-style-link:"HTML con formato previo";
font-family:"Courier New";
mso-fareast-language:ES;}
.MsoChpDefault
{mso-style-type:export-only;
font-family:"Calibri",sans-serif;
mso-fareast-language:EN-US;}
@page WordSection1
{size:612.0pt 792.0pt;
margin:70.85pt 3.0cm 70.85pt 3.0cm;}
div.WordSection1
{page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
<div class="WordSection1">
<p class="MsoNormal">Hi user´s,<o:p></o:p></p>
<p class="MsoNormal"><o:p> </o:p></p>
<p class="MsoNormal"><span lang="EN-GB">I am trying to use type
927 but I don’t understand completely how to define the data
files. Specifically, I don’t know how to obtain the
“Nomalized load flow rate” and “Normalized Source flow
rate”.<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-GB"><o:p> </o:p></span></p>
<p class="MsoNormal"><span lang="EN-GB">Thank you for helping
me.<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-GB">Best regards,<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-GB">Gabriel<o:p></o:p></span></p>
<p class="MsoNormal"><span lang="EN-GB"><o:p> </o:p></span></p>
<div class="MsoNormal" style="text-align:center" align="center"><span
style="color:black;mso-fareast-language:ES">
<hr style="color:#009EE0" width="100%" size="2"
noshade="noshade" align="center">
</span></div>
<p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black;mso-fareast-language:ES">Gabriel
López Martínez-Fortún</span></b><b><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black;mso-fareast-language:ES"><o:p></o:p></span></b></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black;mso-fareast-language:ES">Departamento
de Energías Renovables</span><span
style="font-size:12.0pt;font-family:"Times New
Roman",serif;color:navy;mso-fareast-language:ES"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black;mso-fareast-language:ES">División
de Investigación y Desarrollo Tecnológico<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="color:#1F497D;mso-fareast-language:ES"><img
id="Imagen_x0020_2"
src="cid:part1.C65AEF84.D402A6BD@tess-inc.com"
alt="Descripción: cid:image001.gif@01CE6200.B91ADAB0"
class="" width="305" height="75"></span><span
style="color:#1F497D;mso-fareast-language:ES"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="color:#1F497D;mso-fareast-language:ES"><o:p> </o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">Playa
de Pozo Izquierdo s/n
</span><span style="mso-fareast-language:ES"><a
href="www.itccanarias.org" title="www.itccanarias.org"
moz-do-not-send="true"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:blue">www.itccanarias.org</span></a></span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES"><o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">35119-
Santa Lucía, Las Palmas
</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;mso-fareast-language:ES"><a
href="mailto:glopez@itccanarias.org"
moz-do-not-send="true"><span style="color:#0563C1">glopez@itccanarias.org</span></a><u><span
style="color:navy"><o:p></o:p></span></u></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">+34
928 727 545 (Tel)
<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">+34
928 379 940 (Tel.2)
<o:p></o:p></span></p>
<p class="MsoNormal"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">+34
928 727 590/ (Fax)
<o:p></o:p></span></p>
<div class="MsoNormal" style="text-align:center" align="center"><span
style="font-size:10.0pt;font-family:"Arial",sans-serif;color:black;mso-fareast-language:ES">
<hr style="color:#009EE0" width="100%" size="2"
noshade="noshade" align="center">
</span></div>
<p class="MsoNormal" style="text-align:justify"><u><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">AVISO
LEGAL:</span></u><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">
Este mensaje y los ficheros adjuntos si los hubiere, se
dirigen exclusivamente a la persona destinataria y puede
contener información privilegiada o confidencial. La
transmisión errónea del presente mensaje en ningún momento
supone renuncia a su confidencialidad. Si no es vd. la
persona indicada, queda notificada de que la utilización,
divulgación y/o copia sin autorización está prohibida en
virtud de la legislación vigente. Si ha recibido este
mensaje por error, le rogamos que nos lo comunique
inmediatamente por esta misma vía y proceda a su
destrucción.</span><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES"><o:p></o:p></span></p>
<p class="MsoNormal" style="text-align:justify"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES"><o:p> </o:p></span></p>
<p class="MsoNormal" style="text-align:justify"><u><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">LPD:</span></u><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">
Sus datos personales serán tratados por INSTITUTO
TECNOLOGICO DE CANARIAS, S.A. (ITC), con dirección en la C/
Cebrián, nº 3, 35003, Las Palmas de G.C., 928 379 900, y con
la finalidad de gestionar las comunicaciones realizadas a
través del correo electrónico de los servicios prestados,
información comercial o de las actividades realizadas por la
persona responsable. La base jurídica que legitima el
tratamiento es el consentimiento de la persona interesada o
la ejecución o desarrollo de un contrato. Sus datos serán
conservados indefinidamente mientras no revoque el
consentimiento prestado o solicite la cancelación/supresión
de sus datos o la oposición al tratamiento. No se cederán
datos a terceros, salvo obligación legal.<o:p></o:p></span></p>
<p class="MsoNormal" style="text-align:justify"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES"><o:p> </o:p></span></p>
<p class="MsoNormal" style="text-align:justify"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">Podrá
revocar su consentimiento, así como ejercer sus derechos de
acceso, rectificación, cancelación/supresión, oposición,
limitación y portabilidad a través de correo postal a la
dirección indicada anteriormente o por correo electrónico a
la dirección
<a href="mailto:lpd@itccanarias.org" moz-do-not-send="true"><span
style="color:navy">lpd@itccanarias.org</span></a>.
Asimismo, si considera que sus datos han sido tratados de
forma inadecuada podrá presentar una reclamación ante la
Agencia Española de Protección de Datos.<o:p></o:p></span></p>
<p class="MsoNormal" style="text-align:justify"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES"><o:p> </o:p></span></p>
<p class="MsoNormal" style="text-align:justify"><span
style="font-size:7.5pt;font-family:"Arial",sans-serif;color:navy;mso-fareast-language:ES">Puede
consultar/solicitar información ampliada sobre protección de
datos en
<a href="http://www.itccanarias.org/web/lopd.jsp?lang=es"
moz-do-not-send="true"><span style="color:navy">Política
de privacidad</span></a> o remitir un correo a
<u><a href="mailto:lpd@itccanarias.org"
moz-do-not-send="true"><span style="color:navy">lpd@itccanarias.org</span></a></u><o:p></o:p></span></p>
<p class="MsoNormal"><o:p> </o:p></p>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>