<div dir="ltr">I just realised that my heat pump outlet source temperature is changing between 4 and -1.2 degree as you see in the new clear picture.<br>When I do not use the control system, the output source temperature remained as -1.2 degree(heat pump always turn on) . When I use the control system, the output temperature varied. I think everything is normal. <br><br>I m sorry to hurry up and sent the mail.<br>Regards<br><div><div><img src="cid:ii_k06mfqam2" alt="heatpump2.jpg" width="472" height="295"><div><img src="cid:ii_k06mfqb73" alt="heat1.jpg" width="472" height="295"><br></div></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">Jeff Thornton via TRNSYS-users <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>>, 5 Eyl 2019 Per, 04:43 tarihinde şunu yazdı:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><u></u>
<div>
<p>Emre,</p>
<p>No it's not normal for the outlet temperature to be the inlet temperature - unless there is no heat transfer going on. Did you turn the heat pump and the pump on? Did you plot the energy flows from the heat pump to see what they show? It's hard to see your plot but if the pump temperature in pink is being plotted, and it's the same temperature as the outlet temperature in red, then the pink line would totally cover the red line - which doesn't look like it's happening....</p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---<br>Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
<a href="http://www.tess-inc.com" target="_blank">www.tess-inc.com</a>
E-Mail: <a href="mailto:thornton@tess-inc.com" target="_blank">thornton@tess-inc.com</a>
</pre>
</div>
<p>On 09/04/2019 1:13 pm, Emre Arpaci via TRNSYS-users wrote:</p>
<blockquote type="cite" style="padding-left:5px;border-left:2px solid rgb(16,16,255);margin-left:5px">
<div dir="ltr">hello trnsys users
<div>I m heating a greenhouse with water source heat pump as you see in the figure.</div>
<div>I m using a lake as the heat source ( open loop system)</div>
<div>my heat pump values are there</div>
<div> </div>
<div>Rated heating capacity : 58120 kj/hr</div>
<div>rated heating power : 15120 kj/hr </div>
<div>inlet source flowrate : 1700 kg/hr</div>
<div>inlet load flowrate : 2600 kg/hr</div>
<div> </div>
<div>and my lake montly temperatures</div>
<div>january : 4 santigrad degree</div>
<div>february :5</div>
<div>march : 6 ...etc.</div>
<div> </div>
<div>so my question is that my heat pump output source temperature and the inlet source temperature are same, is this normal ? </div>
<div> </div>
<div>I thınk the output source temperature should be less than inlet source temperature( 4 degrees and changing montly ). because the source energy is absorbed in heating mode.</div>
<div> </div>
<div>thanks </div>
<div>
<div><img src="cid:16d013b9f7457ae84612" alt="heatpmp1.jpg" width="452" height="283">
<div><img src="cid:16d013b9f7357bc9be21" alt="heatpmp2.jpg" width="452" height="283"></div>
</div>
</div>
<div> </div>
</div>
<br>
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</div>
_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
</blockquote></div>