<!DOCTYPE html PUBLIC "-//W3C//DTD XHTML 1.0 Transitional//EN">
<html><body>
<p>Yeyson,</p>
<p>The reason the outlet temperatures are different is that in the first project you have a pump and a controller to modulate the flow through the ground heat exchanger.  In the second project you have no flow...</p>
<p>The error you refer to is that Type 99 cannot read the external data file.  Double click on the External Files tab of Type 99 and select the file it's supposed to be reading.</p>
<p>I would suggest that you carefully review the example projects and tutorials provided with TRNSYS as they can provide a lot of good examples to help you through these basic problems.</p>
<p> </p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---<br />Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577  Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton@tess-inc.com
</pre>
</div>
<p>On 08/20/2019 10:33 am, Yeyson Meza via TRNSYS-users wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->
<div dir="ltr">Hello Mr. <span style="white-space: pre-wrap;">Jeff Thornton, firstly I revise your comment about type 997, This type </span>model allows the user to specify groundwater flows through a horizontal layer of soil, I try to fix this error. On the other hand, I copied the type and pegged in another project (Fig 1), but I have this problem when running the project the outlet temperature is very different from the original (Fig 2 and 3), the performance is totally different. As another option, I copied the whole project, all Type, and pegged this information in the window for the second project, but I have this problem and I don´t understand (Fig 3), why is this happening? 
<div><br />
<div>Figure 1. Copy and page only the type and connect to the input building.</div>
<div>
<div><img src="cid:ebe83b4796403c83e36ba8093df621c6@tess-inc.com" alt="image.png" width="562" height="368" /></div>
</div>
<div> </div>
<div>Figure 2. The outlet temperature of EAHE in the project of figure 1.</div>
<div>
<div><img src="cid:ebe83b4796403c83e36ba8093df621c6@tess-inc.com" alt="image.png" width="562" height="292" /></div>
</div>
<div> </div>
<div>Figure 3. The outlet temperature of EAHE in the original project.</div>
<div>
<div><img src="cid:ebe83b4796403c83e36ba8093df621c6@tess-inc.com" alt="image.png" width="562" height="289" /></div>
</div>
<div> </div>
<div> </div>
<div>Figure 4. Another option to copy and page and this error. </div>
<div>
<div><img src="cid:ebe83b4796403c83e36ba8093df621c6@tess-inc.com" alt="image.png" width="562" height="330" /></div>
</div>
</div>
</div>
<br />
<div class="gmail_quote">
<div class="gmail_attr" dir="ltr">El mar., 20 de ago. de 2019 a la(s) 09:57, Yeyson Meza (<a href="mailto:yeyson.meza90@gmail.com">yeyson.meza90@gmail.com</a>) escribió:</div>
<blockquote class="gmail_quote" style="margin: 0px  0px  0px  0.8ex; border-left: 1px  solid rgb; padding-left: 1ex;">
<div dir="ltr">
<p>Hello Mr. <span style="white-space: pre-wrap;">Jeff Thornton, firstly I revise your comment about type 997, This type </span>model allows the user to specify groundwater flows through a horizontal layer of soil, I try to fix this error. On the other hand, I copied the type and pegged in another project but I have this problem (Fig 1), the outlet temperature </p>
</div>
<br />
<div class="gmail_quote">
<div class="gmail_attr" dir="ltr">El lun., 19 de ago. de 2019 a la(s) 20:33, <<a href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a>> escribió:</div>
<blockquote class="gmail_quote" style="margin: 0px  0px  0px  0.8ex; border-left: 1px  solid rgb; padding-left: 1ex;">Send TRNSYS-users mailing list submissions to<br />         <a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a><br /><br /> To subscribe or unsubscribe via the World Wide Web, visit<br />         <a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br /><br /> or, via email, send a message with subject or body 'help' to<br />         <a href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a><br /><br /> You can reach the person managing the list at<br />         <a href="mailto:trnsys-users-owner@lists.onebuilding.org">trnsys-users-owner@lists.onebuilding.org</a><br /><br /> When replying, please edit your Subject line so it is more specific<br /> than "Re: Contents of TRNSYS-users digest..."<br /> Today's Topics:<br /><br />    1. Re:  How can I take datas the one widows TRNSYS to another?<br />       (Jeff Thornton)<br /><br /><br /><br />---------- Forwarded message ----------<br />From: Jeff Thornton <<a href="mailto:thornton@tess-inc.com">thornton@tess-inc.com</a>><br />To: "TRNSYS users mailing list at OneBuilding.org" <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>><br />Cc: <br />Bcc: <br />Date: Mon, 19 Aug 2019 19:55:40 -0500<br />Subject: Re: [TRNSYS-users]  How can I take datas the one widows TRNSYS to another?<br /><span style="text-decoration: underline;"></span>
<div>
<p>Dear Yeson Meza,</p>
<p>If I understand your question, you can simply click on the proforma of the Type 997 model in your project and then select copy.  Then activate the window for the second project and select paste.  But I do have to point out that Type 997 is NOT intended to be an earth-to-air heat exchanger.  Type 997 assumes a liquid inside of the pipes and not air!  There are earth-to-air heat exchangers available from 3rd party vendors.</p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---<br />Jeff Thornton
President - TESS LLC
3 N. Pinckney Street, Suite 202, Madison WI USA 53703
Office: (608) 274-2577  Fax: (608) 278-1475
<a href="http://www.tess-inc.com">www.tess-inc.com</a>
E-Mail: <a href="mailto:thornton@tess-inc.com">thornton@tess-inc.com</a>
</pre>
</div>
<p>On 08/19/2019 9:13 am, Yeyson Meza via TRNSYS-users wrote:</p>
<blockquote style="padding-left: 5px; border-left: 2px  solid rgb; margin-left: 5px;">
<div dir="ltr"><span style="font-family: arial,sans-serif;">Hello Master, Please I need to help me. I am simulating an </span><span style="font-family: arial,sans-serif;">Earth to Air Heat Exchanger with specific features, I finished it and I obtained the results, but in the other project, I simulated an office building. I want to know how to take the EAHE results and to apply in the building if this is in other windows. Is there a type that imported the information? or It's possible to copy the 997 EAHE type in the other project and <span class="gmail-m_5105279442076412573gmail-m_-1261334142808947227gmail-il">TRNSYS</span> recognizes the same characteristics. For more information, I attach the figures. Thanks. </span>  
<div> </div>
<div>
<div><img src="cid:ebe83b4796403c83e36ba8093df621c6@tess-inc.com" alt="image.png" width="452" height="269" /></div>
<div>
<div><img src="cid:ebe83b4796403c83e36ba8093df621c6@tess-inc.com" alt="image.png" width="452" height="271" /></div>
</div>
<div> </div>
-- <br />
<div class="gmail-m_5105279442076412573gmail-m_-1261334142808947227gmail_signature" dir="ltr">
<div dir="ltr"><span style="color: #351c75;"><strong>Ing. Yeyson Meza Moreno</strong></span>
<div><span style="color: #351c75;"><strong>Universidad Industrial de Santander<br /></strong></span>
<div><span style="color: #351c75;"><strong>Cel: 3013672740</strong></span></div>
</div>
</div>
</div>
</div>
</div>
<br />
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</div>
_______________________________________________<br /> TRNSYS-users mailing list<br /><a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a><br /><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a></blockquote>
</div>
<br clear="all" />
<div> </div>
-- <br />
<div class="gmail-m_5105279442076412573gmail_signature" dir="ltr">
<div dir="ltr"><span style="color: #351c75;"><strong>Ing. Yeyson Meza Moreno</strong></span>
<div><span style="color: #351c75;"><strong>Universidad Industrial de Santander<br /></strong></span>
<div><span style="color: #351c75;"><strong>Cel: 3013672740</strong></span></div>
</div>
</div>
</div>
</blockquote>
</div>
<br clear="all" />
<div> </div>
-- <br />
<div class="gmail_signature" dir="ltr">
<div dir="ltr"><span style="color: #351c75;"><strong>Ing. Yeyson Meza Moreno</strong></span>
<div><span style="color: #351c75;"><strong>Universidad Industrial de Santander<br /></strong></span>
<div><span style="color: #351c75;"><strong>Cel: 3013672740</strong></span></div>
</div>
</div>
</div>
<br />
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</body></html>