    <p>Mohammad,</p>
    <p>You would have to code a new model; there is no way of merging
      Types together. <br>
    </p>
    <p>That said, I am a bit confused about your heat exchanger
      configuration. In a wrap around heat exchanger, the pipes are
      wrapped around the perimeter of the tank in a long helix shape. In
      a vertical tube bank heat exchanger, there is a bundle of tubes
      immersed in the tank and running vertically. In your case, are
      there tubes around the perimeter of the tank that run vertically?
      If so then you might look for models that say they have a mantle
      or jacket heat exchanger. If the tubes run vertically but are not
      on the perimeter then you can use Type534 with the vertical tube
      bank heat exchanger mode.</p>
    <p>Kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 08/18/2019 23:56, Mohammad
      Fakhrulrezza via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CA+BbqF-WAcACRnDZtcepnwZwd3W9b4_UigvG-se5BGP9qocxmQ@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Hello, my name is Rezza. 
        <div><br>
        </div>
        <div>Currently, I am using Trnsys 18.<br>
        </div>
        <div>I would like to know if there is a way for merging two
          component types together.</div>
        <div>The model that i want to simulate is a vertical cylinder
          that has a wrap around heat exchanger and an immersed heat
          exchanger in the arrangement of vertical tube (the number of
          tubes is 60).</div>
        <div><br>
          Therefore, in my case, I would like to merge Type 534
          (Vertical Cylindrical Storage Tank With Immersed Heat
          Exchanger) and Type 1237 (Cylindrical Storage Tank with
          Wrap-Around Heat Exchanger).</div>
        <div><br>
        </div>
        <div>Thanks.</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>