<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html;
      charset=windows-1252">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>Daniel,<br>
    </p>
    <p>Type123 does a computation to find the maximum possible heat
      transfer at the given rated conditions (air and water inlet
      temperature, air inlet humidity, air and water flow rates). It
      then compares the stated capacity to the calculated maximum. In
      the case of the parameters that you have specified below, the
      maximum possible heat transfer is being calculated as 234. kJ/h.
      However! if you reduce the total and sensible heat transfer rates
      to that value you will run into another error. <br>
    </p>
    <p>Fundamentally, the problem is that while Type123 assumes that the
      coil is either totally dry or totally wet during operation its
      basic UA calculation method is invalid if the coil's rated
      conditions are for sensible-only heat transfer. We will certainly
      work on making some better error handling for Type123. I think the
      workaround for your case would be one of two things. You can
      either give the model some rated conditions in which the total
      capacity is greater than the sensible capacity or you could simply
      use a sensible-only heat exchanger model for your cooling coil.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 07/16/2019 06:19, Hofmann, Daniel
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:AM0PR03MB389204BA79ADF982F1F868FE92CE0@AM0PR03MB3892.eurprd03.prod.outlook.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <!--[if !mso]><style>v\:* {behavior:url(#default#VML);}
o\:* {behavior:url(#default#VML);}
w\:* {behavior:url(#default#VML);}
.shape {behavior:url(#default#VML);}
</style><![endif]-->
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0cm;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:#0563C1;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
span.E-MailFormatvorlage17
        {mso-style-type:personal;
        font-family:"Calibri",sans-serif;
        color:black;
        font-weight:normal;
        font-style:normal;
        text-decoration:none none;}
.MsoChpDefault
        {mso-style-type:export-only;
        font-family:"Calibri",sans-serif;
        mso-fareast-language:EN-US;}
@page WordSection1
        {size:612.0pt 792.0pt;
        margin:70.85pt 70.85pt 2.0cm 70.85pt;}
div.WordSection1
        {page:WordSection1;}
--></style><!--[if gte mso 9]><xml>
<o:shapedefaults v:ext="edit" spidmax="1026" />
</xml><![endif]--><!--[if gte mso 9]><xml>
<o:shapelayout v:ext="edit">
<o:idmap v:ext="edit" data="1" />
</o:shapelayout></xml><![endif]-->
      <div class="WordSection1">
        <p class="MsoNormal"><span style="color:black">Hello everyone,<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US">I
            currently try to use Type 123 Cooling Coil with TRNSYS18.
            Type 123 is directly connected to the TRY2017 weather data
            reader. All other inputs to Type 123 are considered to be
            constant.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US">The
            rated parameter values are measured values and do not
            include any dehumidification.
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><img style="width:6.3333in;height:2.7395in"
            id="Grafik_x0020_1"
            src="cid:part1.8E2D7B33.B5134059@tess-inc.com" class=""
            width="608" height="263"><span style="color:black"
            lang="EN-US"><o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US">No
            matter whether I use humidity mode 1 or 2 and no matter
            whether I reduce the total cooling capacity to e.g. 400
            kJ/hr I always get the following error: “The referenced Unit
            has a bad parameter value. Reported information: Parameter
            #7, Reported Problem: The total cooling capacity of the coil
            is impossible at the given conditions.”
            <o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US">And
            an additional warning message is shown: “The referenced Unit
            has called the PSYCHOMETRICS routine one or more times
            during the simulation with a humidity ratio above the
            saturation humidity ratio for the given dry bulb
            temperature. The air was assumed saturated at the given dry
            bulb temperature and the humidity ratio set for this
            condition.”<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US">I
            already checked the connection between the weather data
            reader and Type 123. I also tried a simulation with constant
            input values…..there is still not difference.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US">Thus
            I think it is a bug in Type 123 or the psych subroutine.<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US">Does
            anyone have a solution or an idea what could cause the
            errors? Thanks a lot for any help!<o:p></o:p></span></p>
        <p class="MsoNormal"><span style="color:black" lang="EN-US"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="color:black;mso-fareast-language:DE">Best regards<o:p></o:p></span></p>
        <p class="MsoNormal"><span
            style="color:black;mso-fareast-language:DE"><o:p> </o:p></span></p>
        <p class="MsoNormal"><span
            style="color:black;mso-fareast-language:DE">Daniel Hofmann<br>
            <br>
          </span><o:p></o:p></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>