<div dir="ltr">David,<div>What would be the best assumption to control the ground temperature?</div><div>Regards</div><div>Michele</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, 20 Mar 2019 at 19:34, David BRADLEY <<a href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF">
    <p>Michele, <br>
    </p>
    <p>  it is a bit hard to see the picture but it looks to me as
      though the TGROUND input is unconnected and set to an initial
      value of 0. That means that your building thinks that the ground
      temperature is constantly 0C.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="gmail-m_-965019505762210355moz-cite-prefix">On 03/20/2019 03:52, Michele Vella
      wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">
        <div dir="ltr">
          <div>Hi David</div>
          <div>I checked for links between the TGround and it is not
            linked with anything. How this can be? I used the multizone
            template and entered the weather from Meteonorm files. </div>
          <div><img src="cid:169a4932a2fcb971f161" alt="image.png" width="562" height="302"><br>
          </div>
        </div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Mon, 18 Mar 2019 at 18:14,
          David BRADLEY <<a href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>> wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div bgcolor="#FFFFFF">
            <p>Michele,</p>
            <p>Check your assumptions about ground coupling. It sounds
              as though perhaps the ground temperature beneath the
              church is set to something unrealistically low.</p>
            <p>kind regards,</p>
            <p> David</p>
            <p><br>
            </p>
            <div class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-cite-prefix">On
              03/17/2019 04:52, Michele Vella via TRNSYS-users wrote:<br>
            </div>
            <blockquote type="cite">
              <div dir="ltr">Hi im modeling a church modeled as an
                atrium. But the lower part of the church is showing
                really low temperatures, in summer even difference of 10
                degrees difference from the outside. What could be the
                reason? as the upper parts of the church shows more a
                realistic results
                <div><br>
                </div>
                <div>Regards</div>
                <div>Michele Vella.</div>
              </div>
              <br>
              <fieldset class="gmail-m_-965019505762210355gmail-m_73952418516192313mimeAttachmentHeader"></fieldset>
              <pre class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-quote-pre">_______________________________________________
TRNSYS-users mailing list
<a class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a>
<a class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
            </blockquote>
            <pre class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a class="gmail-m_-965019505762210355gmail-m_73952418516192313moz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
          </div>
        </blockquote>
      </div>
    </blockquote>
    <pre class="gmail-m_-965019505762210355moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="gmail-m_-965019505762210355moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a class="gmail-m_-965019505762210355moz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a class="gmail-m_-965019505762210355moz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

</blockquote></div>