    <p>Olivier,</p>
    <p>  Make sure that the Type109 appears before Type56 in the
      component order. While you are there, make sure that the Type68
      appears after the Type109 and before Type56. Component order can
      be modified in the control cards tool (where you go to set the
      simulation start and stop times)</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 03/08/2019 10:26, Le Talave wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:21ab0de3a0be6ae19549831ff94a1360@letalave.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <p>Dear David,</p>
      <p>thank you for the advice. Unfortunatly, when I link the IA
        directly from type109, I have multiple warnings with this
        message: "Beam radiation greater than 0 occured for an  incident
        angle of   97.52 greater than 90° for orientation   6. Beam
        radiation has been set to 0.!"; and the simulation stops when
        the threshold of 30 warnings is reached.</p>
      <p>Orientation 6 is 90°/315° (south east wall). For the roof's IA,
        there are no problems if only them are linked from 109 to 56.
        When I link one or many walls, this issue happens. Certainly
        because of a mistake of mine, but I don't see what it could be.</p>
      <p>Thanks a lot for your help.</p>
      <p>Kind regards,</p>
      <p>Olivier</p>
      <p><br>
      </p>
      <p>Le 2019-03-08 16:43, David BRADLEY a écrit :</p>
      <blockquote type="cite" style="padding: 0 0.4em; border-left:
        #1010ff 2px solid; margin: 0"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->
        <p>Olivier,</p>
        <p> Almost! the AI-orientation input is asking for the angle of
          incidence of beam radiation on the surface. That should come
          directly from the weather component to Type56. You are correct
          about the other two</p>
        <p>kind regards,</p>
        <p> David</p>
        <p><br>
        </p>
        <div class="moz-cite-prefix">On 03/08/2019 08:38, Le Talave via
          TRNSYS-users wrote:</div>
        <blockquote type="cite" style="padding: 0 0.4em; border-left:
          #1010ff 2px solid; margin: 0">
          <p>Dear Trnsys community,</p>
          <p>To be sure not to make a mistake about how to plug type68
            with type56. Is it true to plug (Type68 ------>Type56):</p>
          <p>Solar Altitude Angle--------->AI-ORIENTATION- ?</p>
          <p>Shaded total rad. for surface--------->IT-ORIENTATION- ?</p>
          <p>Shaded beam rad. for surface---------->IB-ORIENTATION- ?</p>
          <p><br>
          </p>
          <p>Many thanks for your advices</p>
          <p>Best regards,</p>
          <p>Olivier</p>
          <br>
          <fieldset class="mimeAttachmentHeader"></fieldset>
          <pre class="moz-quote-pre">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org" rel="noreferrer" moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank" rel="noreferrer" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
        </blockquote>
        <pre class="moz-signature">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" rel="noreferrer" moz-do-not-send="true">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank" rel="noreferrer" moz-do-not-send="true">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com" target="_blank" rel="noreferrer" moz-do-not-send="true">http://www.trnsys.com</a></pre>
      </blockquote>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>