    <p>Michel,</p>
    <p>  This happens when TRNOpt/GenOpt picks some combination of
      values that results in a simulation error. For instance, if you
      were allowing TRNOpt to find a value of specific heat that best
      fit some data but you did not prevent the guessed values of
      specific heat from being negative then you might get this error.</p>
    <p>  The *.lst and *.log files (where the error is specified) will
      be located in:</p>
    <p> .\TrnsysXX\Optimization\GenOpt\Simulation\tmp-genopt-run-YYY</p>
    <p>Either file can be opened with a text editor.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 01/09/2019 06:28, Michel Tamarzians
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAPCNZs5H5kdHc7jaUhLej1epQXoVxiJysBpqSMoBqdEZTtpDPg@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div dir="ltr">
          <div>Hi all, <br>
          </div>
          <div><br>
          </div>
          <div>I am trying to do an optimization for my pv-hydrogen
            system to find the optimal sizing.</div>
          <div>I wanted to use the Parametric Mesh algorithm, however
            TRNOPT terminates with the following error:</div>
          <div><br>
          </div>
          <div><b>Optimization terminated with error.<br>
              <br>
              Error message:<br>
              **************<br>
              java.lang.ClassNotFoundException: <br>
              genopt.algorithm.EquMesh<br>
              Check whether file 'genopt.algorithm.EquMesh.class' is in
              the correct path.<br>
              <br>
              GenOpt terminated with error.</b></div>
          <div><br>
          </div>
          <div>Can you perhaps tell me where I have to look to find the
            correct path?? The strange thing is that the Parametric
            algorithm works just fine so it should be something with a
            path issue but I can't manage to figure out where to look.</div>
          <div><br>
          </div>
          <div>Any tip/help is appreciated.</div>
          <div>Thanks.</div>
          <div><br>
          </div>
          <div>Kind regards, <br>
          </div>
          <div>Michel Tamarzians<br>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>