    <p>Michel,</p>
    <p>  It does sound as though there is an issue with one of the
      printers or integrators resetting. Your Type55 parameters look
      okay to me. Usually Type55 feeds into a Type25 printer. Make sure
      that the print time (print interval) is set to 8769 as well (so
      long as you want only one value printed at the end of the
      simulation.)<br>
    </p>
    <p>  Another thought is that unless you have to run your simulation
      for more then a year (ie if the time has to go beyond 8769) then
      you could set all of the integrator reset times and print times to
      the variable name "STOP." STOP is a built-in variable that is the
      hour on which the simulation should end.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 12/30/2018 14:48, Michel Tamarzians
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAPCNZs46jkFktKbFsrBoc_hsits2y4RFFej_=rxrCsFc4YOMfg@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div dir="ltr">
          <div>Dear all, <br>
          </div>
          <div><br>
          </div>
          <div>I am running my simulation for one year period. Starting
            simulation time is 9 hr and stopping simulation time is 8769
            hr. However, regardless of the step time all values are
            reset to 0 around timestep of 8765 hr and above. Can someone
            please explain to me why this is happening? Because now I am
            not sure if my end values used within TRNOPT are correct for
            the optimization. Could have something to do with using Type
            24 and Type 55?</div>
          <div><b><br>
            </b></div>
          <div><b>For Type 55 I am using the following parameters:</b></div>
          <div><b><br>
            </b></div>
          <div><b>Parameter 1: Integrate or sum input-1    -1  <br>
            </b></div>
          <div><b> Parameter 2: Relative starting hour for input-1   
              0    <br>
            </b></div>
          <div><b> Parameter 3: Duration for input-1    8769   <br>
            </b></div>
          <div><b>Parameter 4: Cycle repeat time for input-1    8769   
              <br>
            </b></div>
          <div><b>Parameter 5: Reset time for input-1    8769    <br>
            </b></div>
          <div><b>Parameter 6: Absolute starting hour for input-1   
              0    <br>
            </b></div>
          <div><b>Parameter 7: Absolute stopping hour for input -1   
              8769    </b><br>
          </div>
          <div><br>
          </div>
          <div>Any kind of help is more than appreciated!</div>
          <div>Thanks in advance!</div>
          <div><br>
          </div>
          <div>Kind regards, <br>
          </div>
          <div>Michel<br>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>