<div dir="ltr"><div>Dear All</div><div><br></div><div>I'm using Trnsys 16 simulation building, but i don't know creat file building from any where.</div><div><br></div><div>Please help me!</div><div><br></div><div>Thank you.<br></div></div><br><div class="gmail_quote"><div dir="ltr">On Thu, Dec 20, 2018 at 10:56 PM David BRADLEY via TRNSYS-users <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF">
    <p>Muhammad,</p>
    <p> Can you be a bit more specific about what you mean by "transient
      state" analysis? Type1271 uses a performance map lookup method.
      Its compressor is assumed to vary its speed to maintain a constant
      outlet temperature on the load side. In that the heat pump
      compressor adjusts to the present load requirements it does do a
      transient analysis. However, if you are looking for a component
      that uses a more first principals approach and models the state of
      the refrigerant in the heat pumps heat exchangers, compressors,
      and expansion valve then I think you would need to look to a
      different Type than 1271.</p>
    <p><br>
    </p>
    <p>As a side comment, please note that Type1271 is an air (source)
      to water (load) heat pump, not an air to air heat pump. <br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <p><br>
    </p>
    <div class="gmail-m_-3788793019110407215moz-cite-prefix">On 12/20/2018 07:50, Muhammad Abid via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite">
      
      
      <div id="gmail-m_-3788793019110407215divtagdefaultwrapper" style="font-size:12pt;color:rgb(0,0,0);font-family:Calibri,Helvetica,sans-serif" dir="ltr">
        <p style="margin-top:0px;margin-bottom:0px">Hi,</p>
        <p style="margin-top:0px;margin-bottom:0px"><br>
        </p>
        <p style="margin-top:0px;margin-bottom:0px">I am a new user to
          TRNSYS from Ulster University. I would be working for my PhD
          studies on the topic of variable speed air source heat pump .
          I found this "Type 1271v2" ASHP from TESS library useful for
          me.</p>
        <p style="margin-top:0px;margin-bottom:0px"><br>
        </p>
        <p style="margin-top:0px;margin-bottom:0px">I am interested in the
          transient state analysis of the HP. Is this Type suitable for
          me or i should use some other software(like EES or Matlab) for
          the transient state analysis?</p>
        <p style="margin-top:0px;margin-bottom:0px"><br>
        </p>
        <p style="margin-top:0px;margin-bottom:0px">Best Regards</p>
      </div>
      <font size="0" face="Calibri"><br>
        <br>
        This email and any attachments are confidential and intended
        solely for the use of the addressee and may contain information
        which is covered by legal, professional or other privilege. If
        you have received this email in error please notify the system
        manager at <a class="gmail-m_-3788793019110407215moz-txt-link-abbreviated" href="mailto:postmaster@ulster.ac.uk" target="_blank">postmaster@ulster.ac.uk</a> and delete this email
        immediately. Any views or opinions expressed are solely those of
        the author and do not necessarily represent those of Ulster
        University.
        <br>
        The University's computer systems may be monitored and
        communications carried out on them may be recorded to secure the
        effective operation of the system and for other lawful purposes.
        Ulster University does not guarantee that this email or any
        attachments are free from viruses or 100% secure. Unless
        expressly stated in the body of a separate attachment, the text
        of email is not intended to form a binding contract.
        Correspondence to and from the University may be subject to
        requests for disclosure by 3rd parties under relevant
        legislation. <br>
        <b>The Ulster University was founded by Royal Charter in 1984
          and is registered with company number RC000726 and VAT
          registered number GB672390524.The primary contact address for
          Ulster University in Northern Ireland is Cromore Road,
          Coleraine, Co. Londonderry BT52 1SA</b> <br>
      </font>
      <br>
      <fieldset class="gmail-m_-3788793019110407215mimeAttachmentHeader"></fieldset>
      <pre class="gmail-m_-3788793019110407215moz-quote-pre">_______________________________________________
TRNSYS-users mailing list
<a class="gmail-m_-3788793019110407215moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a>
<a class="gmail-m_-3788793019110407215moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <pre class="gmail-m_-3788793019110407215moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="gmail-m_-3788793019110407215moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a class="gmail-m_-3788793019110407215moz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a class="gmail-m_-3788793019110407215moz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div>

_______________________________________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br>
</blockquote></div><br clear="all"><br>-- <br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><span style="color:rgb(0,0,255)"><font size="4"><cite></cite></font></span></div><div style="text-align:center"><div style="text-align:left"><span style="color:rgb(0,0,255)"><b>Nguyen Huu Hoang</b></span></div><div style="text-align:left"><span style="color:rgb(0,0,255)"><b></b></span><br></div><div style="text-align:left"><span style="color:rgb(0,0,0)"><font size="2"><span style="font-weight:bold;display:inline"></span></font></span></div><div style="text-align:left"><span style="color:rgb(0,0,0)"><font size="2"><span style="font-weight:bold;display:inline"></span></font></span><span style="color:rgb(0,0,0)"><font size="2"><span style="font-weight:bold;display:inline"></span><span style="color:rgb(0,0,255)"><b>Thermal Power Plant Engineering<br></b></span></font></span></div><div style="text-align:left"><span style="color:rgb(0,0,0)"><font size="2"><span style="color:rgb(0,0,255)"><b>Email: <a href="mailto:nguyenhuuhoang@gmail.com" target="_blank">nguyenhuuhoang@gmail.com</a></b></span></font></span><br><span style="display:inline"><span style="color:rgb(0,0,255)"><font size="2"><b>Mobile: +84 (0)986224282</b></font></span></span><br></div><div style="text-align:left"><span style="display:inline"></span></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div>