    <p>Behzad,</p>
    <p>  You have caught the most common error (too long a time step)
      and I must admit that I am not sure why reducing the timestep so
      far did not make the simulation start converging again. The reason
      that reducing the time step helps is that if you have pumps (or
      fans) that are pushing a greater volume of fluid around a loop in
      one time step than the devices that have thermal capacitance can
      hold then the problem can become numerically unstable. Devices
      that have thermal capacitance are storage tanks, pipes, and the
      building (if there is one). <br>
    </p>
    <p>  I think you'll need to use the TRACE tool (the icon with the
      foot prints in the toolbar on the left of the simulation studio).
      Activate TRACE on the components that are being flagged as not
      converging in the error/warning log. What TRACE does is to write
      the values of all the parameters, inputs, and outputs for each of
      the activated components to the *.lst file at every iteration. By
      looking at the outputs and inputs from one iteration to the next,
      you can tell specifically which one(s) are causing problems.
      Unfortunately TRACE writes a lot of information to the *.lst file
      and it can be a bit hard to find what you are looking for.
      However, it is a handy tool in cases like this. <br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 12/10/2018 08:17, up201700037 via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:5b184da2aac582485aa82b0837368c83@fe.up.pt">Dear Users,
      <br>
      <br>
      I am simulating a building which is cooled or heated by heat
      generated by sollar collectors and stored in Stratified tank
      type4. The simulation goes well with 6oo liters volume of the
      tank. Then i decided to reduced the size of the tank to reach an
      optimum volume. I tried for the cases of 500 to 100 liters and got
      the results but when reducing the volume to 50 liters the
      simulation diverges because of many warnings stating that many
      types in the simulation did not converge at this time step(30s).
      Therefore, i decided to decrease the timestep. I repeated the
      simulation even for the least time stem defined in trnsys but it
      did not converge. I also tried to change the relaxation factor but
      didnt work. I read that some people suggest that if i increase the
      convergence criteria or the limit number for warnings in the
      control cards, it will converge but it is not solving the problem.
      Actually it seems like cheating. Please help me to solve the
      problem.
      <br>
      <br>
      Best regards,
      <br>
      Behzad shahzamanian sichani
      <br>
      _______________________________________________
      <br>
      TRNSYS-users mailing list
      <br>
      <a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
      <br>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
      <br>
      <br>
    </blockquote>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>