<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>Alexandros,</p>
    <br>
    <blockquote type="cite"
      cite="mid:8d58aeda-8076-efa7-2517-5ea67c1ba38c@uth.gr">1.    Type
      107 and Type680 use a normalized catalog data which has limited
      values for Inlet Hot Water Temperature (from 108.89 (C) to 116.11
      (C)), Entering Cooling Water Temperature (from 26.667 (C) to
      32.222 (C)), Chilled Water Set point (from 5.556 (C)to 10.000
      (C)). Ιf we use values outside this range, do we get wrong
      results?
      <br>
    </blockquote>
    possibly. As it mentions in the documentation the components can
    interpolate within the data range given but they cannot extrapolate
    beyond the range. You'll get a notice as to how much of the time the
    components called the data files outside the range. If it happens
    rarely then I would not worry about the consequences. If it is
    happening all the time then the system needs to be better controlled
    or alternative data (with a wider range) is needed. <br>
    <blockquote type="cite"
      cite="mid:8d58aeda-8076-efa7-2517-5ea67c1ba38c@uth.gr">
      2.    Τhe energy is discharged into the cooling water stream. If
      we want energy rejection to be done in the air, can we achieve it
      by changing the value of cp?
      <br>
    </blockquote>
    I would not recommend doing so. Since the COP of the device is
    looked up from a data file, the effectiveness of the rejection heat
    exchanger is built-in to the performance data file. If the data
    comes from a machine that rejects energy to a water stream then the
    effectiveness built into the COP is that of a brine to water heat
    exchanger. A brine to air heat exchanger would presumably have a
    different effectiveness and therefore a different COP. <br>
    <br>
    In most applications that I have seen the cooling water stream goes
    to a cooling tower where the energy us then rejected to the air. If
    you have a device that rejects directly to air I would try very hard
    to get its performance data and then yes, change the Cp of the
    rejection stream. If you have a device that rejects to a water
    stream and then to a cooling tower I would model it as such. <br>
    <blockquote type="cite"
      cite="mid:8d58aeda-8076-efa7-2517-5ea67c1ba38c@uth.gr">
      3.    Which working pair ( LiBr-H2O, H2O-NH3 ) is it used in the
      data file? Ηow can we study the effect of the concentration in the
      chilled power?
      <br>
    </blockquote>
    I do not recall what brine was used in the example machine. If I had
    to guess, I would say that it was LiBr-H2O. You cannot examine the
    effect of the brine concentration on performance because performance
    is read from a data file. If you have more than one data file (one
    for a high concentration and one for a lower concentration) then you
    could examine such a modification in the context of the system.<br>
    <blockquote type="cite"
      cite="mid:8d58aeda-8076-efa7-2517-5ea67c1ba38c@uth.gr">
      4.    The single effect hot water fired absorption chiller is used
      to solve energy balances between hot water, cooling water, chilled
      water, auxiliary electrical power. A more detailed analysis is it
      possible?
      <br>
    </blockquote>
    No, not really because this is a catalog data lookup table model.
    You'd need to find (or write) a first principals model of the device
    if you want to do a more detailed analysis.<br>
    <br>
    kind regards,<br>
     David<br>
    <br>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>