<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p><span style="font-family:verdana;font-weight:normal;
        font-size:12px;">Noortje,</span></p>
    <p><span style="font-family:verdana;font-weight:normal;
        font-size:12px;">  There is another alternative as well, which
        is Type1267. It is a finite difference model that we wrote to
        really dig into the coupling between buildings and the
        surrounding ground. It is somewhat tricky to set up and it runs
        slowly, however, it can model almost any configuration you want.
        You can set up basements, partial basements (ie where the ground
        slopes), etc. You can also embed pipes in the soil or in the
        slab. Essentially what you are doing in this case is taking the
        floor model out of Type56 and using this finite difference
        approach which does not rely on transfer functions and does not
        have a time base. </span><span
        style="font-family:verdana;font-weight:normal; font-size:12px;"><span
          style="font-family:verdana;font-weight:normal;
          font-size:12px;">The one thing that might be tricky for it is
          to deal with a situation where you've got a radiant slab
          between two floors in the building (as opposed to in a floor
          that has some combination of insulation and soil on the back
          side of it).</span></span></p>
    <p><span style="font-family:verdana;font-weight:normal;
        font-size:12px;"><span
          style="font-family:verdana;font-weight:normal;
          font-size:12px;">David</span></span></p>
    <p><span style="font-family:verdana;font-weight:normal;
        font-size:12px;"><span
          style="font-family:verdana;font-weight:normal;
          font-size:12px;"><br>
        </span> </span></p>
    <br>
    <div class="moz-cite-prefix">On 09/11/2018 09:33, Noortje Alders
      wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:76ae74f7-582b-7bbb-5530-f45f62e4f7d2@peutz.nl">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <p><font face="Verdana">Dear David,</font></p>
      <p><font face="Verdana">Thank you for your answer. This is
          actually what I expected but hoped not to be the case. I think
          the energy consumption of the building can be calculated
          reliably; however, I would like to study the behaviour of the
          floor heating in more detail. I guess I have to decide from
          situation to situation which time-base to use, as the higher
          the time-constant (the slower the system), the less the
          time-base matters. <br>
        </font></p>
      <div class="moz-signature"><span
          style="font-family:verdana;font-weight:normal;
          font-size:12px;"> Met vriendelijke groet,<br>
          Noortje Alders<br>
          <br>
        </span> <img src="cid:part1.D0A8F685.8955BC8A@tess-inc.com"
          class=""><br>
        <span style="font-family:verdana;font-weight:normal;
          font-size:12px;"> Postbus 696<br>
          2700 AR Zoetermeer<br>
          T: 079 3470309<br>
          E: <a class="moz-txt-link-abbreviated"
            href="mailto:n.alders@peutz.nl" moz-do-not-send="true">n.alders@peutz.nl</a><br>
          W: <a class="moz-txt-link-abbreviated"
            href="http://www.peutz.nl" moz-do-not-send="true">www.peutz.nl</a>
          <hr> </span> </div>
      <div class="moz-cite-prefix">Op 11-09-2018 om 16:02 schreef David
        BRADLEY:<br>
      </div>
      <blockquote type="cite"
        cite="mid:4d6cc40d-03e6-6929-9903-4f4082ae7ee6@tess-inc.com">
        <meta http-equiv="Content-Type" content="text/html;
          charset=utf-8">
        <p><span style="font-family:verdana;font-weight:normal;
            font-size:12px;">Noortje,</span></p>
        <p><span style="font-family:verdana;font-weight:normal;
            font-size:12px;">  The time base has to do with how often
            the wall transfer functions are updated. The time base is
            distinct from the simulation time step and while it is ideal
            to have the time base and the time step be equal, it is
            rarely possible. Ventilation and occupancy changes occur as
            a function of the simulation time step. You'll see some
            stepwise behavior in the room air temperature if your time
            step and time base are different but in my experience this
            does not lead to significant problems in computing either
            the comfort or the energy consumption of the building. I
            often have situations in which I use a 1-5 minute time step
            and have to use a 1 hour wall time base in the building.</span></p>
        <p><span style="font-family:verdana;font-weight:normal;
            font-size:12px;">kind regards,</span></p>
        <p><span style="font-family:verdana;font-weight:normal;
            font-size:12px;"> David</span></p>
        <p><span style="font-family:verdana;font-weight:normal;
            font-size:12px;"><br>
          </span></p>
        <br>
        <div class="moz-cite-prefix">On 09/11/2018 03:12, Noortje Alders
          via TRNSYS-users wrote:<br>
        </div>
        <blockquote type="cite"
          cite="mid:2befcd3a-0368-9007-8c83-2e13e978a912@peutz.nl">
          <meta http-equiv="content-type" content="text/html;
            charset=utf-8">
          <p><font face="Verdana">Dear TRNSYS users,</font></p>
          <p><font face="Verdana">I want to analyze the thermal
              behaviour of a dwelling with floor heating in detail.
              Attatched is a drawing of the floor construction. The
              time-base is set by 1 hour by default. I would like to set
              this time-base to a lower value (eg 15 minutes or less) to
              be able to analyse the reaction to change in occupancy
              with accordingly changing ventilation, heating setpoint
              and internal gain. However, the high thermla mass and high
              insulation value doesn't allow me to because the stability
              criteria are not fullfilled. ("Error creating the wall
              transfer coefficients: Stability criteria not
              fullfilled"). In a previous thread of the forum ( </font><br>
            <font face="Verdana"><font face="Verdana"><a
                  class="moz-txt-link-freetext"
href="http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/2012-November/024387.html"
                  moz-do-not-send="true">http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/2012-November/024387.html</a>
                ) I read that there is a "trick" for this. You can
                devide one layer in the ground floor (e.g. the concrete
                slab) with an active layer. However, if I try I get the
                message that only one active layer is allowed. Is there
                another way to tackle this problem?</font></font></p>
          <p><font face="Verdana">Kind regards,</font><br>
          </p>
          <div class="moz-signature"><span
              style="font-family:verdana;font-weight:normal;
              font-size:12px;"> Met vriendelijke groet,<br>
              Noortje Alders<br>
              <br>
            </span> <img src="cid:part1.D0A8F685.8955BC8A@tess-inc.com"
              class=""><br>
            <span style="font-family:verdana;font-weight:normal;
              font-size:12px;"> Postbus 696<br>
              2700 AR Zoetermeer<br>
              T: 079 3470309<br>
              E: <a class="moz-txt-link-abbreviated"
                href="mailto:n.alders@peutz.nl" moz-do-not-send="true">n.alders@peutz.nl</a><br>
              W: <a class="moz-txt-link-abbreviated"
                href="http://www.peutz.nl" moz-do-not-send="true">www.peutz.nl</a>
              <hr> </span> </div>
          <br>
          <a href="http://www.peutz.nl/index.php?pageid=109"
            moz-do-not-send="true">Klik hier</a> om u aan te melden op
          de Peutz Actueel<br>
          <a href="http://www.peutz.nl/index.php?pageid=105"
            moz-do-not-send="true">Klik hier</a> voor het
          cursusoverzicht van Peutz Academy<br>
          E-MAIL DISCLAIMER: <a
            href="http://www.peutz.nl/disclaimer/emaildisclaimer.html"
            moz-do-not-send="true">http://www.peutz.nl/disclaimer/emaildisclaimer.html</a>
          <br>
          <fieldset class="mimeAttachmentHeader"></fieldset>
          <br>
          <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org" moz-do-not-send="true">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" moz-do-not-send="true">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
        </blockquote>
        <br>
        <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" moz-do-not-send="true">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com" moz-do-not-send="true">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com" moz-do-not-send="true">http://www.trnsys.com</a></pre>
      </blockquote>
      <br>
      <br>
      <a href="http://www.peutz.nl/index.php?pageid=109"
        moz-do-not-send="true">Klik hier</a> om u aan te melden op de
      Peutz Actueel<br>
      <a href="http://www.peutz.nl/index.php?pageid=105"
        moz-do-not-send="true">Klik hier</a> voor het cursusoverzicht
      van Peutz Academy<br>
      E-MAIL DISCLAIMER: <a
        href="http://www.peutz.nl/disclaimer/emaildisclaimer.html"
        moz-do-not-send="true">http://www.peutz.nl/disclaimer/emaildisclaimer.html</a>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>