    <p>berkane ahlem</p>
    <p>It is a little hard to answer without knowing the larger story of
      what you are trying to model. Type668 models a single speed
      compressor heat pump and the model computes power consumption as
      an output. If your system is one in which a power source charges a
      battery that is then used to run a heat pump then you could
      accomplish such a thing using Type668, controllers, and equations.
      If, on the other hand, your heat pump can run on a variable amount
      of power (for instance it may have a variable speed compressor in
      it so that it runs as much as it can given the input power
      availability) then you'd need to write a new heat pump model.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 08/08/2018 03:34, berkane ahlem via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CACC+vA7N9d7kVwcXjWP7+owUserf90RbyZmTiKo_3mzgzZpfpg@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=utf-8">
      <p dir="ltr">Hello everyone ,<br>
         I would like to ask, how can i controled the power consumption
        by compressor, i use type 668 water to water heat pump<br>
        Thank you</p>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>