<p>Berkane,</p>
<p>The heat pump is also doing DHW and there are losses to the ground from the floor.  If you've connected things correctly, the energy should always balance...</p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---<br />Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577  Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton@tess-inc.com
</pre>
</div>
<p>On 08/01/2018 2:39 pm, Domenico Mazzeo via TRNSYS-users wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->
<div dir="auto">Hello,
<div dir="auto">I believe that it depends on the set point temperature fixed in the calculation of the energy needs and on the temperatures reached every hour in the building. My idea is that in the simulation with the heat pump, the air temperature in the building is not the same of that set in the simulation performed for the energy needs calculation</div>
<div dir="auto">Regards</div>
</div>
<br />
<div class="gmail_quote">
<div dir="ltr">Il Mer 1 Ago 2018, 21:04 berkane ahlem via TRNSYS-users <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>> ha scritto:</div>
<blockquote class="gmail_quote" style="margin: 0  0  0  .8ex; border-left: 1px  #ccc  solid; padding-left: 1ex;">
<p dir="ltr">Hello,sirs<br /> I simulate a ground source heat pump system for heating a DHWand building, the heating load of building was <strong><em>5019kwh</em></strong>/year,i use a heat pump with capacity 8kw , and i use the relation q=mcp(Tin-Tout) to calculate energy delivered to the radiant floor and i found <strong>14711,6kwh/</strong>year .I did not understand this result , building Just needs 5019kwh/year <br /> Thank you</p>
_______________________________________________<br /> TRNSYS-users mailing list<br /><a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a><br /><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a></blockquote>
</div>
<br />
<div style="font-size: 1.3em;">-------------------------------------------------------------------------------</div>
<div><span style="font-family: Arial, Helvetica, sans-serif;">Il banner è generato automaticamente dal servizio di posta elettronica dell'Università della Calabria</span></div>
<div><a href="http://www.unical.it/ammissione"><img src="cid:c852808670b80775594e12cbe87d732f@tess-inc.com" alt="" /></a></div>
<br />
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</body></html>