    <p>There is not a way of adding those inputs or outputs to Type56.
      Instead you have to determine how the energy in the water coming
      from the heat pump is transferred to the zone. Is it by a
      radiator? By a fan coil? Does it go to a radiant floor? You'll
      need to define the delivery device as another Type in your
      project. If energy is delivered by an air stream then in TRNBuild
      you'll need to define a VENTILATION with temperature, flow rate,
      and RH as inputs. If energy is delivered by a radiant floor then
      you'll need to define an active layer in the floor of your
      building in TRNBuild.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 05/18/2018 08:19, berkane ahlem via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CACC+vA7Jh7BTbMpzNxwB_nEQjr8_cFs67Rc4h27tLd9tk32uyg@mail.gmail.com">
      <p dir="ltr">Hello sirs,<br>
        how can i add in the input and <u>output</u> of type 56 the
        water (<u>flow</u>,temperater) caming from heat pump<br>
        Thank you</p>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>