<div dir="ltr">Dear Christoph,<div><br></div><div>Thanks for the reply, I tried with that output (QSIAB), and also I tried the QIBAB and QIDAB for the same surface (the ground floor), but I get the same value on QIDAB as in QSIAB, meaning that all the incident radiation is diffuse. Am I right? Is there a need to adjust some parameter? I saw something about GEOSURF parameter, but I do not have it clear how to justifiy what number to put there. </div><div><br></div><div>The multiplication of the Global Radiation by the Transmisivity of the cover it was just a simplification that crossed my mind, but if one output give me a better result, I will not follow that methodology. </div><div><br></div><div>Best,</div><div>Mario<br><div class="gmail_extra"><br><div class="gmail_quote">2018-04-24 8:03 GMT-05:00  <span dir="ltr"><<a href="mailto:trnsys-users-request@lists.onebuilding.org" target="_blank">trnsys-users-request@lists.onebuilding.org</a>></span>:<br><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><br><br>---------- Mensaje reenviado ----------<br>From: hotline <<a href="mailto:hotline@transsolar.com">hotline@transsolar.com</a>><br>To: "TRNSYS users mailing list at OneBuilding.org" <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>><br>Cc: <br>Bcc: <br>Date: Tue, 24 Apr 2018 11:44:31 +0000<br>Subject: Re: [TRNSYS-users] Incident solar radiation on greenhouse ground<br>





<div lang="DE">
<div class="gmail-m_5648491547702098783WordSection1">
<p class="MsoNormal"><span>Dear Mario,<u></u><u></u></span></p>
<p class="MsoNormal"><span><u></u> <u></u></span></p>
<p class="MsoNormal"><span>surface output 79 (QSIAB: solar (direct+diffuse) radiation being absorbed at inside surface) is the one you are looking for.<u></u><u></u></span></p>
<p class="MsoNormal"><span>What do you want to achieve exactly by
</span>multipling the Global Radiation by the Transmisivity of the cover?<span><u></u><u></u></span></p>
<p class="MsoNormal"><span><u></u> <u></u></span></p>
<p class="MsoNormal"><span>Best,<u></u><u></u></span></p>
<p class="MsoNormal"><span>Christoph<u></u><u></u></span></p>
<p class="MsoNormal"><span><u></u> <u></u></span></p>
<p class="MsoNormal"><b>Von:</b> TRNSYS-users [mailto:<a href="mailto:trnsys-users-bounces@lists.onebuilding.org" target="_blank">trnsys-users-bounces@<wbr>lists.onebuilding.org</a>]
<b>Im Auftrag von </b>Mario González via TRNSYS-users<br>
<b>Gesendet:</b> Dienstag, 24. April 2018 00:36<br>
<b>An:</b> <a href="mailto:trnsys-users@lists.onebuilding.org" target="_blank">trnsys-users@lists.<wbr>onebuilding.org</a><br>
<b>Cc:</b> Mario González <<a href="mailto:marioglezx@gmail.com" target="_blank">marioglezx@gmail.com</a>><br>
<b>Betreff:</b> [TRNSYS-users] Incident solar radiation on greenhouse ground<u></u><u></u></p>
<p class="MsoNormal"><u></u> <u></u></p>
<div>
<p class="MsoNormal">Dear TRNSYS users,<u></u><u></u></p>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">I am working on a greenhouse simulation using TRNSYS 17, and I want to know the Incident Radiation on the ground surface.<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Is there an output from TRNBuild that gives me this data? I've seen the outputs (or NTYPEs) 12 (QSOLTR), 14 and 15 (QTABS), and the  surface output 79 (QSIAB), but I am not so sure which of these is the correct one. <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Also I was thinking to just multiply the Global Radiation by the Transmisivity of the cover (simplifying a lot). <u></u><u></u></p>
</div>
<div>
<p class="MsoNormal"><u></u> <u></u></p>
</div>
<div>
<p class="MsoNormal">Thanks in advance,<u></u><u></u></p>
</div>
<div>
<p class="MsoNormal">Mario<u></u><u></u></p>
</div>
</div>
</div>
</div>

<br><br></blockquote></div></div></div></div>