<p>LiaoGang,</p>
<p> This is quite a common issue and the behavior you are seeing is
normal. The short answer to your question is: stick to using a
small time step.<br>
</p>
<p> Remember that TRNSYS iterates at each timestep to find a
converged solution if there are any control decisions to be made
then TRNSYS can make one control decision (such as turning on or
off a piece of equipment) per time step. The equipment must then
stay on (or off) for the entire duration of the next timestep. If
your time step is big then the system will be driven a long way
from where it started before the end of the time step. Imagine if
the thermostat in your home could decide to turn on heating only
once per hour. If the heating had to stay on for the entire hour
then chances are that the home would be uncomfortably hot by the
time the thermostat was allowed to make a new decision. TRNSYS
forsees this (in a way) and can't decide whether it is better to
leave the heat on or off. If you shorten the time step then the
on/off decision becomes quite a lot simpler and overheating and
undercooling become less of a problem.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<br>
<div class="moz-cite-prefix">On 04/19/2018 04:11, 廖刚 via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:32365d8f.1885.162dd2cb7f2.Coremail.163912048@csu.edu.cn">
<p class="MsoNormal"><span lang="EN-US"><span
style="mso-spacerun:yes"> </span>Dear
TRNSYS users,</span></p>
<p class="MsoNormal"
style="text-indent:5.25pt;mso-char-indent-count:.5"><span
lang="EN-US"><span style="mso-spacerun:yes"> </span>I met a
very strange problem when
I run my simulation model, I found that my model works well
when the simulation
time is relatively small, but when I increase the simulation
stop time , it
gives warning “The inputs to the listed units have not
converged at this
timestep “and then corrupted with an fatal error.</span></p>
<p class="MsoNormal"><span lang="EN-US"><span
style="mso-spacerun:yes"> </span>I
would be very appreciated if someone can help me solve this
problem,</span></p>
<p class="MsoNormal"><span lang="EN-US"><span
style="mso-spacerun:yes"> </span>Best</span></p>
<p class="MsoNormal"><span lang="EN-US">LiaoGang</span></p>
<!--[if gte mso 9]><xml>
<o:OfficeDocumentSettings>
<o:AllowPNG/>
</o:OfficeDocumentSettings>
</xml><![endif]--><!--[if gte mso 9]><xml>
<w:WordDocument>
<w:View>Normal</w:View>
<w:Zoom>0</w:Zoom>
<w:TrackMoves/>
<w:TrackFormatting/>
<w:PunctuationKerning/>
<w:DrawingGridVerticalSpacing>7.8 磅</w:DrawingGridVerticalSpacing>
<w:DisplayHorizontalDrawingGridEvery>0</w:DisplayHorizontalDrawingGridEvery>
<w:DisplayVerticalDrawingGridEvery>2</w:DisplayVerticalDrawingGridEvery>
<w:ValidateAgainstSchemas/>
<w:SaveIfXMLInvalid>false</w:SaveIfXMLInvalid>
<w:IgnoreMixedContent>false</w:IgnoreMixedContent>
<w:AlwaysShowPlaceholderText>false</w:AlwaysShowPlaceholderText>
<w:DoNotPromoteQF/>
<w:LidThemeOther>EN-US</w:LidThemeOther>
<w:LidThemeAsian>ZH-CN</w:LidThemeAsian>
<w:LidThemeComplexScript>X-NONE</w:LidThemeComplexScript>
<w:Compatibility>
<w:SpaceForUL/>
<w:BalanceSingleByteDoubleByteWidth/>
<w:DoNotLeaveBackslashAlone/>
<w:ULTrailSpace/>
<w:DoNotExpandShiftReturn/>
<w:AdjustLineHeightInTable/>
<w:BreakWrappedTables/>
<w:SnapToGridInCell/>
<w:WrapTextWithPunct/>
<w:UseAsianBreakRules/>
<w:DontGrowAutofit/>
<w:SplitPgBreakAndParaMark/>
<w:EnableOpenTypeKerning/>
<w:DontFlipMirrorIndents/>
<w:OverrideTableStyleHps/>
<w:UseFELayout/>
</w:Compatibility>
<m:mathPr>
<m:mathFont m:val="Cambria Math"/>
<m:brkBin m:val="before"/>
<m:brkBinSub m:val="--"/>
<m:smallFrac m:val="off"/>
<m:dispDef/>
<m:lMargin m:val="0"/>
<m:rMargin m:val="0"/>
<m:defJc m:val="centerGroup"/>
<m:wrapIndent m:val="1440"/>
<m:intLim m:val="subSup"/>
<m:naryLim m:val="undOvr"/>
</m:mathPr></w:WordDocument>
</xml><![endif]--><!--[if gte mso 9]><xml>
<w:LatentStyles DefLockedState="false" DefUnhideWhenUsed="false"
DefSemiHidden="false" DefQFormat="false" DefPriority="99"
LatentStyleCount="371">
<w:LsdException Locked="false" Priority="0" QFormat="true" Name="Normal"/>
<w:LsdException Locked="false" Priority="9" QFormat="true" Name="heading 1"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 2"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 3"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 4"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 5"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 6"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 7"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 8"/>
<w:LsdException Locked="false" Priority="9" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="heading 9"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 6"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 7"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 8"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index 9"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 1"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 2"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 3"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 4"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 5"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 6"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 7"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 8"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" Name="toc 9"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Normal Indent"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="footnote text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="annotation text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="header"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="footer"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="index heading"/>
<w:LsdException Locked="false" Priority="35" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="caption"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="table of figures"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="envelope address"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="envelope return"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="footnote reference"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="annotation reference"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="line number"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="page number"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="endnote reference"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="endnote text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="table of authorities"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="macro"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="toa heading"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Bullet 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Number 5"/>
<w:LsdException Locked="false" Priority="10" QFormat="true" Name="Title"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Closing"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Signature"/>
<w:LsdException Locked="false" Priority="1" SemiHidden="true"
UnhideWhenUsed="true" Name="Default Paragraph Font"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text Indent"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="List Continue 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Message Header"/>
<w:LsdException Locked="false" Priority="11" QFormat="true" Name="Subtitle"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Salutation"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Date"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text First Indent"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text First Indent 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Note Heading"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text Indent 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Body Text Indent 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Block Text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Hyperlink"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="FollowedHyperlink"/>
<w:LsdException Locked="false" Priority="22" QFormat="true" Name="Strong"/>
<w:LsdException Locked="false" Priority="20" QFormat="true" Name="Emphasis"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Document Map"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Plain Text"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="E-mail Signature"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Top of Form"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Bottom of Form"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Normal (Web)"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Acronym"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Address"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Cite"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Code"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Definition"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Keyboard"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Preformatted"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Sample"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Typewriter"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="HTML Variable"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Normal Table"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="annotation subject"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="No List"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Outline List 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Outline List 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Outline List 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Simple 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Simple 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Simple 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Classic 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Colorful 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Colorful 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Colorful 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Columns 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 6"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 7"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Grid 8"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 4"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 5"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 6"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 7"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table List 8"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table 3D effects 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table 3D effects 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table 3D effects 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Contemporary"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Elegant"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Professional"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Subtle 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Subtle 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Web 1"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Web 2"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Web 3"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Balloon Text"/>
<w:LsdException Locked="false" Priority="39" Name="Table Grid"/>
<w:LsdException Locked="false" SemiHidden="true" UnhideWhenUsed="true"
Name="Table Theme"/>
<w:LsdException Locked="false" SemiHidden="true" Name="Placeholder Text"/>
<w:LsdException Locked="false" Priority="1" QFormat="true" Name="No Spacing"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading"/>
<w:LsdException Locked="false" Priority="61" Name="Light List"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 1"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 1"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 1"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 1"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 1"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 1"/>
<w:LsdException Locked="false" SemiHidden="true" Name="Revision"/>
<w:LsdException Locked="false" Priority="34" QFormat="true"
Name="List Paragraph"/>
<w:LsdException Locked="false" Priority="29" QFormat="true" Name="Quote"/>
<w:LsdException Locked="false" Priority="30" QFormat="true"
Name="Intense Quote"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 1"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 1"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 1"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 1"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 1"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 1"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 1"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 1"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 2"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 2"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 2"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 2"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 2"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 2"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 2"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 2"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 2"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 2"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 2"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 2"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 2"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 2"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 3"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 3"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 3"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 3"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 3"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 3"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 3"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 3"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 3"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 3"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 3"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 3"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 3"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 3"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 4"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 4"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 4"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 4"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 4"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 4"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 4"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 4"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 4"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 4"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 4"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 4"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 4"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 4"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 5"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 5"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 5"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 5"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 5"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 5"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 5"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 5"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 5"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 5"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 5"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 5"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 5"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 5"/>
<w:LsdException Locked="false" Priority="60" Name="Light Shading Accent 6"/>
<w:LsdException Locked="false" Priority="61" Name="Light List Accent 6"/>
<w:LsdException Locked="false" Priority="62" Name="Light Grid Accent 6"/>
<w:LsdException Locked="false" Priority="63" Name="Medium Shading 1 Accent 6"/>
<w:LsdException Locked="false" Priority="64" Name="Medium Shading 2 Accent 6"/>
<w:LsdException Locked="false" Priority="65" Name="Medium List 1 Accent 6"/>
<w:LsdException Locked="false" Priority="66" Name="Medium List 2 Accent 6"/>
<w:LsdException Locked="false" Priority="67" Name="Medium Grid 1 Accent 6"/>
<w:LsdException Locked="false" Priority="68" Name="Medium Grid 2 Accent 6"/>
<w:LsdException Locked="false" Priority="69" Name="Medium Grid 3 Accent 6"/>
<w:LsdException Locked="false" Priority="70" Name="Dark List Accent 6"/>
<w:LsdException Locked="false" Priority="71" Name="Colorful Shading Accent 6"/>
<w:LsdException Locked="false" Priority="72" Name="Colorful List Accent 6"/>
<w:LsdException Locked="false" Priority="73" Name="Colorful Grid Accent 6"/>
<w:LsdException Locked="false" Priority="19" QFormat="true"
Name="Subtle Emphasis"/>
<w:LsdException Locked="false" Priority="21" QFormat="true"
Name="Intense Emphasis"/>
<w:LsdException Locked="false" Priority="31" QFormat="true"
Name="Subtle Reference"/>
<w:LsdException Locked="false" Priority="32" QFormat="true"
Name="Intense Reference"/>
<w:LsdException Locked="false" Priority="33" QFormat="true" Name="Book Title"/>
<w:LsdException Locked="false" Priority="37" SemiHidden="true"
UnhideWhenUsed="true" Name="Bibliography"/>
<w:LsdException Locked="false" Priority="39" SemiHidden="true"
UnhideWhenUsed="true" QFormat="true" Name="TOC Heading"/>
<w:LsdException Locked="false" Priority="41" Name="Plain Table 1"/>
<w:LsdException Locked="false" Priority="42" Name="Plain Table 2"/>
<w:LsdException Locked="false" Priority="43" Name="Plain Table 3"/>
<w:LsdException Locked="false" Priority="44" Name="Plain Table 4"/>
<w:LsdException Locked="false" Priority="45" Name="Plain Table 5"/>
<w:LsdException Locked="false" Priority="40" Name="Grid Table Light"/>
<w:LsdException Locked="false" Priority="46" Name="Grid Table 1 Light"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark"/>
<w:LsdException Locked="false" Priority="51" Name="Grid Table 6 Colorful"/>
<w:LsdException Locked="false" Priority="52" Name="Grid Table 7 Colorful"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 1"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 1"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 1"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 1"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 1"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 2"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 2"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 2"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 2"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 2"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 3"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 3"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 3"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 3"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 3"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 4"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 4"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 4"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 4"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 4"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 5"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 5"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 5"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 5"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 5"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="46"
Name="Grid Table 1 Light Accent 6"/>
<w:LsdException Locked="false" Priority="47" Name="Grid Table 2 Accent 6"/>
<w:LsdException Locked="false" Priority="48" Name="Grid Table 3 Accent 6"/>
<w:LsdException Locked="false" Priority="49" Name="Grid Table 4 Accent 6"/>
<w:LsdException Locked="false" Priority="50" Name="Grid Table 5 Dark Accent 6"/>
<w:LsdException Locked="false" Priority="51"
Name="Grid Table 6 Colorful Accent 6"/>
<w:LsdException Locked="false" Priority="52"
Name="Grid Table 7 Colorful Accent 6"/>
<w:LsdException Locked="false" Priority="46" Name="List Table 1 Light"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark"/>
<w:LsdException Locked="false" Priority="51" Name="List Table 6 Colorful"/>
<w:LsdException Locked="false" Priority="52" Name="List Table 7 Colorful"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 1"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 1"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 1"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 1"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 1"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 1"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 2"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 2"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 2"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 2"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 2"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 2"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 3"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 3"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 3"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 3"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 3"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 3"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 4"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 4"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 4"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 4"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 4"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 4"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 5"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 5"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 5"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 5"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 5"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 5"/>
<w:LsdException Locked="false" Priority="46"
Name="List Table 1 Light Accent 6"/>
<w:LsdException Locked="false" Priority="47" Name="List Table 2 Accent 6"/>
<w:LsdException Locked="false" Priority="48" Name="List Table 3 Accent 6"/>
<w:LsdException Locked="false" Priority="49" Name="List Table 4 Accent 6"/>
<w:LsdException Locked="false" Priority="50" Name="List Table 5 Dark Accent 6"/>
<w:LsdException Locked="false" Priority="51"
Name="List Table 6 Colorful Accent 6"/>
<w:LsdException Locked="false" Priority="52"
Name="List Table 7 Colorful Accent 6"/>
</w:LatentStyles>
</xml><![endif]--><!--[if gte mso 10]>
<style>
/* Style Definitions */
table.MsoNormalTable
{mso-style-name:普通表格;
mso-tstyle-rowband-size:0;
mso-tstyle-colband-size:0;
mso-style-noshow:yes;
mso-style-priority:99;
mso-style-parent:"";
mso-padding-alt:0cm 5.4pt 0cm 5.4pt;
mso-para-margin:0cm;
mso-para-margin-bottom:.0001pt;
mso-pagination:widow-orphan;
font-size:10.5pt;
mso-bidi-font-size:11.0pt;
font-family:"Calibri",sans-serif;
mso-ascii-font-family:Calibri;
mso-ascii-theme-font:minor-latin;
mso-hansi-font-family:Calibri;
mso-hansi-theme-font:minor-latin;
mso-font-kerning:1.0pt;}
</style>
<![endif]--><br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>