    <p>Amit,</p>
    <p> There is a component in the TESS Utility library (Type572:
      equipment fouling) that was designed for this purposes. The
      disadvantage of it is that you have to define the reduction in
      production efficiency as a function of the dust. However, once you
      do the component will linearly degrade component performance and
      will then account for periodic cleanings.</p>
    <p>  If you do not have access to that component you are probably
      best multiplying the performance of the PV by a performance
      reduction factor using an equation.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 01/29/2018 03:17, Amit Verma via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAGJ6am+kBiSDSK_wkHpbA83c9evQqkf6UHEkrgm=wS9es0a32A@mail.gmail.com">
      <div dir="ltr">Hello Everyone,
        <div><br>
        </div>
        <div>I am doing a project on type 94 (PV Module) . I have to
          find dust effect on PV module's Efficiency. Please suggest me
          how to enroll it with PV module .</div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>Kind Regards</div>
        <div>Amit Verma</div>
        <div><br>
        </div>
      </div>
      <div id="DAB4FAD8-2DD7-40BB-A1B8-4E2AA1F9FDF2"><br>
        <table style="border-top:1px solid #d3d4de">
          <tbody>
            <tr>
              <td style="width:55px;padding-top:13px"><a
href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail"
                  target="_blank" moz-do-not-send="true"><img
src="https://ipmcdn.avast.com/images/icons/icon-envelope-tick-round-orange-animated-no-repeat-v1.gif"
                    alt="" style="width: 46px; height: 29px;"
                    moz-do-not-send="true" height="29" width="46"></a></td>
              <td
style="width:470px;padding-top:12px;color:#41424e;font-size:13px;font-family:Arial,Helvetica,sans-serif;line-height:18px">Virus-free.
                <a
href="https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=webmail"
                  target="_blank" style="color:#4453ea"
                  moz-do-not-send="true">www.avast.com</a> </td>
            </tr>
          </tbody>
        </table>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Thu, Jan 25, 2018 at 6:00 AM, <span
            dir="ltr"><<a
              href="mailto:trnsys-users-request@lists.onebuilding.org"
              target="_blank" moz-do-not-send="true">trnsys-users-request@lists.onebuilding.org</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Send
            TRNSYS-users mailing list submissions to<br>
                    <a href="mailto:trnsys-users@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users@lists.<wbr>onebuilding.org</a><br>
            <br>
            To subscribe or unsubscribe via the World Wide Web, visit<br>
                    <a
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
              rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
            <br>
            or, via email, send a message with subject or body 'help' to<br>
                    <a
              href="mailto:trnsys-users-request@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users-request@lists.<wbr>onebuilding.org</a><br>
            <br>
            You can reach the person managing the list at<br>
                    <a
              href="mailto:trnsys-users-owner@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users-owner@lists.<wbr>onebuilding.org</a><br>
            <br>
            When replying, please edit your Subject line so it is more
            specific<br>
            than "Re: Contents of TRNSYS-users digest..."<br>
            <br>
            Today's Topics:<br>
            <br>
               1. airchange between zones (Alex moreno)<br>
               2. Re: airchange between zones (David BRADLEY)<br>
            <br>
            <br>
            ---------- Forwarded message ----------<br>
            From: Alex moreno <<a
              href="mailto:alamoreno19@hotmail.com"
              moz-do-not-send="true">alamoreno19@hotmail.com</a>><br>
            To: trnsys_users <<a
              href="mailto:trnsys-users@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users@lists.onebuilding.org</a>><br>
            Cc: <br>
            Bcc: <br>
            Date: Wed, 24 Jan 2018 14:22:02 +0000<br>
            Subject: [TRNSYS-users] airchange between zones<br>
            Hi<br>
            <br>
            I have a doubt when i modeling a single family building with
            two floors,<br>
            how i can connect the airchange between of  two zones (first
            floor and<br>
            second floor)<br>
            <br>
            another doubt is:<br>
            <br>
            Firstly i simulated the two floors us one zones, but now i
            simulate the<br>
            buildign us two zones, the results of heating differ 2%
            respec of  one<br>
            zone building and differ cooling 10%, it is normally?<br>
            <br>
            regards<br>
            <br>
            <br>
            Alex<br>
            <br>
            <br>
            <br>
            ---------- Forwarded message ----------<br>
            From: David BRADLEY <<a
              href="mailto:d.bradley@tess-inc.com"
              moz-do-not-send="true">d.bradley@tess-inc.com</a>><br>
            To: "TRNSYS users mailing list at OneBuilding.org" <<a
              href="mailto:trnsys-users@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users@lists.onebuilding.org</a>><br>
            Cc: Alex moreno <<a href="mailto:alamoreno19@hotmail.com"
              moz-do-not-send="true">alamoreno19@hotmail.com</a>><br>
            Bcc: <br>
            Date: Wed, 24 Jan 2018 16:49:40 -0600<br>
            Subject: Re: [TRNSYS-users] airchange between zones<br>
            Alex,<br>
            <br>
              When you define an ADJACENT wall (or floor/ceiling)
            between two zones you have the ability to define a coupling
            air flow rate from each to the other. You can set the flow
            rate as a constant, as a scheduled value, or as an input.
            Type56 leaves it to you to determine how much air flows back
            and forth between the zones.<br>
            <br>
              The most correct way of determining the quantity of
            airflow is to use an airflow modeling tool such as TRNFlow
            or Type97/CONTAM.<br>
            <br>
              It is hard to answer your second question. The answer
            depends on what metrics you are looking at. For instance, I
            would be surprised to see the loads of the building change
            by 10% based on 1 zone or 2. However, if you are looking at
            consumption of energy by an HVAC system then it is possible,
            especially if you are using a single thermostat to control
            the system.<br>
            <br>
            kind regards,<br>
            <br>
             David<br>
            <br>
            <br>
            <br>
            On 01/24/2018 08:22, Alex moreno via TRNSYS-users wrote:<br>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              Hi<br>
              <br>
              I have a doubt when i modeling a single family building
              with two floors,<br>
              how i can connect the airchange between of  two zones
              (first floor and<br>
              second floor)<br>
              <br>
              another doubt is:<br>
              <br>
              Firstly i simulated the two floors us one zones, but now i
              simulate the<br>
              buildign us two zones, the results of heating differ 2%
              respec of  one<br>
              zone building and differ cooling 10%, it is normally?<br>
              <br>
              regards<br>
              <br>
              <br>
              Alex<br>
              <br>
              ______________________________<wbr>_________________<br>
              TRNSYS-users mailing list<br>
              <a href="mailto:TRNSYS-users@lists.onebuilding.org"
                target="_blank" moz-do-not-send="true">TRNSYS-users@lists.onebuilding<wbr>.org</a><br>
              <a
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/l<wbr>istinfo.cgi/trnsys-users-onebu<wbr>ilding.org</a><br>
            </blockquote>
            <br>
            -- <br>
            ***************************<br>
            David BRADLEY<br>
            Principal<br>
            Thermal Energy Systems Specialists, LLC<br>
            22 North Carroll Street - suite 370<br>
            Madison, WI  53703 USA<br>
            <br>
            P:+1.608.274.2577<br>
            F:+1.608.278.1475<br>
            <a href="mailto:d.bradley@tess-inc.com" target="_blank"
              moz-do-not-send="true">d.bradley@tess-inc.com</a><br>
            <br>
            <a href="http://www.tess-inc.com" rel="noreferrer"
              target="_blank" moz-do-not-send="true">http://www.tess-inc.com</a><br>
            <a href="http://www.trnsys.com" rel="noreferrer"
              target="_blank" moz-do-not-send="true">http://www.trnsys.com</a><br>
            <br>
            <br>
            <br>
            ______________________________<wbr>_________________<br>
            TRNSYS-users mailing list<br>
            <a href="mailto:TRNSYS-users@lists.onebuilding.org"
              moz-do-not-send="true">TRNSYS-users@lists.<wbr>onebuilding.org</a><br>
            <a
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
              rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>