<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>Amit,</p>
    <p>  I am not clear as to whether you are asking for an explanation
      of the equation V = max(0,time-10) or whether you are asking about
      the format of the characteristic of a photovoltaic's I-V curve. <br>
    </p>
    <p> If it is the first case then the max(:,:) function returns the
      maximum of two arguments. TIME is a built-in variable. The
      equation sets a variable (V) to the maximum of zero or the present
      simulation time minus 10. <br>
    </p>
    <p> If you want to know about the characteristic curve of a PV I
      would recommend reading the 04-MathematicalReference manual
      section about the PV Type that you are using.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 01/09/2018 07:23, Amit Verma via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAGJ6amK6jAYsTvu1nLw7usysTWqMZ=QZs1nTee-7779MmgLDNA@mail.gmail.com">
      <div dir="ltr">Hello Everyone !!!
        <div><br>
        </div>
        <div>Can anyone describe how to write Eqn  for I-V Curve in
          Photovoltaic i.e V=max (0,time-10)</div>
        <div><br>
        </div>
        <div>Regards</div>
        <div>Amit Verma</div>
      </div>
      <div class="gmail_extra"><br>
        <div class="gmail_quote">On Tue, Jan 9, 2018 at 2:03 PM, <span
            dir="ltr"><<a
              href="mailto:trnsys-users-request@lists.onebuilding.org"
              target="_blank" moz-do-not-send="true">trnsys-users-request@lists.onebuilding.org</a>></span>
          wrote:<br>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">Send
            TRNSYS-users mailing list submissions to<br>
                    <a href="mailto:trnsys-users@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users@lists.<wbr>onebuilding.org</a><br>
            <br>
            To subscribe or unsubscribe via the World Wide Web, visit<br>
                    <a
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
              rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
            <br>
            or, via email, send a message with subject or body 'help' to<br>
                    <a
              href="mailto:trnsys-users-request@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users-request@lists.<wbr>onebuilding.org</a><br>
            <br>
            You can reach the person managing the list at<br>
                    <a
              href="mailto:trnsys-users-owner@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users-owner@lists.<wbr>onebuilding.org</a><br>
            <br>
            When replying, please edit your Subject line so it is more
            specific<br>
            than "Re: Contents of TRNSYS-users digest..."<br>
            <br>
            Today's Topics:<br>
            <br>
               1. Re: curve of WTG (MACIAS VICENTE, SERGIO)<br>
            <br>
            <br>
            ---------- Forwarded message ----------<br>
            From: "MACIAS VICENTE, SERGIO" <<a
              href="mailto:SMACIAS@external.gamesacorp.com"
              moz-do-not-send="true">SMACIAS@external.gamesacorp.com</a>><br>
            To: "'David BRADLEY'" <<a
              href="mailto:d.bradley@tess-inc.com"
              moz-do-not-send="true">d.bradley@tess-inc.com</a>>,
            "TRNSYS users mailing list at OneBuilding.org" <<a
              href="mailto:trnsys-users@lists.onebuilding.org"
              moz-do-not-send="true">trnsys-users@lists.onebuilding.org</a>><br>
            Cc: <br>
            Bcc: <br>
            Date: Tue, 9 Jan 2018 08:33:50 +0000<br>
            Subject: Re: [TRNSYS-users] curve of WTG<br>
            <div bgcolor="white" link="blue" vlink="purple" lang="ES">
              <div class="m_5304206081160449409WordSection1">
                <p class="MsoNormal"><span
                    class="m_5304206081160449409shorttext"><span
                      lang="EN">Hello,</span></span><span lang="EN"><br>
                    <br>
                    <span class="m_5304206081160449409shorttext">Thank
                      you very much. The fault was that.</span></span></p>
                <p class="MsoNormal"><span
                    class="m_5304206081160449409shorttext"><span
                      lang="EN"> </span></span></p>
                <p class="MsoNormal"><span
                    class="m_5304206081160449409shorttext"><span
                      lang="EN">Best regards.</span></span><span
                    style="color:#1f497d"></span></p>
                <p class="MsoNormal"><span style="color:#1f497d"> </span></p>
                <div>
                  <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                        lang="EN-US">Sergio Macías Vicente</span></b></p>
                  <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                      lang="EN-US">Offgrid Technical</span><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"></span></p>
                  <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a">Siemens
                      Gamesa Offgrid</span></p>
                  <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><img
                        id="m_5304206081160449409_x0000_i1028"
                        src="cid:part9.A5C8DFD0.62833F57@tess-inc.com"
                        alt="Descripción: Descripción:
                        cid:image001.png@01D2AD3E.E2146250" class=""
                        height="56" width="166"></span><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4b4d4f"></span></p>
                  <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a">Gamesa
                        Corporación Tecnológica</span></b><span
                      style="color:#1f497d"></span></p>
                </div>
                <p class="MsoNormal"> </p>
                <div>
                  <div style="border:none;border-top:solid #b5c4df
                    1.0pt;padding:3.0pt 0cm 0cm 0cm">
                    <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">De:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
                        David BRADLEY [mailto:<a
                          href="mailto:d.bradley@tess-inc.com"
                          target="_blank" moz-do-not-send="true">d.bradley@tess-inc.com</a><wbr>]
                        <br>
                        <b>Enviado el:</b> viernes, 22 de diciembre de
                        2017 18:55<br>
                        <b>Para:</b> MACIAS VICENTE, SERGIO; TRNSYS
                        users mailing list at OneBuilding.org<br>
                        <b>Asunto:</b> Re: [TRNSYS-users] curve of WTG</span></p>
                  </div>
                </div>
                <p class="MsoNormal"> </p>
                <p>Sergio,</p>
                <p> I suggested the distributor route because this forum
                  is (supposedly) for users to help users whereas the
                  distributors are (hopefully) more likely to respond to
                  tech support questions like yours.</p>
                <p>I did look at the project you sent. The wind turbine
                  is internally controlled so that if the wind speed
                  exceeds the rated wind speed (specified in the data
                  file) the rotors change pitch to shed wind so that the
                  turbine is not damaged. When the incident wind speed
                  exceeds rated wind speed the turbine will produce its
                  rated power.</p>
                <p>kind regards,</p>
                <p> David</p>
                <p> </p>
                <p class="MsoNormal"> </p>
                <div>
                  <p class="MsoNormal">On 12/20/2017 01:50, MACIAS
                    VICENTE, SERGIO wrote:</p>
                </div>
                <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
                  <p class="MsoNormal"><span lang="EN">Hello,<br>
                      <br>
                      I attach all the files. Surely someone can help
                      me. It is a simple example to verify that the
                      behavior of the wind turbine is correct.</span></p>
                  <p class="MsoNormal"><span lang="EN"> </span></p>
                  <p class="MsoNormal"><span lang="EN">Thank you.</span></p>
                  <p class="MsoNormal"><span lang="EN"> </span></p>
                  <p class="MsoNormal"><span lang="EN">Best regards.</span></p>
                  <p class="MsoNormal"><span style="color:#1f497d"
                      lang="EN-US"> </span></p>
                  <div>
                    <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                          lang="EN-US">Sergio Macías Vicente</span></b></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                        lang="EN-US">Offgrid Technical</span></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a">Siemens
                        Gamesa Offgrid</span></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><img
                          id="m_5304206081160449409_x0000_i1025"
                          src="cid:part9.A5C8DFD0.62833F57@tess-inc.com"
                          alt="Descripción: Descripción:
                          cid:image001.png@01D2AD3E.E2146250" class=""
                          height="56" width="166"></span></p>
                    <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a">Gamesa
                          Corporación Tecnológica</span></b></p>
                  </div>
                  <p class="MsoNormal"> </p>
                  <div>
                    <div style="border:none;border-top:solid #b5c4df
                      1.0pt;padding:3.0pt 0cm 0cm 0cm">
                      <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">De:</span></b><span
style="font-size:10.0pt;font-family:"Tahoma","sans-serif";color:windowtext">
                          David BRADLEY [<a
                            href="mailto:d.bradley@tess-inc.com"
                            target="_blank" moz-do-not-send="true">mailto:d.bradley@tess-inc.com</a><wbr>]
                          <br>
                          <b>Enviado el:</b> martes, 19 de diciembre de
                          2017 21:19<br>
                          <b>Para:</b> TRNSYS users mailing list at
                          OneBuilding.org<br>
                          <b>CC:</b> MACIAS VICENTE, SERGIO<br>
                          <b>Asunto:</b> Re: [TRNSYS-users] curve of WTG</span></p>
                    </div>
                  </div>
                  <p class="MsoNormal"> </p>
                  <p><span lang="EN">Sergio,</span></p>
                  <p><span lang="EN"> I would recommend that you send
                      your project to your distributor so that they can
                      determine why the turbine is giving less power
                      than expected.</span></p>
                  <p><span lang="EN"> The distributor will need to have
                      your project (*.tpf file) and the wind turbine
                      data file that you are using as well as any other
                      files needed in order to run the simulation.</span></p>
                  <p><span lang="EN">kind regards,</span></p>
                  <p><span lang="EN"> David</span></p>
                  <p> </p>
                  <p class="MsoNormal"> </p>
                  <div>
                    <p class="MsoNormal">On 12/19/2017 09:47, MACIAS
                      VICENTE, SERGIO via TRNSYS-users wrote:</p>
                  </div>
                  <blockquote
                    style="margin-top:5.0pt;margin-bottom:5.0pt">
                    <p class="MsoNormal"><span lang="EN">Hello, my name
                        is Sergio.<br>
                        <br>
                        I have a question. I have the curve of a wind
                        turbine as in the image. The behavior is not
                        correct, since at 25 m / s they produce 95 kW.
                        Can you insert a curve in the next way?</span></p>
                    <p class="MsoNormal"><span lang="EN"> </span></p>
                    <p class="MsoNormal"><span lang="EN">Thanks.</span></p>
                    <p class="MsoNormal"><span lang="EN"> </span></p>
                    <p class="MsoNormal"><span lang="EN">Best regards.</span></p>
                    <p class="MsoNormal"><span lang="EN"> </span></p>
                    <p class="MsoNormal"><span><img
                          id="m_5304206081160449409Imagen_x0020_2"
                          src="cid:part13.68633FB2.7E6CB8AA@tess-inc.com"
                          class="" height="794" width="276" border="0"></span></p>
                    <p class="MsoNormal"><span lang="EN-US"> </span></p>
                    <p class="MsoNormal"><span lang="EN-US"> </span></p>
                    <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                          lang="EN-US">Sergio Macías Vicente</span></b></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                        lang="EN-US">Offgrid Technical</span></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a">Siemens
                        Gamesa Offgrid</span></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif""><img
                          id="m_5304206081160449409Imagen_x0020_1"
                          src="cid:part9.A5C8DFD0.62833F57@tess-inc.com"
                          alt="Descripción: Descripción:
                          cid:image001.png@01D2AD3E.E2146250" class=""
                          height="56" width="166" border="0"></span></p>
                    <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a">Gamesa
                          Corporación Tecnológica</span></b></p>
                    <p class="MsoNormal"><b><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"> </span></b></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4b4d4f">Crta.
                        Pozaldez km.1</span></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#4b4d4f">47400
                        Medina del Campo</span></p>
                    <p class="MsoNormal"><span
style="font-size:10.0pt;font-family:"Arial","sans-serif";color:#5a5a5a">Spain</span></p>
                    <p class="MsoNormal"><span> </span></p>
                    <p class="MsoNormal"><span><a
                          href="mailto:smacias@external.gamesacorp.com"
                          target="_blank" moz-do-not-send="true">smacias@external.gamesacorp.<wbr>com</a></span></p>
                    <p class="MsoNormal"><span><a
                          href="http://www.gamesacorp.com/"
                          target="_blank" moz-do-not-send="true"><span
                            lang="EN-US">www.gamesacorp.com</span></a></span></p>
                    <p class="MsoNormal"><span lang="EN-US"> </span></p>
                    <p class="MsoNormal"><i><span
style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                          lang="EN-US">“Before printing this mail or any
                          of its attachments please be sure it is
                          absolutely necessary. Protection of the
                          environment is everyone's responsibility. We
                          have the right to enjoy it but also the
                          obligation to preserve it"</span></i></p>
                    <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                        lang="EN-US"> </span></p>
                    <p class="MsoNormal"><span
style="font-size:8.0pt;font-family:"Arial","sans-serif";color:#5a5a5a"
                        lang="EN-US">DISCLAIMER: "The content of the
                        present communication, and its annexes, is for
                        informational purposes only and does not in any
                        case constitute a binding offer, acceptance or
                        opinion for GAMESA unless so set forth in
                        separate document subscribed by a representative
                        of the company with sufficient faculties to do
                        so. This message may contain private and
                        confidential information and is directed
                        exclusively to its addressee. GAMESA will not
                        assume any obligation, nor execute orders or
                        mandates received or sent by electronic mail."</span></p>
                    <p class="MsoNormal"><span lang="EN-US"> </span></p>
                    <p class="MsoNormal"><span style="font-size:12.0pt"><br>
                        <br>
                        <br>
                        <br>
                      </span></p>
                    <pre>______________________________<wbr>_________________</pre>
                    <pre>TRNSYS-users mailing list</pre>
                    <pre><a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank" moz-do-not-send="true">TRNSYS-users@lists.<wbr>onebuilding.org</a></pre>
                    <pre><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a></pre>
                  </blockquote>
                  <p class="MsoNormal"><span style="font-size:12.0pt"><br>
                      <br>
                      <br>
                    </span></p>
                  <pre>-- </pre>
                  <pre>***************************</pre>
                  <pre>David BRADLEY</pre>
                  <pre>Principal</pre>
                  <pre>Thermal Energy Systems Specialists, LLC</pre>
                  <pre>22 North Carroll Street - suite 370</pre>
                  <pre>Madison, WI  53703 USA</pre>
                  <pre> </pre>
                  <pre>P:+1.608.274.2577</pre>
                  <pre>F:+1.608.278.1475</pre>
                  <pre><a href="mailto:d.bradley@tess-inc.com" target="_blank" moz-do-not-send="true">d.bradley@tess-inc.com</a></pre>
                  <pre> </pre>
                  <pre><a href="http://www.tess-inc.com" target="_blank" moz-do-not-send="true">http://www.tess-inc.com</a></pre>
                  <pre><a href="http://www.trnsys.com" target="_blank" moz-do-not-send="true">http://www.trnsys.com</a></pre>
                </blockquote>
                <p class="MsoNormal"><span
                    style="font-size:12.0pt;font-family:"Times New
                    Roman","serif""><br>
                    <br>
                  </span></p>
                <pre>-- </pre>
                <pre>***************************</pre>
                <pre>David BRADLEY</pre>
                <pre>Principal</pre>
                <pre>Thermal Energy Systems Specialists, LLC</pre>
                <pre>22 North Carroll Street - suite 370</pre>
                <pre>Madison, WI  53703 USA</pre>
                <pre> </pre>
                <pre>P:+1.608.274.2577</pre>
                <pre>F:+1.608.278.1475</pre>
                <pre><a href="mailto:d.bradley@tess-inc.com" target="_blank" moz-do-not-send="true">d.bradley@tess-inc.com</a></pre>
                <pre> </pre>
                <pre><a href="http://www.tess-inc.com" target="_blank" moz-do-not-send="true">http://www.tess-inc.com</a></pre>
                <pre><a href="http://www.trnsys.com" target="_blank" moz-do-not-send="true">http://www.trnsys.com</a></pre>
              </div>
            </div>
            <br>
            ______________________________<wbr>_________________<br>
            TRNSYS-users mailing list<br>
            <a href="mailto:TRNSYS-users@lists.onebuilding.org"
              moz-do-not-send="true">TRNSYS-users@lists.<wbr>onebuilding.org</a><br>
            <a
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
              rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>