    <p>Ravinda,</p>
    <p>  There is a pressure reducing valve component in the TESS CHP
      library. It is typically used in steam applications and assumes
      steam as the working fluid. </p>
    <p>  Typically we do not model refrigeration systems at the heat
      exchanger / compressor / expansion valve level but take the whole
      cycle as a component. The time constant of the transient behavior
      within the refrigeration cycle is so small that a typical TRNSYS
      time step (1-5 minutes in the kind of systems that we work with)
      that the refrigeration loop can be seen as steady state. We
      therefore assign a COP that is dependent on the external inlet
      conditions (such as temperature and humidity of the air on the
      condenser and evaporator sides).</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 12/19/2017 04:19, v ravindra via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CADb1Z3LpOCBpD7Wgn83wS+iesJm5tiBZJz=-o8C9g29-TRoTQg@mail.gmail.com">
      <div dir="ltr">What is the component that models a Throttle valve
        used in Refrigeration cycles in TRNSYS.
        <div> <br clear="all">
          <div>
            <div class="gmail_signature"
              data-smartmail="gmail_signature">
              <div dir="ltr">
                <div dir="ltr">V.Ravindra<br>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>