<font size=2 face="sans-serif">Jeff,</font><br><br><font size=2 face="sans-serif">It's great to hear from the creator
of the component! I have taken this wrong assumption because the mathematical
reference says that: </font><font size=2 face="Arial">"... For the
sake of simulation speed, the model breaks the ground along two axes of
symmetry (in the x and y directions) and simulates only one quarter of
the field, multiplying energy transfer results to arrive at the total effect."</font><br><font size=2 face="Arial">What I would like to simulate is something
like:</font><br><img src=cid:_1_26EC723C08F81210003D8F06C12581D7 width=1136 height=390><font size=2 face="Arial"> </font><br><font size=2 face="Arial">38 pipes of 55m length in the ground buried
on average 2.5m (centerline of middle row). All pipes are connected at
inlets and outlets with collectors, and the same mass flow rate is assumed.</font><br><font size=2 face="Arial">The HX is close to the building wall: 1.5m,
which is insulated from the outside. At the end I want also combine building
thermal simulation with the 997 type in simulation studio, but I dont'
have building geometry yet.  </font><br><font size=2 face="Arial">The shift in the middle row can be neglected
if the tool is not capable of including that. </font><br><font size=2 face="Arial">My goal is to simulate 25 years of HX and
get outlet temperatures and ground temperatures. I read that there's GroundTemperatureViewer
tool capable to see the .soil file, but it cannot find it yet. </font><br><br><font size=2 face="sans-serif">Best regards,</font><br><font size=3 color=#5f5f5f face="Calibri Light"><b>Jakub Winiarski</b><br>R&D Specialist / Energy Simulations </font><p><img src=cid:_2_08F7B65C08F7B3F0003D8F06C12581D7><br><font size=3 color=#5f5f5f face="Calibri Light">kom. +48 882 341 596<br>e-mail: </font><a href=mailto:b.starosielec@mostostal.waw.pl><font size=3 color=#0082bf face="Calibri Light"><u>j.winiarski@mostostal.waw.pl</u></font></a><p><font size=3 color=#002060 face="Calibri Light">mostostal.waw.pl</font><font size=3></font><br><img src=cid:_2_08F7C29408F7C028003D8F06C12581D7><font size=3 color=#002060 face="Calibri Light"><b> 
      BUDUJEMY</b> PRZYSZŁOŚĆ</font><font size=3 color=red face="Calibri Light">.</font><font size=3 color=#002060 face="Calibri Light"><br>        Mostostal Warszawa SA, ul. Konstruktorska
12A, 02-673 Warszawa, tel.: +48 22 250 70 00, fax: +48 22 250 70 01 <br>        Sąd Rejonowy dla m. st. Warszawy w
Warszawie, XIII Wydział Gospodarczy Krajowego Rejestru Sądowego<br>        Nr KRS 0000008820, NIP: 526-020-49-95,
Regon: 012059053</font><font size=3> </font><br><br><font size=3 color=#8f8f8f face="Calibri Light">Jesteśmy jednym z
sygnatariuszy Porozumienia dla Bezpieczeństwa w Budownictwie – inicjatywy
utworzonej w sierpniu 2010 r. przez siedmiu największych generalnych wykonawców
w naszym kraju. Misją Porozumienia jest prowadzenie działań na rzecz
podniesienia poziomu kultury bezpieczeństwa pracy w branży budowlanej,
a celem wyeliminowanie wypadków śmiertelnych na polskich budowach. <br> </font><font size=3> </font><br><br><br><br><font size=1 color=#5f5f5f face="sans-serif">Od:      
 </font><font size=1 face="sans-serif">Jeff Thornton via TRNSYS-users
<trnsys-users@lists.onebuilding.org></font><br><font size=1 color=#5f5f5f face="sans-serif">Do:      
 </font><font size=1 face="sans-serif">"TRNSYS users
mailing list at OneBuilding.org" <trnsys-users@lists.onebuilding.org></font><br><font size=1 color=#5f5f5f face="sans-serif">DW:      
 </font><font size=1 face="sans-serif">Jeff Thornton <thornton@tess-inc.com></font><br><font size=1 color=#5f5f5f face="sans-serif">Data:      
 </font><font size=1 face="sans-serif">10.11.2017 17:34</font><br><font size=1 color=#5f5f5f face="sans-serif">Temat:      
 </font><font size=1 face="sans-serif">Re: [TRNSYS-users]
[TRNSYS users] Type 997 modification (Horizontal Field Ground Heat Exchanger)</font><br><font size=1 color=#5f5f5f face="sans-serif">Wysłane przez:  
     </font><font size=1 face="sans-serif">"TRNSYS-users"
<trnsys-users-bounces@lists.onebuilding.org></font><br><hr noshade><br><br><br><font size=3>Jakub,</font><p><font size=3>As the author of Type997, I can tell you that the model
most certainly does NOT use 1/4 symmetry.  There's no way to apply
the symmetry as the fluid changes temperature along the entire length axis
and across the entire width and depth of the piping array.  That's
why Type997 takes both the left and right, and both the front and back,
parameters (insulation extension, far-field boundary etc.).  If it
was 1/4 symmetry it would need only one of front/back or left/right.  Why
don't you send a sketch showing what you'd like to model and we can see
if 997 is the right model.  We have other more generic models that
can handle a wider range of geometries.</font><p><font size=3> </font><p><font size=3>Jeff</font><p><font size=3> </font><p><tt><font size=3>---<br>Jeff Thornton<br>President - TESS LLC<br>22 N. Carroll Street, Madison WI USA 53703<br>Office: (608) 274-2577  Fax: (608) 278-1475<br></font></tt><a href="www.tess-inc.com"><tt><font size=3>www.tess-inc.com</font></tt></a><tt><font size=3><br>E-Mail: thornton@tess-inc.com<br></font></tt><p><font size=3>On 11/10/2017 4:15 am, Jakub Winiarski via TRNSYS-users
wrote:</font><p><font size=2>Dear Users,</font><font size=3><br></font><font size=2><br>Have anybody tried to modify the Type 997 component: Horizontal Field Ground
Heat Exchanger, so that the insulation on Near Field surface can be set
on just one side of HX domain? By deafult in order to reduce calculation
cost the model is symmetrical in both x and y axis so that only quarter
of domain is calculated. That is why the user can provide insulation on
all four bounding surfaces or none. If there is a way to 'turn off' the
symmetry in FORTRAN code and apply the boundary conditions on particular
bounding surfaces it will be all I need. <br>Perhaps someone already have done such modification?</font><font size=3><br></font><font size=2><br>Best regards,</font><font size=3 color=#5f5f5f face="Calibri"><b><br>Jakub Winiarski</b><br>R&D Specialist / Energy Simulations </font><p><font size=3 color=#5f5f5f face="Calibri"><br>kom. +48 882 341 596<br>e-mail: </font><a href=mailto:b.starosielec@mostostal.waw.pl><font size=3 color=#0082bf face="Calibri"><u>j.winiarski@mostostal.waw.pl</u></font></a><p><font size=3 color=#002060 face="Calibri">mostostal.waw.pl</font><font size=3><br></font><font size=3 color=#002060 face="Calibri"><b>      
 BUDUJEMY</b> PRZYSZŁOŚĆ</font><font size=3 color=red face="Calibri">.</font><font size=3 color=#002060 face="Calibri"><br>       Mostostal Warszawa SA, ul. Konstruktorska 12A, 02-673
Warszawa, tel.: +48 22 250 70 00, fax: +48 22 250 70 01 <br>       Sąd Rejonowy dla m. st. Warszawy w Warszawie, XIII
Wydział Gospodarczy Krajowego Rejestru Sądowego<br>       Nr KRS 0000008820, NIP: 526-020-49-95, Regon: 012059053</font><font size=3><br></font><font size=3 color=#8f8f8f face="Calibri"><br>Jesteśmy jednym z sygnatariuszy Porozumienia dla Bezpieczeństwa w Budownictwie
– inicjatywy utworzonej w sierpniu 2010 r. przez siedmiu największych
generalnych wykonawców w naszym kraju. Misją Porozumienia jest prowadzenie
działań na rzecz podniesienia poziomu kultury bezpieczeństwa pracy w
branży budowlanej, a celem wyeliminowanie wypadków śmiertelnych na polskich
budowach. <br> </font><font size=3> </font><p><tt><font size=3>_______________________________________________<br>TRNSYS-users mailing list<br></font></tt><a href="mailto:TRNSYS-users@lists.onebuilding.org"><tt><font size=3 color=blue><u>TRNSYS-users@lists.onebuilding.org</u></font></tt></a><tt><font size=3><br></font></tt><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"><tt><font size=3 color=blue><u>http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</u></font></tt></a><tt><font size=3><br></font></tt><tt><font size=2>_______________________________________________<br>TRNSYS-users mailing list<br>TRNSYS-users@lists.onebuilding.org<br></font></tt><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"><tt><font size=2>http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</font></tt></a><tt><font size=2><br></font></tt><p><font face="sans-serif"></font>