<!DOCTYPE html PUBLIC "-//W3C//DTD XHTML 1.0 Transitional//EN">
<html><body>
<p>Yang,</p>
<p>There is an aquifer thermal energy storage model (TRNATES) available from your distributor (TESS, TRANSSOLAR etc.).  We've used it a few times with pretty good results but it does have a few limitations (the bores don't interact thermally for example).  We've also managed to couple MODFLOW and MT3D with TRNSYS (popular groundwater models) and can provide more information if needed.</p>
<p> </p>
<p>Jeff</p>
<div>
<pre>---<br />Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577  Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton@tess-inc.com
</pre>
</div>
<p>On 08/05/2017 12:30 pm, WANG Yang via TRNSYS-users wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->
<div dir="ltr"><span style="font-size: large;">Dear all,</span>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">I am modeling a <strong>Open Loop Borehole system for two Open Wells</strong>, one for abstracting underground water, another well for discharging, using TESS lib. However, I'd like to ask you <strong>which type</strong> is available for Open Loop Borehole system? I just found a Type 557 for U-tube borehole.</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">Look forward to your reply.</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">Many thanks</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">Br</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">Yang </span></div>
<div>
<div> </div>
<div> </div>
<div class="gmail_extra"><br />
<div class="gmail_quote">2017-08-02 10:53 GMT+01:00 WANG Yang <span><<a href="mailto:wanghongyang1767@gmail.com">wanghongyang1767@gmail.com</a>></span>:<br />
<blockquote class="gmail_quote" style="margin: 0px  0px  0px  0.8ex; border-left: 1px  solid rgb; padding-left: 1ex;">
<div dir="ltr"><span style="font-size: large;">Dear all,</span>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">I'd like to ask you one question about the error for Radiator Type 1231 shown in attached picture.</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">I used its heat transfer rate output to connect Type 56's own-defined input as the heating power. Then it appears that error. If I delete Radiator Type 1231, it runs well.</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">Many thanks</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">Br.</span></div>
<div><span style="font-size: large;"> </span></div>
<div><span style="font-size: large;">Yang  </span></div>
<div>
<div class="gmail_extra"><br />
<div class="gmail_quote">2017-08-01 21:12 GMT+01:00 via TRNSYS-users <span><<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>></span>:<br />
<blockquote class="gmail_quote" style="margin: 0px  0px  0px  0.8ex; border-left: 1px  solid rgb; padding-left: 1ex;">Send TRNSYS-users mailing list submissions to<br />         <a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a><br /><br /> To subscribe or unsubscribe via the World Wide Web, visit<br />         <a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br /><br /> or, via email, send a message with subject or body 'help' to<br />         <a href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.onebuilding.org</a><br /><br /> You can reach the person managing the list at<br />         <a href="mailto:trnsys-users-owner@lists.onebuilding.org">trnsys-users-owner@lists.onebuilding.org</a><br /><br /> When replying, please edit your Subject line so it is more specific<br /> than "Re: Contents of TRNSYS-users digest..."<br /><br />Today's Topics:<br /><br />    1. Re: variable timestep (Domenico Mazzeo via TRNSYS-users)<br />    2. Re: Exact same control signal for different Type 11f gives<br />       diferent results. (Jeff Thornton via TRNSYS-users)<br /><br /><br />---------- 已转发邮件 ----------<br />From: Domenico Mazzeo via TRNSYS-users <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>><br />To: "TRNSYS users mailing list at OneBuilding.org" <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>>, Jeff Thornton <<a href="mailto:thornton@tess-inc.com">thornton@tess-inc.com</a>><br />Cc: Jorge Facao <<a href="mailto:jorge.facao@lneg.pt">jorge.facao@lneg.pt</a>><br />Bcc: <br />Date: Tue, 1 Aug 2017 18:09:08 +0200<br />Subject: Re: [TRNSYS-users] variable timestep<br />
<div dir="auto">You could run more simulation with different time steps.
<div dir="auto">Then you could join the results with a variable time step.</div>
<div dir="auto">Regards</div>
</div>
<div class="gmail_extra"><br />
<div class="gmail_quote">Il 01 Ago 2017 16:53, "Jeff Thornton via TRNSYS-users" <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>> ha scritto:<br />
<blockquote class="gmail_quote" style="margin: 0px  0px  0px  0.8ex; border-left: 1px  solid rgb; padding-left: 1ex;">No, TRNSYS uses a fixed time step for the duration of the simulation.<br /><br /> Jeff<br /><br /> Sent from my iPhone<br /><br /> > On Jul 31, 2017, at 11:10 AM, Jorge Facao via TRNSYS-users <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>> wrote:<br /> ><br /> > Hello,<br /> > Is it possible to run a simulation with variable time-step in TRNSYS 17?<br /> > I have tried to put a time-step as a string in control cards but TRNSYS<br /> > consider the initial value of the string for all simulation.<br /> > Thanks in advance and best regards,<br /> ><br /> > --<br /> > Jorge Facão<br /> ><br /> > Laboratório Nacional de Energia e Geologia (LNEG)<br /> > Laboratório de Energia Solar<br /> > Estrada do Paço do Lumiar, 22<br /> > 1649-038 Lisboa - Portugal<br /> > T: <a href="tel:%2B351-210924600">+351-210924600</a>/1; Ext: 4379<br /> > skype: jfacao<br /> ><br /> > - AVISO -<br /> ><br /> > Esta mensagem de correio eletrónico e quaisquer dos seus ficheiros anexos, caso existam, são confidenciais e destinados apenas à(s) pessoa(s) ou entidade(s) acima referida(s), podendo conter informação confidencial, privilegiada, a qual não deverá ser divulgada, copiada, gravada ou distribuída nos termos da lei vigente. Se não é o destinatário da mensagem, ou se ela lhe foi enviada por engano, agradecemos que não faça uso ou divulgação da mesma. Se recebeu esta mensagem por engano, por favor avise-nos de imediato, por correio eletrónico, para o endereço acima e apague este e-mail do seu sistema.<br /> ><br /> > Obrigado.<br /> ><br /> ><br /> ><br /> > - NOTICE -<br /> ><br /> > This e-mail transmission and eventual attached files are intended only for the use of the individual or entity named above and may contain information that is confidential, privileged and exempt from disclosure under applicable law. If you are not the intended recipient, or if you have received this transmission in error, please immediately notify us by e-mail at the above address and delete this e-mail from your system.<br /> ><br /> > Thank you.<br /> > _______________________________________________<br /> > TRNSYS-users mailing list<br /> > <a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a><br /> > <a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br /><br /> _______________________________________________<br /> TRNSYS-users mailing list<br /><a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a><br /><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a></blockquote>
</div>
</div>
<br />
<div style="font-size: 1.3em;">-------------------------------------------------------------------------------</div>
<div><span style="font-family: Arial,Helvetica,sans-serif;">Il banner è generato automaticamente dal servizio di posta elettronica dell'Università della Calabria</span></div>
<div><span style="font-family: Arial,Helvetica,sans-serif;"> </span></div>
<div><a href="http://www.unical.it"><img src="cid:450696d512de2c9f2a4001ad2c873479@tess-inc.com" alt="" /></a></div>
<br /><br />---------- 已转发邮件 ----------<br />From: Jeff Thornton via TRNSYS-users <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>><br />To: <a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a><br />Cc: <br />Bcc: <br />Date: Tue, 01 Aug 2017 14:57:14 -0500<br />Subject: Re: [TRNSYS-users] Exact same control signal for different Type 11f gives diferent results.<br /><span style="text-decoration: underline;"></span>
<div>
<p>Javier,</p>
<p>That sounds suspiciously like a convergence problem.  Have you checked the list file to see if you are running into convergence issues?  Have you tried to TRACE the models in question to see what's happening on an iteration by iteration basis?  If it's convergence problems then the questions become: are you using a small timestep?  Are you using a controller with hysteresis? etc.</p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---<br />Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: <a href="tel:(608)%20274-2577">(608) 274-2577</a>  Fax: <a href="tel:(608)%20278-1475">(608) 278-1475</a>
<a href="http://www.tess-inc.com">www.tess-inc.com</a>
E-Mail: <a href="mailto:thornton@tess-inc.com">thornton@tess-inc.com</a>
</pre>
</div>
<p>On 08/01/2017 7:56 am, Javier Vega via TRNSYS-users wrote:</p>
<blockquote style="padding-left: 5px; border-left: 2px  solid rgb; margin-left: 5px;">
<div dir="ltr"><span style="font-size: 12.8px;">Hello TRNSYS users,</span>
<div style="font-size: 12.8px;"> </div>
<div style="font-size: 12.8px;">I want to use two Type 11f (controller flow diverter) components with the same control signal. One Type 11f redirects solar collector flow </div>
<div style="font-size: 12.8px;">(Type 553), while the other redirects another circuit's flow to one an Air-Source Heat Pump or a Water Source Heat Pump  (Type 941 or Type 927). The  events are supposed to happen at the same time.</div>
<div style="font-size: 12.8px;"> </div>
<div style="font-size: 12.8px;">Monitoring the results, my DHW temperature falls. When I looked it up, the flow diverters aren't working at the same time. And what it's worse, something happens with the Heat Pumps: I studied the control signals, and they are activated at the same time, but the heat pump's circuit redirects the flow when it isn't supposed to happen and also the Heat Pump that by mistakes recieves flow doesn't heat the water flow. This is what bothers me the most because I set the Heating control signal to a constant 1, so everytime the HP recieves flow it heats.</div>
<div style="font-size: 12.8px;"> </div>
<div style="font-size: 12.8px;">I simply don't know how to address this issue, same control signals giving different results, and a Heat Pump that recieves flow by mistake but doesn't heat. I would appreciate some help.</div>
<div style="font-size: 12.8px;"> </div>
<div style="font-size: 12.8px;">Kind Regards,<br />Javier Vega</div>
<div style="font-size: 12.8px;">Universidad de Concepcion</div>
</div>
<div class="gmail_extra"><br />
<div class="gmail_quote">2017-07-28 15:29 GMT-04:00 Javier Vega <span><<a href="mailto:jvega025@gmail.com">jvega025@gmail.com</a>></span>:<br />
<blockquote class="gmail_quote" style="margin: 0px  0px  0px  0.8ex; border-left: 1px  solid rgb; padding-left: 1ex;">
<div dir="ltr">Hello TRNSYS users,
<div> </div>
<div>I want to use two Type 11f (controller flow diverter) components with the same control signal. One Type 11f redirects solar collector flow </div>
<div>(Type 553), while the other redirects another circuit's flow to one an Air-Source Heat Pump or a Water Source Heat Pump  (Type 941 or Type 927). The  events are supposed to happen at the same time.</div>
<div> </div>
<div>Monitoring the results, my DHW temperature falls. When I looked it up, the flow diverters aren't working at the same time. And what it's worse, something happens with the Heat Pumps: I studied the control signals, and they are activated at the same time, but the heat pump's circuit redirects the flow when it isn't supposed to happen and also the Heat Pump that by mistakes recieves flow doesn't heat the water flow. This is what bothers me the most because I set the Heating control signal to a constant 1, so everytime the HP recieves flow it heats.</div>
<div> </div>
<div>I simply don't know how to address this issue, same control signals giving different results, and a Heat Pump that recieves flow by mistake but doesn't heat. I would appreciate some help.</div>
<div> </div>
<div>Kind Regards,<br />Javier Vega</div>
<div>Universidad de Concepcion</div>
</div>
</blockquote>
</div>
</div>
<br />
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</div>
<br />_______________________________________________<br /> TRNSYS-users mailing list<br /><a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a><br /><a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a><br /><br /></blockquote>
</div>
</div>
</div>
</div>
</blockquote>
</div>
</div>
</div>
</div>
<br />
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</body></html>