    <p>It means that your system is experiencing conditions that are not
      physically possible. The problem could be from Type56 (TRNBuild is
      an interface for generating Type56 files) or it could be
      originating in one of the system components. I would recommend
      that you temporarily disconnect the flow of air into the building
      but leave the exhaust flow connected. Using a Type65, watch the
      temperature, RH, and flow rate of air through each of the
      components in the system as it proceeds from ambient conditions to
      the conditions that are being supplied to the building. You should
      be able to get a clearer idea what is happening to the air and
      where the problem lies. <br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 07/15/2017 08:59, S.O.Daei.N via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:494428722.980955.1500127162303@mail.yahoo.com">
      <div style="font-family:Helvetica Neue, Helvetica, Arial,
        sans-serif;font-size:medium;">
        <div>Hi there</div>
        <div>I have problem with my project</div>
        <div>I get this error, what is that mean?</div>
        <div>Is that related to my house simulation on TRNBUILD?</div>
        <div>
          <div> ***** ERROR *****        TRNSYS ERROR # 116</div>
          <div> UNIT  14 TYPE 505</div>
          <div> THE PSYCHROMETRICS SUBROUTINE WAS CALLED WITH CONDITIONS</div>
          <div> YIELDING A SATURATION PRESSURE GREATER THAN  AMBIENT
            PRESSURE</div>
          <div><br>
          </div>
          <div><br>
          </div>
          <div> ***** ERROR *****        TRNSYS ERROR # 116</div>
          <div> UNIT  64 TYPE 667</div>
          <div> THE PSYCHROMETRICS SUBROUTINE WAS CALLED WITH CONDITIONS</div>
          <div> YIELDING A SATURATION PRESSURE GREATER THAN  AMBIENT
            PRESSURE</div>
        </div>
        <div>Please help me<br>
          regards,</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>