<p>Ravindra,</p>
<p> Models for the expansion valve and heat exchangers for vapor
compression cycles don't exist in TRNSYS as far as I am aware. In
order to write such a model you would need to know what
refrigerant is being used in the cycle and you'd need a routine to
give you refrigerant properties.</p>
<p> I am not sure if TRNSYS is the right tool to use to model a
vapor compression cycle. Typically we work with systems in TRNSYS
that have transient behavior on the order of a minute or longer.
The transients in the individual components of a vapor compression
cycle are much shorter than that. At one minute intervals such a
refrigeration cycle looks quite steady state and so we typically
use performance maps to model them. When I need to look inside the
cycle, I typically use a program called EES (Engineering Equation
Solver).</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<br>
<div class="moz-cite-prefix">On 06/30/2017 01:51, v ravindra via
TRNSYS-users wrote:<br>
</div>
<blockquote type="cite"
cite="mid:CADb1Z3Lvve+hoPCrhAC92i-XJYX-yQY_o=VP0aHw3zWdBr7SUg@mail.gmail.com">
<div dir="ltr"><span style="font-size:12.8px">Which component
(Type) can i use to represent a Suction line heat exchanger
having sub cooling and super heating while setting up a Vapour
compression cycle in TRNSYS 17.</span>
<div><span style="font-size:12.8px"><br clear="all">
</span>
<div>
<div class="gmail_signature">
<div dir="ltr">
<div dir="ltr">V.Ravindra<br>
<br>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>