    <p>Mohamed,</p>
    <p>  There are two ways that you can do it. If you are trying to
      model a tempering valve (a device that prevents one stream of
      liquid from overheating by mixing in some colder liquid) then you
      can use Type11. Look in the 04-MathematicalReference manual and it
      will give you an example of how to model it.</p>
    <p>  If you have a more general case and you want to know in what
      ratio to mix the liquids to obtain a certain mixed temperature
      then the ratio can be computed based on knowing the temperatures.
      Once you solve the mathematics, you can then implement them as an
      equation in your input file. Use the ratio as the control signal
      to a mixing valve model.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 05/31/2017 02:26, Mohamed Kaheal via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAJTneOTtA9sHZZKMX0J=dYPkj6YBE8BBodgzttA8mqf+HD8bFQ@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello TRNSYS team,
        <div><br>
        </div>
        <div>I would like to mix two streams of fluids. the temperature
          of the fluids are known. the flow rate of the first stream is
          fixed. I need to take part of the second stream to mix it with
          the first stream in order to reach to some specific
          temperature values. Could you please tell me how can I do
          that. Any help will be appreciated </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>Thanks a lot</div>
        <div>Mohamed</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>