<div dir="ltr">Jeff,<br><br>You are right, the monitored value won't change as temperatures do. I will check on your solution. Thank you very much.<div><br></div><div>Best regards,</div><div>Javier</div></div><div class="gmail_extra"><br><div class="gmail_quote">2017-06-02 9:52 GMT-04:00 Jeff Thornton <span dir="ltr"><<a href="mailto:thornton@tess-inc.com" target="_blank">thornton@tess-inc.com</a>></span>:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">Javier,<br>
<br>
Since the value you are watching won't change with the control decision, you don't need a controller with hysteresis.  I would simply use an equation:<br>
<br>
Glim = 1000<br>
On_Controller = GE(IncidentRadiation,Glim)<br>
<br>
where the incident radiation is an input to the equation component.<br>
<br>
Jeff - TESS<br>
<br>
Sent from my iPhone<br>
<br>
> On Jun 2, 2017, at 8:27 AM, Javier Vega via TRNSYS-users <<a href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.<wbr>onebuilding.org</a>> wrote:<br>
><br>
> Hello TRNSYS users,<br>
><br>
> I want to set a control strategy for my system based on the amount of solar radiation on a certain surface. It is simple, if the total radiation on the surface is below a Glim, I need the controller to output 1. If the total solar radiation is above Glim, set 0. The controller output will be used to divide a certain flow.<br>
><br>
> Which controller would you recommend? Is the differential controller Type 2d (Generic) convenient for this case? I'm using the succesive substitution method.<br>
><br>
> Thanks in advance for your advice,<br>
> Javier Vega<br>
> ______________________________<wbr>_________________<br>
> TRNSYS-users mailing list<br>
> <a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.<wbr>onebuilding.org</a><br>
> <a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
<br>
</blockquote></div><br></div>