    <p>Over the course of the year usually the energy balance works out
      fairly well. However, if there is a difference in the amount of
      energy stored in the tank at the beginning of the simulation and
      at the end of the simulation, you have to account for that in your
      energy balance. Type4 has an output for this value. Also, it may
      be that you are adding auxiliary energy to the tank. Type4 has a
      number of modes in which it can automatically keep itself at a set
      point temperatures.<br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 05/12/2017 23:27, Rm Chemilo via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAGdzsCrQUMuLjoMPu_snU8HT9Sacs9xdfZ5vsCKSqvXPYGOWrQ@mail.gmail.com"
      type="cite">
      <div dir="auto">Dear all,
        <div dir="auto"><br>
        </div>
        <div dir="auto">I'm doing simulation for domestic water heating
          by using solar collector, hx, and storage tank(without
          auxiliary heater). Then after plotting storage tank energy
          balance for one year, I found heat in 874 MWh, heat out
          811MWh, thermal losses 101MWh. Why the thermal losses is not
          qin-qout? Can anyone help me?</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Thanks</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>