    <p>Yang,</p>
    <p>  There is no difference in functionality between the commercial
      and education versions; the only difference is a price discount
      offered to degree-granting institutions.</p>
    <p>  In order to simulation the ground source heat pumps you'll need
      the TESS GHP library. You can model the boilers with standard
      components in the Trnsys18 library. There are a number of models
      in the TESS HVAC, controls, and hydronics libraries that might be
      helpful as well in modeling the balance of system.</p>
    <p>  Without knowing more about the specifics of your smart grid, it
      is hard to suggest a particular Type. I think that you would be
      able to model such technologies using equations. If not then
      Trnsys18 includes a built-in utility for writing new Types so you
      could consider writing your own component.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 05/02/2017 11:14, WANG Yang via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CABF0dEsfKNkFFAXKVOa68dbEQmTe7zoALYB4w25txdEzs00=YA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Dear all,
        <div><br>
        </div>
        <div>I'd like to ask you what difference for functions etc. is
          between education and commercial versions?</div>
        <div><br>
        </div>
        <div>If I want to simulate electricity (smart grids) and heat
          (ground source heat pump and conventional boilers) networks
          for 2 buildings, which type/components should I use?</div>
        <div><br>
        </div>
        <div>Many thanks</div>
        <div><br>
        </div>
        <div>Br.</div>
        <div><br>
        </div>
        <div>Yang <br>
          <div class="gmail_extra"><br>
            <div class="gmail_quote">2017-05-01 21:11 GMT+01:00 via
              TRNSYS-users <span dir="ltr"><<a
                  moz-do-not-send="true"
                  href="mailto:trnsys-users@lists.onebuilding.org"
                  target="_blank">trnsys-users@lists.onebuilding.org</a>></span>:<br>
              <blockquote class="gmail_quote" style="margin:0 0 0
                .8ex;border-left:1px #ccc solid;padding-left:1ex">Send
                TRNSYS-users mailing list submissions to<br>
                        <a moz-do-not-send="true"
                  href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.<wbr>onebuilding.org</a><br>
                <br>
                To subscribe or unsubscribe via the World Wide Web,
                visit<br>
                        <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                  rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
                <br>
                or, via email, send a message with subject or body
                'help' to<br>
                        <a moz-do-not-send="true"
                  href="mailto:trnsys-users-request@lists.onebuilding.org">trnsys-users-request@lists.<wbr>onebuilding.org</a><br>
                <br>
                You can reach the person managing the list at<br>
                        <a moz-do-not-send="true"
                  href="mailto:trnsys-users-owner@lists.onebuilding.org">trnsys-users-owner@lists.<wbr>onebuilding.org</a><br>
                <br>
                When replying, please edit your Subject line so it is
                more specific<br>
                than "Re: Contents of TRNSYS-users digest..."<br>
                <br>
                Today's Topics:<br>
                <br>
                   1. Re: Type 1246 and type 697 (Jeff Thornton via
                TRNSYS-users)<br>
                   2. Re: Type 1246 and type 697 (Raouf Bilal via
                TRNSYS-users)<br>
                <br>
                <br>
                ---------- 已转发邮件 ----------<br>
                From: Jeff Thornton via TRNSYS-users <<a
                  moz-do-not-send="true"
                  href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>><br>
                To: <a moz-do-not-send="true"
                  href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a><br>
                Cc: <br>
                Bcc: <br>
                Date: Sun, 30 Apr 2017 18:26:20 -0500<br>
                Subject: Re: [TRNSYS-users] Type 1246 and type 697<br>
                <div>
                  <p>Type 1246 and Type 697 are part of the TESS HVAC
                    Library add-on for TRNSYS.  Ordering details can be
                    found online at <a moz-do-not-send="true"
                      href="http://www.trnsys.com" target="_blank">www.trnsys.com</a>.</p>
                  <p> </p>
                  <p>Jeff</p>
                  <p> </p>
                  <div>
                    <pre>---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: <a moz-do-not-send="true" href="tel:%28608%29%20274-2577" value="+16082742577" target="_blank">(608) 274-2577</a>  Fax: <a moz-do-not-send="true" href="tel:%28608%29%20278-1475" value="+16082781475" target="_blank">(608) 278-1475</a>
<a moz-do-not-send="true" href="http://www.tess-inc.com" target="_blank">www.tess-inc.com</a>
E-Mail: <a moz-do-not-send="true" href="mailto:thornton@tess-inc.com" target="_blank">thornton@tess-inc.com</a>
</pre>
                  </div>
                  <p>On 04/29/2017 8:27 am, Raouf Bilal via TRNSYS-users
                    wrote:</p>
                  <blockquote type="cite"
                    style="padding-left:5px;border-left:#1010ff 2px
                    solid;margin-left:5px">
                    <div dir="ltr">
                      <div
class="m_-4381351341454684708gmail-m_1059913969974995880yiv0931541147gmail_default"
style="font-size:12.8px;font-family:tahoma,sans-serif;color:#000000">Dear
                        colleagues,</div>
                      <div> </div>
                      <div>Where i can find the type 1246 (axilary
                        cooler) and type 69 (performance map cooling
                        coil) in trnsys 17</div>
                      <div> </div>
                      <div>Raouf Bilal</div>
                      <div> </div>
                      <div> </div>
                    </div>
                    <br>
                    <pre>______________________________<wbr>_________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.<wbr>onebuilding.org</a>
<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a>
</pre>
</blockquote>
</div>


---------- 已转发邮件 ----------
From: Raouf Bilal via TRNSYS-users <<a moz-do-not-send="true" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>>
To: <a moz-do-not-send="true" href="mailto:thornton@tess-inc.com">thornton@tess-inc.com</a>, "TRNSYS users mailing list at OneBuilding.org" <<a moz-do-not-send="true" href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>>
Cc: 
Bcc: 
Date: Mon, 1 May 2017 12:35:25 +0100
Subject: Re: [TRNSYS-users] Type 1246 and type 697
<div dir="ltr">Thank you, i find the both types</div><div class="gmail_extra">
<div class="gmail_quote">2017-05-01 0:26 GMT+01:00 Jeff Thornton via TRNSYS-users <span dir="ltr"><<a moz-do-not-send="true" href="mailto:trnsys-users@lists.onebuilding.org" target="_blank">trnsys-users@lists.<wbr>onebuilding.org</a>></span>:
<blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div>
<p>Type 1246 and Type 697 are part of the TESS HVAC Library add-on for TRNSYS.  Ordering details can be found online at <a moz-do-not-send="true" href="http://www.trnsys.com" target="_blank">www.trnsys.com</a>.</p>
<p> </p>
<p>Jeff</p>
<p> </p>
<div>
<pre>---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: <a moz-do-not-send="true" href="tel:%28608%29%20274-2577" value="+16082742577" target="_blank">(608) 274-2577</a>  Fax: <a moz-do-not-send="true" href="tel:%28608%29%20278-1475" value="+16082781475" target="_blank">(608) 278-1475</a>
<a moz-do-not-send="true" href="http://www.tess-inc.com" target="_blank">www.tess-inc.com</a>
E-Mail: <a moz-do-not-send="true" href="mailto:thornton@tess-inc.com" target="_blank">thornton@tess-inc.com</a>
</pre>
</div><div><div class="m_-5089328855906020747h5">
<p>On 04/29/2017 8:27 am, Raouf Bilal via TRNSYS-users wrote:</p>
</div></div><blockquote type="cite" style="padding-left:5px;border-left:#1010ff 2px solid;margin-left:5px"><div><div class="m_-5089328855906020747h5">
<div dir="ltr">
<div class="m_-5089328855906020747m_7766380486500005202gmail-m_1059913969974995880yiv0931541147gmail_default" style="font-size:12.8px;font-family:tahoma,sans-serif;color:#000000">Dear colleagues,</div>
<div> </div>
<div>Where i can find the type 1246 (axilary cooler) and type 69 (performance map cooling coil) in trnsys 17</div>
<div> </div>
<div>Raouf Bilal</div>
<div> </div>
<div> </div>
</div>


</div></div><pre>______________________________<wbr>_________________
TRNSYS-users mailing list
<a moz-do-not-send="true" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding<wbr>.org</a>
<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/l<wbr>istinfo.cgi/trnsys-users-onebu<wbr>ilding.org</a>
</pre>
</blockquote>
</div>

______________________________<wbr>_________________

TRNSYS-users mailing list

<a moz-do-not-send="true" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.onebuilding<wbr>.org</a>

<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/l<wbr>istinfo.cgi/trnsys-users-onebu<wbr>ilding.org</a>


</blockquote></div>
</div>

______________________________<wbr>_________________

TRNSYS-users mailing list

<a moz-do-not-send="true" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.<wbr>onebuilding.org</a>

<a moz-do-not-send="true" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a>


</blockquote></div>
</div></div></div>


<fieldset class="mimeAttachmentHeader"></fieldset>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>

</blockquote>
<pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre></body></html>