<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <p>Rasyiddin,</p>
    <p>  The equation dq/dt = m*Cp*dT/dt is derived with the assumption
      that the specific heat is constant over the temperature range. If
      the specific heat is not constant over the temperature range then
      you would have to rederive all of the energy transfer terms in the
      effected Types to account for the dCp/dt term. You would then need
      to modify the Types' source code and recompile. <br>
    </p>
    <p>  There are some components in the TESS High Temperature Solar
      library that allow Cp to change. If you have access to that
      library, it might be worth a look.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 05/01/2017 23:17, Rasyiddin Muhammad
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CADru2nh1Je0htW1EAJiweKTToxeXtHvY9oiKAU8w23w1noTRtA@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi,
        <div><br>
        </div>
        <div>I am trying to change the fluid for a solar thermal system
          from water to therminol 66. Thus, I would like to change the
          specific heat capacity to a function of temperature instead of
          having a single average value. </div>
        <div>Is there a way that I can do this?<br>
        </div>
        <div><br>
        </div>
        <div>Also is there a way that I can change the fluid properties
          for the whole system so that I would not have to change the
          fluid properties for each component?</div>
        <div><br>
        </div>
        <div>Any help would be appreciated.</div>
        <div>Thanks!</div>
        <div><br>
        </div>
        <div>Rasyiddin </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>