    <p>Grégoire,</p>
    <p>  A 30% oversize on necessary heating capacity is not unusual in
      US HVAC design practice. I will refrain from adding personal
      opinions about whether this is a good practice or not. ASHRAE 90.1
      suggests a 25% oversize in their Appendix G. <br>
    </p>
    <p><br>
    </p>
    <p>  You mention that you have sized the heating based on envelope
      losses and infiltration. Don't forget that there is also usually
      some fresh air that must be supplied to a space and that air must
      also be conditioned (ie be part of your heating capacity).</p>
    <p> </p>
    <p>  The recovery time also has a good bit to do with the thermal
      capacity of a zone and of the delivery systems. In some work that
      we have done on radiant floor systems we have seen that aggressive
      night time setbacks are a bad idea because the thermal flywheel of
      the radiant floor becomes very hard to control.</p>
    <p><br>
    </p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 04/26/2017 06:48, Greg B via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:AM5PR0901MB0852D9E1DDEF61FF6F0E99D3F4110@AM5PR0901MB0852.eurprd09.prod.outlook.com"
      type="cite">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <style type="text/css" style="display:none;"><!-- P {margin-top:0;margin-bottom:0;} --></style>
      <div id="divtagdefaultwrapper" dir="ltr" style="font-size:12pt;
        color:#000000; font-family:Calibri,Arial,Helvetica,sans-serif">
        <p>Hello,</p>
        <p><br>
        </p>
        <p>I'm currently modeling an old terraced building (construction
          type bricks / 8 zones / North Europa - Belgium) with a certain
          level of refurbishement (let's say an overall of 8cm
          insulation). I designed the heating power of the different
          zones, in the heating manger of type 56 in limited power,
          based on the heating losses by transmission and infiltration
          (design temperatures :  internal temp 20°C / external -10°C).
          But when I launch the simulation in winter in a intermittent
          set point scenario (0h-6h : 16°C 6-8h: 20°C 8h-15h :16°C
          15h-22h:20°C 22h-0h :16°C) the recovery time is very high and
          in some cases it is not even possible to reach the high set
          point even after more than 8 hours.</p>
        <p><br>
        </p>
        <p>I don't know if some of you experienced this same problem
          (such long recovery times)? I read in most of documentations
          that I have to oversize the heating power in order to have a
          reasonnable recovery time (let's say between 1 or 2 hours to
          reach the high set temperature). When I do this I have to
          oversize at least 30% of the original power and this seems
          quiet high, isn't it? Any idea or doucmentation about a such
          issue?</p>
        <p><br>
        </p>
        <p>Thank you in adavance.</p>
        <p><br>
        </p>
        <p>Best regards,</p>
        <p><br>
        </p>
        <p>Grégoire</p>
        <p><br>
        </p>
        <p> </p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>