<p>Francesca,</p>
<p> Instead of defining a VENTILATION type that has inputs for the
mass flow rate, air temperature and air humidity in TRNBuild you
will define an active layer in TRNBuild and you will indicate that
the mass flow rate and temperature of liquid entering the active
layer are inputs to Type56.</p>
<p>kind regards,</p>
<p> David</p>
<p><br>
</p>
<br>
<div class="moz-cite-prefix">On 03/28/2017 05:20, francesca lorusso
via TRNSYS-users wrote:<br>
</div>
<blockquote
cite="mid:CAKqUUv+Y1_6FGL0ErD__nq+Ft4NVp=CnWK2X70gn6vxgt4u9=Q@mail.gmail.com"
type="cite">
<div dir="ltr"><br clear="all">
<div>Dear all,</div>
<div>concerning the tutorial "temperature level control from
energy rate control.", what does it change, if i have to make
control temperature with heating/cooling system and not with
ventilation one? I create an active layer as a radiant floor
and I want to link my heating system (in simulation studio)
with my building (TRNbuilding).</div>
<div><br>
</div>
<div>Best regards,</div>
<div>Francesca</div>
<div class="gmail_signature"><br>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
<br>
<pre class="moz-signature" cols="72">--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
</body>
</html>