<div dir="ltr">Dear David and Ahamd,<div>if i want to make a temperature control with active layer how i have to manage heating and cooling in the trnbuilding file?</div><div><br></div><div>Beste regards,</div><div>francesca</div></div><div class="gmail_extra"><br><div class="gmail_quote">2017-02-09 17:30 GMT+01:00 David BRADLEY via TRNSYS-users <span dir="ltr"><<a href="mailto:trnsys-users@lists.onebuilding.org" target="_blank">trnsys-users@lists.onebuilding.org</a>></span>:<br><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF" text="#000000">
    <p>Ahmad <br>
    </p>
    <p>  I am not aware of such an example or tutorial. However, the
      principal is the same as for controlling temperature. Define a
      humidistat that watches the zone RH or humidity ratio then pass
      the humidistat's outputs to appropriate
      humidification/<wbr>dehumidification equipment that acts on the air
      stream that is introduced into the zone.</p>
    <p>kind regards,</p>
    <p> David</p><div><div class="h5">
    <p><br>
    </p>
    <br>
    <div class="m_-1023093539308046093moz-cite-prefix">On 02/09/2017 09:20, ahmad abbasian
      wrote:<br>
    </div>
    <blockquote type="cite">
      
      
      <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;font-family:Calibri,Arial,Helvetica,sans-serif" dir="ltr">
        <p>Dear David</p>
        <p><br>
        </p>
        <p>Thank you very much for the useful links. Now I know  how to
          control the temperature of a building. Is there any example of
          controlling the humidity also?</p>
        <p><br>
        </p>
        <p>Thank you</p>
        <p><br>
        </p>
        <div id="m_-1023093539308046093Signature">
          <div id="m_-1023093539308046093divtagdefaultwrapper" dir="ltr" style="font-size:12pt;color:#000000;font-family:Calibri,Arial,Helvetica,sans-serif">
            <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
..............................<wbr>..............................<wbr>..............................<wbr>....</div>
            <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
              Ahmad abbasianzadeh</div>
            <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
              Solar energy Researcher</div>
            <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
              <b>Harrisburg, Pensylvania</b></div>
            <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
              <br>
            </div>
            <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
              <br>
            </div>
            <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
               </div>
          </div>
        </div>
      </div>
      <hr style="display:inline-block;width:98%">
      <div id="m_-1023093539308046093divRplyFwdMsg" dir="ltr"><font style="font-size:11pt" face="Calibri, sans-serif" color="#000000"><b>From:</b> David
          BRADLEY <a class="m_-1023093539308046093moz-txt-link-rfc2396E" href="mailto:d.bradley@tess-inc.com" target="_blank"><d.bradley@tess-inc.com></a><br>
          <b>Sent:</b> Tuesday, February 7, 2017 11:33:57 AM<br>
          <b>To:</b> ahmad abbasian; TRNSYS users mailing list at
          OneBuilding.org; <a class="m_-1023093539308046093moz-txt-link-abbreviated" href="mailto:thornton@tess-inc.com" target="_blank">thornton@tess-inc.com</a><br>
          <b>Subject:</b> Re: [TRNSYS-users] how to control HVAC ?</font>
        <div> </div>
      </div>
      <div>
        <p>Ahmad,</p>
        <p> I would recommend that you download the tutorial called
          "Temperature Level Control from Energy Rate Control " at:<br>
        </p>
        <p><br>
        </p>
        <p><a class="m_-1023093539308046093moz-txt-link-freetext" href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex17.htm" target="_blank">http://sel.me.wisc.edu/trnsys/<wbr>downloads/tutorials_and_<wbr>examples/tutex17.htm</a></p>
        <p><br>
        </p>
        <p>or if you are using v16</p>
        <p><br>
        </p>
        <p><a class="m_-1023093539308046093moz-txt-link-freetext" href="http://sel.me.wisc.edu/trnsys/downloads/tutorials_and_examples/tutex.htm" target="_blank">http://sel.me.wisc.edu/trnsys/<wbr>downloads/tutorials_and_<wbr>examples/tutex.htm</a></p>
        <p><br>
        </p>
        <p>It will explain some of the differences between calculating a
          building load and simulating the performance of HVAC systems.
          It will also lead you through an example of converting a load
          computation simulation into an HVAC system simulation.</p>
        <p>kind regards,</p>
        <p> David</p>
        <p><br>
        </p>
        <p><br>
        </p>
        <br>
        <div class="m_-1023093539308046093moz-cite-prefix">On 02/07/2017 13:34, ahmad abbasian
          via TRNSYS-users wrote:<br>
        </div>
        <blockquote type="cite">
          
          <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;font-family:Calibri,Arial,Helvetica,sans-serif" dir="ltr">
            <p>Dear Jeff</p>
            <p>Thank you for your guiding. I have simulated my HVAC
              system at nominal condition, alone not using the building
              model. Now I'm going to use this system connected to a
              building. Now my question is how should I match the HVAC
              cooling production to the building load which is
              transient? should I control the temperature and humidity
              also or just the flow rate should be controlled to meet
              the load? </p>
            <p>I couldn't find a similar example in TRNSYS examples.
              Could you send me an example in case of having some
              please?</p>
            <p>Thank you</p>
            <div id="m_-1023093539308046093Signature">
              <div id="m_-1023093539308046093divtagdefaultwrapper" dir="ltr" style="font-size:12pt;color:#000000;font-family:Calibri,Arial,Helvetica,sans-serif">
                <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
..............................<wbr>..............................<wbr>..............................<wbr>....</div>
                <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                  Ahmad abbasianzadeh</div>
                <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                  Solar energy Researcher</div>
                <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                  <b>Harrisburg, Pensylvania</b></div>
                <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                  <br>
                </div>
                <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                  <br>
                </div>
                <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                   </div>
              </div>
            </div>
          </div>
          <hr style="display:inline-block;width:98%">
          <div id="m_-1023093539308046093divRplyFwdMsg" dir="ltr"><font style="font-size:11pt" face="Calibri, sans-serif" color="#000000"><b>From:</b>
              TRNSYS-users
              <a class="m_-1023093539308046093moz-txt-link-rfc2396E" href="mailto:trnsys-users-bounces@lists.onebuilding.org" target="_blank">
                <trnsys-users-bounces@lists.<wbr>onebuilding.org></a>
              on behalf of Jeff Thornton via TRNSYS-users
              <a class="m_-1023093539308046093moz-txt-link-rfc2396E" href="mailto:trnsys-users@lists.onebuilding.org" target="_blank">
                <trnsys-users@lists.<wbr>onebuilding.org></a><br>
              <b>Sent:</b> Tuesday, February 7, 2017 7:09:11 AM<br>
              <b>To:</b> <a class="m_-1023093539308046093moz-txt-link-abbreviated" href="mailto:trnsys-users@lists.onebuilding.org" target="_blank">
                trnsys-users@lists.<wbr>onebuilding.org</a><br>
              <b>Subject:</b> Re: [TRNSYS-users] how to control HVAC ?</font>
            <div> </div>
          </div>
          <div>
            <p>Ahmad,</p>
            <p>There are literally hundreds of ways to control the
              temperature and humidity in a space.  I would suggest you
              do some reading to figure out a common HVAC system given
              your climate and type of building - then you can begin to
              replicate that system in TRNSYS. 
            </p>
            <p> </p>
            <p>Jeff</p>
            <p> </p>
            <div>
              <pre>---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: <a href="tel:(608)%20274-2577" value="+16082742577" target="_blank">(608) 274-2577</a>  Fax: <a href="tel:(608)%20278-1475" value="+16082781475" target="_blank">(608) 278-1475</a>
<a class="m_-1023093539308046093moz-txt-link-abbreviated" href="http://www.tess-inc.com" target="_blank">www.tess-inc.com</a>
E-Mail: <a class="m_-1023093539308046093moz-txt-link-abbreviated" href="mailto:thornton@tess-inc.com" target="_blank">thornton@tess-inc.com</a>
</pre>
            </div>
            <p>On 02/07/2017 12:08 pm, ahmad abbasian via TRNSYS-users
              wrote:</p>
            <blockquote type="cite" style="padding-left:5px;border-left:#1010ff 2px solid;margin-left:5px">
              
              <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;font-family:Calibri,Arial,Helvetica,sans-serif" dir="ltr">
                <p>Hello</p>
                <p>I'm simulating a solar assisted coolig system for a
                  building. The building cooling load is transient. so
                  how the HVAC system should be controlled to cover the
                  building load? I guess that the supply air temperature
                  and humidity ratio should be constant ( a value in the
                  comfort region ) and the air flow rate should be
                  controlled using a variable speed fan to cover the
                  cooling load. Is it right? any better idea?</p>
                <p>Also I don't know how the control system should be?
                  should I use a thermostat? </p>
                <p>If any one can send me an example it will be very
                  useful for me to learn</p>
                <p>Thank you </p>
                <p> </p>
                <div id="m_-1023093539308046093Signature">
                  <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;font-family:Calibri,Arial,Helvetica,sans-serif" dir="ltr">
                    <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
..............................<wbr>..............................<wbr>..............................<wbr>....</div>
                    <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                      Ahmad abbasianzadeh</div>
                    <div id="m_-1023093539308046093divtagdefaultwrapper" style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                      master of energy systems engineering</div>
                    <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                      Solar energy Researcher</div>
                    <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                      <strong>Harrisburg, Pensylvania</strong></div>
                    <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                       </div>
                    <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                       </div>
                    <div style="font-size:12pt;color:#000000;background-color:#ffffff;font-family:Calibri,Arial,Helvetica,sans-serif">
                       </div>
                  </div>
                </div>
              </div>
              <br>
              <pre>______________________________<wbr>_________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.<wbr>onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a>
</pre>
            </blockquote>
          </div>
          <br>
          <fieldset class="m_-1023093539308046093mimeAttachmentHeader"></fieldset>
          <br>
          <pre>______________________________<wbr>_________________
TRNSYS-users mailing list
<a class="m_-1023093539308046093moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org" target="_blank">TRNSYS-users@lists.<wbr>onebuilding.org</a>
<a class="m_-1023093539308046093moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a>
</pre>
        </blockquote>
        <br>
        <pre class="m_-1023093539308046093moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:<a href="tel:(608)%20274-2577" value="+16082742577" target="_blank">+1.608.274.2577</a>
F:<a href="tel:(608)%20278-1475" value="+16082781475" target="_blank">+1.608.278.1475</a>
<a class="m_-1023093539308046093moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a class="m_-1023093539308046093moz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a class="m_-1023093539308046093moz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
      </div>
    </blockquote>
    <br>
    <pre class="m_-1023093539308046093moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:<a href="tel:(608)%20274-2577" value="+16082742577" target="_blank">+1.608.274.2577</a>
F:<a href="tel:(608)%20278-1475" value="+16082781475" target="_blank">+1.608.278.1475</a>
<a class="m_-1023093539308046093moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com" target="_blank">d.bradley@tess-inc.com</a>

<a class="m_-1023093539308046093moz-txt-link-freetext" href="http://www.tess-inc.com" target="_blank">http://www.tess-inc.com</a>
<a class="m_-1023093539308046093moz-txt-link-freetext" href="http://www.trnsys.com" target="_blank">http://www.trnsys.com</a></pre>
  </div></div></div>

<br>______________________________<wbr>_________________<br>
TRNSYS-users mailing list<br>
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.<wbr>onebuilding.org</a><br>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org" rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
<br></blockquote></div><br><br clear="all"><div><br></div>-- <br><div class="gmail_signature" data-smartmail="gmail_signature"><i style="font-family:garamond,serif"><u><b>FRANCESCA LORUSSO<span style="background-color:rgb(102,102,102)"></span></b></u></i><br></div>
</div>