<html>
  <head>
    <meta content="text/html; charset=windows-1252"
      http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <p>Arian,</p>
    <p>  There could be many reasons for this. For example, if you have
      heating and cooling enabled in your building so that the zone
      temperature is forced to always be between 20C and 21C then
      regardless of the timestep and whether or not you interpolate the
      weather file the building temperature is always going to be
      between 20 and 21C.</p>
    <p>regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 03/07/2017 11:34, Arian Bahrami via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
      cite="mid:9B1F528A-93CB-4A77-A326-6D052818A188@yahoo.com"
      type="cite">
      <meta http-equiv="content-type" content="text/html;
        charset=windows-1252">
      <div>Dear Jeff</div>
      <div id="AppleMailSignature"><br>
      </div>
      <div id="AppleMailSignature">I am using TRNSYS 16. I only used
        Type 109-TMY2 and when I changed the time step to less than 1
        hour, like min or s , the output result which is the indoor
        temperature of the building type 56 is the same as 1 hour even
        to the last digit.</div>
      <div id="AppleMailSignature"><br>
      </div>
      <div id="AppleMailSignature">Best Regards,</div>
      <div id="AppleMailSignature"><br>
      </div>
      <div id="AppleMailSignature">Arian<br>
        <br>
        Sent from my iPhone</div>
      <div><br>
        On 7 Mar 2017, at 6:19 pm, Jeff Thornton via TRNSYS-users <<a
          moz-do-not-send="true"
          href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>>
        wrote:<br>
        <br>
      </div>
      <blockquote type="cite">
        <div>
          <meta http-equiv="content-type" content="text/html;
            charset=windows-1252">
          <div>The TRNSYS weather components all have interpolation
            schemes built into the models for seamless simulations at
            time steps less than an hour.</div>
          <div id="AppleMailSignature"><br>
          </div>
          <div id="AppleMailSignature">Jeff / TESS</div>
          <div id="AppleMailSignature"><br>
            Sent from my iPhone</div>
          <div><br>
            On Mar 7, 2017, at 9:55 AM, Amirreza Heidary via
            TRNSYS-users <<a moz-do-not-send="true"
              href="mailto:trnsys-users@lists.onebuilding.org">trnsys-users@lists.onebuilding.org</a>>
            wrote:<br>
            <br>
          </div>
          <blockquote type="cite">
            <div>
              <div dir="ltr">DearArian
                <div>you can use excell or EES and develope an
                  interpolation code <br>
                  <br>
                  <br>
                  <br>
                  <div class="mt-signature">
                    <div class="mt-signature-inner"> <a
                        moz-do-not-send="true"
                        href="https://mailtrack.io/"
                        class="mt-signature-logo"
                        style="text-decoration:none"> <img
                          moz-do-not-send="true"
src="https://s3-eu-west-1.amazonaws.com/mailtrack-crx/icon-signature.png"
                          height="14">  </a> <font
                        class="mt-signature-text" color="#999999"> Sent
                        with <a moz-do-not-send="true"
href="https://mailtrack.io/install?source=signature&lang=en&referral=amirrezaheidarysbu@gmail.com&idSignature=22"
                          class="mt-install">Mailtrack</a> </font> </div>
                  </div>
                </div>
                <img moz-do-not-send="true" class="mailtrack-img"
src="https://mailtrack.io/trace/mail/7273acba1defefe2fa2eb43651eeb19e23ca1f52.png?u=1249159"
                  height="0" width="0"></div>
              <div class="gmail_extra"><br clear="all">
                <div>
                  <div class="gmail_signature"
                    data-smartmail="gmail_signature">
                    <div dir="ltr">
                      <div>
                        <div dir="ltr">
                          <div>
                            <div dir="ltr">
                              <div>
                                <div dir="ltr">
                                  <div>
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div>
                                          <div style="text-align:right">
                                            <div style="text-align:left"><br>
                                            </div>
                                            <div style="text-align:left">--------------------------------------------------------------------------------------------------------------------------------------------------<br>
                                              <img
                                                moz-do-not-send="true"
src="https://docs.google.com/uc?id=0B56a_joPrCZuYUg5aFkzTlR2dTg&export=download"
                                                height="96" width="96"><br>
                                            </div>
                                            <div
                                              style="text-align:left;font-size:12.8px"><b><font
                                                  face="georgia, serif">amirrezaheidary</font></b></div>
                                            <div
                                              style="text-align:left;font-size:12.8px"><i><font
                                                  face="trebuchet ms,
                                                  sans-serif"
                                                  color="#444444">master
                                                  student of energy
                                                  systems Engineering</font></i></div>
                                            <div
                                              style="text-align:left;font-size:12.8px"><font
                                                face="trebuchet ms,
                                                sans-serif"
                                                color="#444444"><i>Sharif
                                                  university of
                                                  technology</i></font></div>
                                            <div
                                              style="text-align:left;font-size:12.8px"><font
                                                face="trebuchet ms,
                                                sans-serif"
                                                color="#444444"><i>Tehran-Iran</i></font></div>
                                            <div
                                              style="text-align:left;font-size:12.8px"><font
                                                face="georgia, serif"><i>E-mail
                                                  address</i></font><font
                                                face="comic sans ms,
                                                sans-serif">:</font></div>
                                            <blockquote
                                              style="margin:0px 0px 0px
0.8ex;padding-left:1ex;font-size:12.8px;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid">
                                              <p style="text-align:left"><font
                                                  face="tahoma,
                                                  sans-serif"
                                                  color="#1155cc"><a
                                                    moz-do-not-send="true"
href="mailto:heidari@energy.sharif.edu" target="_blank">heidari@energy.sharif.edu</a></font></p>
                                            </blockquote>
                                            <blockquote
                                              style="margin:0px 0px 0px
0.8ex;padding-left:1ex;font-size:12.8px;border-left-color:rgb(204,204,204);border-left-width:1px;border-left-style:solid">
                                              <p style="text-align:left"><font
style="color:rgb(17,85,204)" face="tahoma, sans-serif"><a
                                                    moz-do-not-send="true"
style="color:rgb(17,85,204)" href="mailto:sm_mousavi@pwut.ac.ir"
                                                    target="_blank">a</a><a
moz-do-not-send="true" href="mailto:mirrezaheidarysbu@gmail.com"
                                                    target="_blank">mirrezaheidarysbu@gmail.com</a></font></p>
                                            </blockquote>
                                            <div style="text-align:left"><b
style="color:rgb(0,0,0);font-family:"times new
                                                roman","new
                                                york",times,serif;font-size:small"><span
style="color:green;font-family:Webdings" lang="EN-GB">P</span></b><i
                                                style="color:rgb(0,0,0);font-family:"times
                                                new
                                                roman","new
                                                york",times,serif;font-size:small"><span
                                                  style="color:navy"
                                                  lang="EN-GB"> </span></i><b
style="color:rgb(0,0,0);font-family:"times new
                                                roman","new
                                                york",times,serif;font-size:small"><i><span
                                                    style="color:green"
                                                    lang="EN-GB">Save a
                                                    tree... Please don't
                                                    print this E-mail
                                                    unless you really
                                                    need to.</span></i></b><b><font
                                                  color="#0000ff"><font
                                                    size="1">           
                                                                       
                                                                       
                                                                       
                                                                       
                                                                       
                                                                  </font></font></b><br>
                                            </div>
                                            <br>
                                          </div>
                                          <font color="#0000ff"><font
                                              size="1"><br>
                                            </font></font></div>
                                        <div><font color="#0000ff"><font
                                              size="1"><br>
                                            </font></font>
                                          <div>
                                            <div><font color="#0000ff"><font
                                                  size="1"><br>
                                                </font></font></div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
                <br>
                <div class="gmail_quote">On Tue, Mar 7, 2017 at 8:04 PM,
                  Arian Bahrami via TRNSYS-users <span dir="ltr"><<a
                      moz-do-not-send="true"
                      href="mailto:trnsys-users@lists.onebuilding.org"
                      target="_blank">trnsys-users@lists.onebuilding.org</a>></span>
                  wrote:<br>
                  <blockquote class="gmail_quote" style="margin:0 0 0
                    .8ex;border-left:1px #ccc solid;padding-left:1ex">Dear
                    all,<br>
                    <br>
                    I want to know whether TRNSYS has a default
                    interpolating weather data component like EnergyPlus
                    since most of the solar data is hourly and as I see,
                    TRNSY can simulate in smaller time step such as min
                    and s. So, Is there way to accomplished such a
                    thing.<br>
                    <br>
                    Best Regards,<br>
                    <br>
                    Arian.<br>
                    <br>
                    Sent from my iPhone<br>
                    ______________________________<wbr>_________________<br>
                    TRNSYS-users mailing list<br>
                    <a moz-do-not-send="true"
                      href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.<wbr>onebuilding.org</a><br>
                    <a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org"
                      rel="noreferrer" target="_blank">http://lists.onebuilding.org/<wbr>listinfo.cgi/trnsys-users-<wbr>onebuilding.org</a><br>
                  </blockquote>
                </div>
                <br>
              </div>
            </div>
          </blockquote>
          <blockquote type="cite">
            <div><span>_______________________________________________</span><br>
              <span>TRNSYS-users mailing list</span><br>
              <span><a moz-do-not-send="true"
                  href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a></span><br>
              <span><a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a></span><br>
            </div>
          </blockquote>
        </div>
      </blockquote>
      <blockquote type="cite">
        <div><span>_______________________________________________</span><br>
          <span>TRNSYS-users mailing list</span><br>
          <span><a moz-do-not-send="true"
              href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a></span><br>
          <span><a moz-do-not-send="true"
href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>