    <p>Javier,</p>
    <p>  If you need properties from the fluids that are not in the
      FluidProperties() routine then you would need to add them by
      modifying the Fluids.f90 source code file and then to recompile
      the TRNDll using a Fortran compiler.</p>
    <p>  Before you try to modify that file, however, I'd like to
      understand a bit more about the heat pump model that you want to
      write. For a number of reasons, TRNSYS's heat pump models
      (primarily in the TESS HVAC Library) rely on a catalog data lookup
      approach instead of being first principals models. By looking up
      the capacity and COP at certain operating conditions the models do
      not rely on the refrigerant properties, which makes for a more
      flexible and easy to implement model. If you'd like to send me an
      email directly, please feel free to do so. With a little more
      explanation about what you're looking for in a heat pump model I
      may be able to give you some additional direction.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 01/13/2017 14:33, Javier Vega via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAEju=PqQw-WG5Xm8XovN9hwhHVFW3Sb0JUKGbXc=m8E7O=EEow@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hello TRNSYS users,
        <div><br>
        </div>
        <div>I'm looking forward to program my own heat pump Type
          component. I was checking on the programmer's guide to get
          familiar with FORTRAN (first time I'm going to write in this)
          and the different functions in general.</div>
        <div><br>
        </div>
        <div>For now, all is OK except for the refrigerants listed in
          the Fluid Properties. Preferably, I would like to simulate a
          heat pump using R410a, which doesn't seem to be in the
          refrigerants available. What are my options?</div>
        <div><br>
        </div>
        <div>Thank you very much,</div>
        <div>Javier Vega</div>
        <div>Mechanical Engineering Student, Universidad de Concepción,
          Chile</div>
        <div><br>
        </div>
        <div><br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>