    <p>Adnan,</p>
    <p>  The solar azimuth that comes from Type16 is relative to the
      North/South axis. It is not relative to the building. If you have
      modeled your building starting with Trnsys3D and you drew the
      building using plan North (as opposed to absolute north) then
      you'll need to add an equation after Type16 that adds the turn
      angle to the solar azimuth angle coming from Type16 before then
      passing it on to Type56.</p>
    <p>  If you look at the 3D building example (especially at some of
      the later steps) you'll be able to see one way of implementing the
      equation.</p>
    <p>  If you drew your building using absolute north or if you did
      not use Trnsys3D such that the solar radiation falling on your
      building (as calculated by Type16) is the correct amount based on
      the direction that each wall faces then you do not need to modify
      the solar azimuth angle coming from Type16.<br>
    </p>
    <p>  kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 01/12/2017 02:39, adnan rasheed via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAG9tXZgwHmPOVz0=bNfPaLr6Gg36Z1vML51TVpAOgwdJfkrVhg@mail.gmail.com"
      type="cite">
      <div dir="ltr">Hi everyone
        <div><br>
        </div>
        <div>i am using type 9 and type 16, for processing weather data,
          my problem is i am using turn equations to change the position
          of the building. everything is clear to me except solar
          azimuth angle(output of Type 16) Type 16 automatically
          calculate this or i need to give some input value from weather
          component. problem is i am changing turn but no change in
          solar gain. </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>Regards</div>
        <div>Adnan </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>