<div dir="ltr">Hi again!<div><br></div><div>Jeff, after your response, I've tried several things. The interesting results I've got is that in the same configuration I have, supressing Type 93 (I put that to soften the control function before noticing this problem) and connecting the "Fraction of Maximum Flow" directly to the pump's "Control function" input, I get good results. As soon as I put the proper capacitance of the collector's array, the negative peaks start to pop up again.</div><div><br></div><div>Trying with the "Control Colector technique" it's the same. I've set the control collector without mass and connecting the control output to Type 695 pump. Then, if I set the real collector without mass, i get good results, if I put mass on the real collector, I get the negative peaks.</div><div><br></div><div>Is it really a control/numerical problem, or is it that because the capacitance of the collectors, everytime the pump starts, the collectors must heat first with the energy from the solar tank?</div><div><br></div><div>Again, I attach some pictures and plots.</div><div><br></div><div>Thanks in advance,<br>Javier Vega Benavente</div><div>Mechanical Engineering Student, Universidad de Concepción, Chile</div><div><br></div><div><br></div></div>