<pre>Louis,<br /><br />Are you reducing the flow rate such that you have the same flow rate per bore when you connect them in series? I.E. The total flow rate for 6 bores in series should only be 1/6 of the flow if they were all in parallel.<br /><br />Jeff<br /><br />---<br />Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577 Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton@tess-inc.com
</pre>
</div>
<p>On 12/14/2016 12:59 pm, via TRNSYS-users wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px"><!-- html ignored --><!-- head ignored --><!-- meta ignored --><!-- meta ignored --><!-- node type 8 --><!-- node type 8 -->
<div class="WordSection1">
<p class="MsoNormal"><span>Dear all, <!-- o ignored --></span></p>
<p class="MsoNormal"><span>I want to see the effect of the number of boreholes in series in a typical ground storage application. I have 72 boreholes and I change the number of boreholes in series as well as the number of radial regions to 1, 6 12, etc… and the results are always unchanged ?? <!-- o ignored --></span></p>
<p class="MsoNormal"><span>Does anyone knows why ? <!-- o ignored --></span></p>
<p class="MsoNormal"><span>Thank you very much <!-- o ignored --></span></p>
<p class="MsoNormal"><span><!-- o ignored --> </span></p>
<p class="MsoNormal"><span>Louis Lamarche <!-- o ignored --></span></p>
<p class="MsoNormal"><span><!-- o ignored --> </span></p>
</div>
<!-- html ignored --><br />
<pre>_______________________________________________
TRNSYS-users mailing list
<a href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
</blockquote>
</body></html>