    <p>Khem,</p>
    <p>  In the Type927 parameter list in your example project, the
      parameter that sets the number of source temperatures in the
      heating performance data file is set to 5 but in fact there are 6
      values of source temperature in the data file. If you change the
      value of parameter 9 from 5 to 6 then the Type will return the
      expected power consumption and COP.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 11/02/2016 14:57, bridjesh gautam
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAC+SyVYsTPhPaoV7BbVGkNZ+gZdoLEj-XFxjWovXXromjA7+2g@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div>Dear TRNSYS Users,</div>
        <div><br>
        </div>
        <div>I am trying to use either TYPE 927 or 1221 in combination
          with unglazed solar collectors and have some questions. If you
          have any experience with W-W HP components, I would love to
          hear from you. </div>
        <div><br>
        </div>
        <div><b>1. Calculation of COP and Power </b></div>
        <div><br>
        </div>
        <div>For some reason, when I input load temperature ,source
          temperature and flow rate exactly as listed in heating
          performance file, the COP and power consumption calculated by
          the component is different than the values entered in the data
          file. <br>
        </div>
        <div><b><br>
          </b></div>
        <div><b>Example </b></div>
        <div>A line of  example heating data file reads: (pre-installed
          example) (Heating capacity =30000, Heating power=6000) </div>
        <div><br>
        </div>
        <div>0.9007<span class="gmail-Apple-tab-span" style="white-space:pre">  </span>0.6731<span class="gmail-Apple-tab-span" style="white-space:pre">                                                </span>!Normalized
          Capacity and Normalized Power at 1, 1, 15.556[C], -1.1111[C]<br>
        </div>
        <div><br>
        </div>
        <div>But when I put input load temperature 15.556  , source
          -1.11, input and output mass flow = 1440 ( 0.4 l/s ,rated) ,
          the model calculates Power and COP  as 5961 kJ/hr and 4.59,
          when clearly the input file shows power to be (0.67*6000),
          which is not at all equal to what model calculates. COP values
          are different too. For all these I just used Type 927 with no
          change and the file is attached. </div>
        <div><br>
        </div>
        <div><b>So my question is, am I understanding everything wrong
            or are there some bugs in the code itself ? </b></div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div>I hope, someone will be kind enough to answer me. </div>
        <div><br>
        </div>
        <div>Your's</div>
        <div>Khem Gautam </div>
        <div>Masters student </div>
        <div>Aarhus University, Denmark. </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
        <div><br>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>