    <p>Nuha,</p>
    <p>  I am not sure what data you are passing from Type9 to Type107
      but Type107 does not take chiller load as an input. It takes the
      temperature and flow rate of three streams of water (the hot water
      (source energy) stream, the chilled water stream, and the cooling
      water stream). Unless you have made some computations outside of
      TRNSYS in order to convert the loads that you are reading with
      Type9 into a temperature and flow rate of chilled water returning
      from the load to the absorption chiller then the connection you
      have made needs to be revised.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 11/01/2016 04:20, Nuha Juneidi via
      TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAKGbA4ngyucySuVYBGGddd+6dcWLNbzdS+B69ktRro-0_nMnww@mail.gmail.com"
      type="cite">
      <div dir="ltr">Dear users,
        <div><br>
        </div>
        <div>I am working on a project for my masters thesis, it's an
          solar cooling. I almost get closer to acomplish it, but I
          found some difficulties in using <b>Type 107</b> (Absorption
          Chiller) and <b>Type 9e</b> (Data Readers). Does anyone
          worked on a similar project? Any ideas about using the Types
          107 and 9e? Can anyone help?<br>
        </div>
        <div><br>
        </div>
        <div>Please find out in attached file a screenshot of my
          connections I have made.</div>
        <div><br>
        </div>
        <div>Kind regards,</div>
        <div>Nuha</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>