<html>
  <head>
    <meta content="text/html; charset=UTF-8" http-equiv="Content-Type">
  </head>
  <body bgcolor="#FFFFFF" text="#000000">
    <p>Issmail <br>
    </p>
    <p>  Type56 has built-in idealized heating and cooling types that
      will meet a setpoint temperature if you have set them up to have
      unlimited heating and cooling capacity. What you are looking at in
      TRNBuild is the heating set point temperature that is being met.
      The temperature maintained in the room is based on the equation
      5*schedule + 15 where schedule is the value of a SCHEDULE function
      defined in the TRNBuild schedule manager. It probably has a value
      of either 0 or 1 depending on when the building is occupied. This
      would mean that when the building is unoccupied the heating set
      temperature would be 15C and that when the building is occupied,
      the heating set temperature would be 20C.</p>
    <p>kind regards,</p>
    <p> David</p>
    <p><br>
    </p>
    <br>
    <div class="moz-cite-prefix">On 07/14/2016 08:42, Issmail Ouhallou
      via TRNSYS-users wrote:<br>
    </div>
    <blockquote
cite="mid:CAA779b1soBMycd+4=GA1VQ1tG0qndS9tNuGcmg7OUo0a5dZL1g@mail.gmail.com"
      type="cite">
      <div dir="ltr">
        <div class="gmail_default"
          style="font-family:tahoma,sans-serif;color:rgb(0,0,0)">​Dear
          users,</div>
        <div class="gmail_default"
          style="font-family:tahoma,sans-serif;color:rgb(0,0,0)">  In
          the order of setting a new heating type, I don't understand
          the difference between the <b><i>room temperature control</i></b>
          when it's set up to constant value (20 °C for instance) and
          the schedule value (5*schedule + 15 °C for instance) !!</div>
        <div class="gmail_default"
          style="font-family:tahoma,sans-serif;color:rgb(0,0,0)">  Can
          some one explain to me the difference, specially for the
          second value : 5*schedule + 15 °C ?</div>
        <div class="gmail_default"
          style="font-family:tahoma,sans-serif;color:rgb(0,0,0)"><br>
        </div>
        <div class="gmail_default"
          style="font-family:tahoma,sans-serif;color:rgb(0,0,0)">Best
          regards,</div>
        <div class="gmail_default"
          style="font-family:tahoma,sans-serif;color:rgb(0,0,0)"> 
          ISSMAIL.</div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
TRNSYS-users mailing list
<a class="moz-txt-link-abbreviated" href="mailto:TRNSYS-users@lists.onebuilding.org">TRNSYS-users@lists.onebuilding.org</a>
<a class="moz-txt-link-freetext" href="http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org">http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org</a>
</pre>
    </blockquote>
    <br>
    <pre class="moz-signature" cols="72">-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
<a class="moz-txt-link-abbreviated" href="mailto:d.bradley@tess-inc.com">d.bradley@tess-inc.com</a>

<a class="moz-txt-link-freetext" href="http://www.tess-inc.com">http://www.tess-inc.com</a>
<a class="moz-txt-link-freetext" href="http://www.trnsys.com">http://www.trnsys.com</a></pre>
  </body>
</html>